Hello Arno,
Can apply the patch directly or should I recompile nut?
Best regards,
Panagiotis
On 3/4/2015 5:06 μμ, Arnaud Quette wrote:
Hello Panagiotis
2015-04-03 14:28 GMT+02:00 Panagiotis Kritikakos
<panagiotis.kritika...@nikitec.gr
<mailto:panagiotis.kritika...@nikitec.gr>>:
Hello Arno,
Question: have you also tested oldmge-shut?
Otherwise, that might be interesting to do so and send back
the results of these tests...
Yes, I've tried this as well with worse results unfortunately.
This driver seems to be even more unstable. When it gets able to
set communication with the UPS (which is not always the case), it
usually lost it again after a while.
~# /usr/local/libexec/nut/oldmge-shut -DD -a ups-filesrv01
Network UPS Tools - Eaton / SHUT driver 0.70 (2.7.2)
0.000000 debug level is '2'
0.000882 entering upsdrv_initups()
0.001019 entering shut_ups_start()
0.028445 Communication with UPS established
0.028457 entering shut_get_descriptor(n 21, 9)
0.111394 shut_wait_ack(): ACK received
0.185328 entering shut_get_descriptor(n 01, 18)
0.273455 shut_wait_ack(): ACK received
0.423238 Device Descriptor:
bLength: 0x12
bDescriptorType: 0x01
bcdUSB: 0x0110
bDeviceClass: 0x00
bDeviceSubClass: 0x00
bDeviceProtocol: 0x00
bMaxPacketSize0: 0x08
idVendor: 0x0463
idProduct: 0xffff
bcdDevice: 0x0100
iManufacturer: 0x01
iProduct: 0x02
iSerialNumber: 0x03
bNumConfigurations: 0x01
0.423251 entering shut_get_descriptor(n 22, 1538)
0.525087 shut_wait_ack(): ACK received
9.705471 Unable to get Report Descriptor
It there a possibility to be an issue of the UPS, or the
connection between the serial port of the machine and the UPS?
thanks for the confirmation with oldmge-shut. I'm not astonished on
the results, but was worth a try.
I've double checked the related code difference for mge-shut between
2.7.1 and 2.7.2.
Again, the only diff I see is the one pointed previously (setline...).
So, it would be great if you could test this patch (through some
reboots) and report back.
Then, I don't think it's an issue with the device.
There is a long run TODO (mentioned in the header of libshut.c) that
is the baudrate negotiation.
The driver still communicates at 2400bauds, which is not that much for
such verbose units. We could go at least for 9600 on these units,
which is 4 times faster already.
This may cause some slowness and behavior issues as you're
experiencing, under some circumstances.
For example, the test using a 5SC750 on Linux (Debian Jessie) shows
that report descriptor (size 1538) takes ~10 seconds to be retrieved,
which is quite long.
Then, even if this "new"mge-shut is a lot better than the oldmge-shut,
it can still be perfected on the error handling (and not optimal
cases), which you may be hitting.
And finally, the notification handling could also help to poll less
the unit, while being notified of critical status changes.
cheers,
Arno
--
Eaton Data Center Automation - Opensource Leader
NUT (Network UPS Tools) Project Leader - http://www.networkupstools.org