El 22/04/15 a les 01:55, Charles Lepple ha escrit:
On Apr 21, 2015, at 12:09 PM, dmanye <dma...@urv.cat> wrote:
Apr 21 17:45:23 jessie641 upsmon[532]: FSD set on UPS smt750i@10.21.102.241
failed: ERR ACCESS-DENIED
Apr 21 17:45:23 jessie641 upsmon[532]: Executing automatic power-fail shutdown
Apr 21 17:45:23 jessie641 upsmon[532]: Auto logout and shutdown proceeding
i think the problem may be the first line. do you know what can be the cause?
The MONITOR line in upsmon.conf needs to correspond to one of the user definitions in upsd.users,
and that user needs "upsmon master" or "upsmon slave" permission.
Note that entries in upsd.users should probably be called "roles" to avoid
confusion with system users in /etc/passwd, but that is how everything is named at the
moment.
i've found the problem. i had in upsd.users in the master node:
[upsmon]
upsmon master
password blah
i didn't write a '=' in the second line because the first one doesn't
have it. what works for me is:
[upsmon]
upsmon master
password = blah
thank you very much.
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser