On Sep 15, 2015, at 5:12 PM, Rob Groner <rgro...@rtd.com> wrote: > > Charles, > > Trying to track down the source of the problem, I checked Yast to make sure I > had at least 0.1.8 version for libusb. I saw this (attached photo). Is it > then actually using –compat instead of the “real” libusb? And is that a > problem?
You're right, both the -compat and real libusb packages will use the same libusb-0.1.so* name. It's not necessarily a problem, but it does mean that there is different code between your driver and the kernel. Most of the NUT testing has been done with the original libusb. > I just thought of something else that has changed since the last time I was > trying this.... I am now using the "--with-pidpath=/var/run/ups" > configuration parameter to change where everything keeps the pid files. I > wasn't doing that before. Since that's mounted to tmpfs, is it possible > that's getting unmounted before the shutdown command happens (and thus not > finding the .pid file, it tries to start it instead)? You might be on to something, but if so, the race happens earlier than the "usbhid-ups -k" invocation. Because the "-k" flag is meant to be called at the end of the shutdown sequence, it doesn't assume /var is mounted, and consequently, it doesn't check for other PID files. However, if a driver happens to still be running, it could cause the "-k" option to report a busy error. https://github.com/networkupstools/nut/blob/master/drivers/main.c#L588 -- Charles Lepple clepple@gmail _______________________________________________ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser