On Nov 21, 2015, at 8:54 AM, Róbert SZAKSZ <rob...@szaksz.eu> wrote:
>>> If the UPS is capable of the smart protocol, I still think that is worth >>> trying first. But it's up to you. >> I am not 100% sure that smart protocol is capable, because the only one >> place where it is mentioned is the picture I sended you. >But your original email mentioned "UPS TxD" and "UPS RxD"... Yes, that's the problem, I have nothing more than this peace of schema and there is mentioned TxD and RxD, but I nowhere find some information to the UPS. May be I disasemble the UPS and look inside to see the physical connection. >> Question for contact cable >> http://web.archive.org/web/20100106160328/http://ups.miem.edu.ru/ups_faq5.html >> type 5.2.1 is to set >> CP[RTS] OL[CTS] LB[DCD] SD[DTR] is this correct? >Probably. The testing procedure at >http://www.networkupstools.org/docs/man/genericups.html#_testing_compatibility >should help in case some of the signals need a "-". This settings is working, OL is appeared but OB not. I will try to change some settings... Thanks a lot, Robert SZAKSZ. _______________________________________________ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser