Hi, This might be a simple thing to fix, but I can’t figure it out. We replaced the battery for the first time in our Eaton 5PX a couple of weeks ago, but we haven’t been able to clear the “ups.alarm: replace battery!” status.
Details of our installation are: OS: Debian 6 NUT version: 2.7.4 Installation method: from source tarball UPS device: Eaton 5PX2000IRT, 240V, 1800W, 2000VA, bought in October 2013 Here’s the status as reported by upsc: battery.capacity: 9.00 battery.charge: 100 battery.charge.low: 20 battery.charge.restart: 0 battery.charger.status: floating battery.energysave: no battery.protection: yes battery.runtime: 1032 battery.type: PbAc device.mfr: EATON device.model: Eaton 5PX 2000 device.serial: G098D27047 device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.parameter.synchronous: no driver.parameter.vendorid: 0463 driver.version: 2.7.4 driver.version.data: MGE HID 1.39 driver.version.internal: 0.41 input.current: 0.00 input.frequency: 49.9 input.frequency.extended: no input.frequency.nominal: 50 input.sensitivity: normal input.transfer.boost.low: 184 input.transfer.high: 294 input.transfer.low: 160 input.transfer.trim.high: 265 input.voltage: 235.0 input.voltage.extended: no input.voltage.nominal: 230 outlet.1.autoswitch.charge.low: 0 outlet.1.current: 1.20 outlet.1.delay.shutdown: 65535 outlet.1.delay.start: 3 outlet.1.desc: PowerShare Outlet 1 outlet.1.id: 1 outlet.1.power: 282 outlet.1.powerfactor: 57.00 outlet.1.realpower: 162 outlet.1.status: on outlet.1.switchable: yes outlet.2.autoswitch.charge.low: 0 outlet.2.current: 0.40 outlet.2.delay.shutdown: 65535 outlet.2.delay.start: 6 outlet.2.desc: PowerShare Outlet 2 outlet.2.id: 2 outlet.2.power: 94 outlet.2.powerfactor: 72.00 outlet.2.realpower: 68 outlet.2.status: on outlet.2.switchable: yes outlet.current: 1.00 outlet.desc: Main Outlet outlet.id: 0 outlet.power: 276 outlet.powerfactor: 99.00 outlet.realpower: 274 outlet.switchable: no output.current: 2.60 output.frequency: 49.9 output.frequency.nominal: 50 output.powerfactor: 0.82 output.voltage: 235.0 output.voltage.nominal: 230 ups.alarm: Replace battery! ups.beeper.status: enabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.efficiency: 95 ups.firmware: 06 ups.load: 30 ups.load.high: 105 ups.mfr: EATON ups.model: Eaton 5PX 2000 ups.power: 611 ups.power.nominal: 2000 ups.productid: ffff ups.realpower: 504 ups.realpower.nominal: 1800 ups.serial: G098D27047 ups.shutdown: enabled ups.start.auto: yes ups.start.battery: yes ups.start.reboot: yes ups.status: ALARM OL CHRG RB ups.test.interval: 604800 ups.test.result: Done and passed ups.timer.shutdown: 0 ups.timer.start: 0 ups.type: offline / line interactive ups.vendorid: 0463 And here’s the output from /usr/local/nut/bin/usbhid-ups -DD -a <ups-name> I had to ^C it after a bit as it was just retrying. Looks like a communications problem with the UPS over the USB cable? We’ve unplugged it and replugged it half a dozen times before this. Network UPS Tools - Generic HID driver 0.41 (2.7.4) USB communication driver 0.33 0.000000 debug level is '2' 0.000279 upsdrv_initups... 0.000424 Checking device (0463/FFFF) (002/008) 0.275036 - VendorID: 0463 0.275054 - ProductID: ffff 0.275056 - Manufacturer: EATON 0.275059 - Product: Eaton 5PX 0.275061 - Serial Number: G098D27047 0.275063 - Bus: 002 0.275065 - Device release number: 0100 0.275068 Trying to match device 0.275102 Device matches 0.309531 HID descriptor length 2580 4.749244 Report Descriptor size = 2580 4.749684 Using subdriver: MGE HID 1.39 4.749691 234 HID objects found 4.778444 Path: UPS.BatterySystem.Battery.AudibleAlarmControl, Type: Feature, ReportID: 0x28, Offset: 0, Size: 8, Value: 2 4.816700 Path: UPS.BatterySystem.Battery.BatteryID, Type: Feature, ReportID: 0x20, Offset: 0, Size: 8, Value: 1 4.850696 Path: UPS.BatterySystem.Battery.Count, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 0 4.886600 Path: UPS.BatterySystem.Battery.DeepDischargeProtection, Type: Feature, ReportID: 0x22, Offset: 0, Size: 8, Value: 1 4.925954 Path: UPS.BatterySystem.Battery.DesignCapacity, Type: Feature, ReportID: 0x23, Offset: 0, Size: 32, Value: 32400 4.964082 Path: UPS.BatterySystem.Battery.PresentStatus.Present, Type: Feature, ReportID: 0x27, Offset: 0, Size: 8, Value: 1 4.964102 Path: UPS.BatterySystem.Battery.PresentStatus.Present, Type: Input, ReportID: 0x27, Offset: 0, Size: 8, Value: 1 4.994604 Path: UPS.BatterySystem.Battery.Test, Type: Feature, ReportID: 0x24, Offset: 0, Size: 8, Value: 1 5.033884 Path: UPS.BatterySystem.Battery.TestPeriod, Type: Feature, ReportID: 0x25, Offset: 0, Size: 32, Value: 604800 5.033899 Path: UPS.BatterySystem.BatterySystemID, Type: Feature, ReportID: 0x20, Offset: 8, Size: 8, Value: 1 5.066597 Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1 5.066620 Path: UPS.BatterySystem.Charger.ChargerID, Type: Feature, ReportID: 0x20, Offset: 16, Size: 8, Value: 1 5.103461 Path: UPS.BatterySystem.Charger.ChargerType, Type: Feature, ReportID: 0x26, Offset: 0, Size: 8, Value: 4 5.103480 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 5.103489 Path: UPS.BatterySystem.Charger.PresentStatus.Floating, Type: Feature, ReportID: 0x27, Offset: 8, Size: 8, Value: 1 5.103557 Path: UPS.BatterySystem.Charger.PresentStatus.Floating, Type: Input, ReportID: 0x27, Offset: 8, Size: 8, Value: 1 5.103569 Path: UPS.BatterySystem.Charger.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x27, Offset: 16, Size: 8, Value: 0 5.103579 Path: UPS.BatterySystem.Charger.PresentStatus.InternalFailure, Type: Input, ReportID: 0x27, Offset: 16, Size: 8, Value: 0 5.103589 Path: UPS.BatterySystem.Charger.PresentStatus.Used, Type: Feature, ReportID: 0x27, Offset: 24, Size: 8, Value: 1 5.103599 Path: UPS.BatterySystem.Charger.PresentStatus.Used, Type: Input, ReportID: 0x27, Offset: 24, Size: 8, Value: 1 5.103609 Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooHigh, Type: Feature, ReportID: 0x27, Offset: 32, Size: 8, Value: 0 5.103619 Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooHigh, Type: Input, ReportID: 0x27, Offset: 32, Size: 8, Value: 0 5.103628 Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooLow, Type: Feature, ReportID: 0x27, Offset: 40, Size: 8, Value: 0 5.103637 Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooLow, Type: Input, ReportID: 0x27, Offset: 40, Size: 8, Value: 0 5.138588 Path: UPS.Flow.[1].ConfigFrequency, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 50 5.175587 Path: UPS.Flow.[1].ConfigVoltage, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 230 5.215207 Path: UPS.Flow.[1].FlowID, Type: Feature, ReportID: 0x0b, Offset: 0, Size: 8, Value: 1 5.247504 Path: UPS.Flow.[4].ConfigActivePower, Type: Feature, ReportID: 0x74, Offset: 0, Size: 16, Value: 1800 5.283621 Path: UPS.Flow.[4].ConfigApparentPower, Type: Feature, ReportID: 0x75, Offset: 0, Size: 16, Value: 2000 5.320753 Path: UPS.Flow.[4].ConfigFrequency, Type: Feature, ReportID: 0x0d, Offset: 0, Size: 8, Value: 50 5.354218 Path: UPS.Flow.[4].ConfigPercentLoad, Type: Feature, ReportID: 0x16, Offset: 0, Size: 8, Value: 105 5.391725 Path: UPS.Flow.[4].ConfigVoltage, Type: Feature, ReportID: 0x72, Offset: 0, Size: 16, Value: 230 5.391743 Path: UPS.Flow.[4].FlowID, Type: Feature, ReportID: 0x0b, Offset: 8, Size: 8, Value: 4 5.473244 Path: UPS.HistorySystem.Event.[1].Code, Type: Feature, ReportID: 0x71, Offset: 0, Size: 16, Value: 0 5.473263 Path: UPS.HistorySystem.Event.[2].Code, Type: Feature, ReportID: 0x71, Offset: 16, Size: 16, Value: 0 5.473271 Path: UPS.HistorySystem.Event.[3].Code, Type: Feature, ReportID: 0x71, Offset: 32, Size: 16, Value: 0 5.473279 Path: UPS.HistorySystem.Event.[4].Code, Type: Feature, ReportID: 0x71, Offset: 48, Size: 16, Value: 0 5.473287 Path: UPS.HistorySystem.Event.[5].Code, Type: Feature, ReportID: 0x71, Offset: 64, Size: 16, Value: 0 5.473297 Path: UPS.HistorySystem.Event.[6].Code, Type: Feature, ReportID: 0x71, Offset: 80, Size: 16, Value: 0 5.473311 Path: UPS.HistorySystem.Event.[7].Code, Type: Feature, ReportID: 0x71, Offset: 96, Size: 16, Value: 0 5.473325 Path: UPS.HistorySystem.Event.[8].Code, Type: Feature, ReportID: 0x71, Offset: 112, Size: 16, Value: 0 5.473340 Path: UPS.HistorySystem.Event.[9].Code, Type: Feature, ReportID: 0x71, Offset: 128, Size: 16, Value: 0 5.473359 Path: UPS.HistorySystem.Event.[10].Code, Type: Feature, ReportID: 0x71, Offset: 144, Size: 16, Value: 0 5.473368 Path: UPS.HistorySystem.Event.[11].Code, Type: Feature, ReportID: 0x71, Offset: 160, Size: 16, Value: 0 5.473376 Path: UPS.HistorySystem.Event.[12].Code, Type: Feature, ReportID: 0x71, Offset: 176, Size: 16, Value: 0 5.473384 Path: UPS.HistorySystem.Event.[13].Code, Type: Feature, ReportID: 0x71, Offset: 192, Size: 16, Value: 0 5.473392 Path: UPS.HistorySystem.Event.[14].Code, Type: Feature, ReportID: 0x71, Offset: 208, Size: 16, Value: 0 5.473399 Path: UPS.HistorySystem.Event.[15].Code, Type: Feature, ReportID: 0x71, Offset: 224, Size: 16, Value: 0 5.498223 Path: UPS.LCMSystem.LCMAlarm.[1].Count, Type: Feature, ReportID: 0x51, Offset: 0, Size: 8, Value: 0 5.537897 Path: UPS.LCMSystem.LCMAlarm.[1].Interval, Type: Feature, ReportID: 0x54, Offset: 0, Size: 32, Value: 2.592e+06 5.572599 Path: UPS.LCMSystem.LCMAlarm.[1].LCMAlarmID, Type: Feature, ReportID: 0x50, Offset: 0, Size: 8, Value: 1 5.606524 Path: UPS.LCMSystem.LCMAlarm.[1].Mode, Type: Feature, ReportID: 0x57, Offset: 0, Size: 8, Value: 0 5.643485 Path: UPS.LCMSystem.LCMAlarm.[1].PresentStatus.TimerExpired, Type: Feature, ReportID: 0x5d, Offset: 0, Size: 8, Value: 1 5.643505 Path: UPS.LCMSystem.LCMAlarm.[1].PresentStatus.TimerExpired, Type: Input, ReportID: 0x5d, Offset: 0, Size: 8, Value: 1 5.681732 Path: UPS.LCMSystem.LCMAlarm.[1].Timer, Type: Feature, ReportID: 0x5a, Offset: 0, Size: 32, Value: 0 5.714495 Path: UPS.LCMSystem.LCMAlarm.[2].Count, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0 5.753866 Path: UPS.LCMSystem.LCMAlarm.[2].Interval, Type: Feature, ReportID: 0x55, Offset: 0, Size: 32, Value: 2.592e+06 5.753885 Path: UPS.LCMSystem.LCMAlarm.[2].LCMAlarmID, Type: Feature, ReportID: 0x50, Offset: 8, Size: 8, Value: 2 5.786526 Path: UPS.LCMSystem.LCMAlarm.[2].Mode, Type: Feature, ReportID: 0x58, Offset: 0, Size: 8, Value: 0 5.786541 Path: UPS.LCMSystem.LCMAlarm.[2].PresentStatus.TimerExpired, Type: Feature, ReportID: 0x5d, Offset: 8, Size: 8, Value: 1 5.786547 Path: UPS.LCMSystem.LCMAlarm.[2].PresentStatus.TimerExpired, Type: Input, ReportID: 0x5d, Offset: 8, Size: 8, Value: 1 5.825868 Path: UPS.LCMSystem.LCMAlarm.[2].Timer, Type: Feature, ReportID: 0x5b, Offset: 0, Size: 32, Value: 0 5.825882 Path: UPS.LCMSystem.LCMSystemID, Type: Feature, ReportID: 0x50, Offset: 16, Size: 8, Value: 1 5.890506 Path: UPS.OutletSystem.Outlet.[1].ActivePower, Type: Feature, ReportID: 0x83, Offset: 0, Size: 16, Value: 279 5.890528 Path: UPS.OutletSystem.Outlet.[1].ApparentPower, Type: Feature, ReportID: 0x83, Offset: 16, Size: 16, Value: 281 5.890541 Path: UPS.OutletSystem.Outlet.[1].Current, Type: Feature, ReportID: 0x83, Offset: 32, Size: 16, Value: 1.1 5.919144 Path: UPS.OutletSystem.Outlet.[1].FlowID, Type: Feature, ReportID: 0x80, Offset: 0, Size: 8, Value: 4 5.919158 Path: UPS.OutletSystem.Outlet.[1].OutletID, Type: Feature, ReportID: 0x80, Offset: 8, Size: 8, Value: 0 5.919167 Path: UPS.OutletSystem.Outlet.[1].PowerFactor, Type: Feature, ReportID: 0x83, Offset: 48, Size: 8, Value: 99 5.952998 Path: UPS.OutletSystem.Outlet.[1].PresentStatus.Switchable, Type: Feature, ReportID: 0x81, Offset: 0, Size: 8, Value: 0 6.015393 Path: UPS.OutletSystem.Outlet.[1].Statistic.[1].Energy, Type: Feature, ReportID: 0x8c, Offset: 0, Size: 32, Value: 982000 6.015450 Path: UPS.OutletSystem.Outlet.[1].Statistic.[1].Interval, Type: Feature, ReportID: 0x8c, Offset: 32, Size: 32, Value: 3600 6.015468 Path: UPS.OutletSystem.Outlet.[1].Statistic.[4].Energy, Type: Feature, ReportID: 0x8c, Offset: 64, Size: 32, Value: 2.59786e+10 6.038539 Path: UPS.OutletSystem.Outlet.[1].Statistic.[4].ModuleReset, Type: Feature, ReportID: 0x64, Offset: 0, Size: 8, Value: 0 6.038558 Path: UPS.OutletSystem.Outlet.[1].Statistic.[4].Reset.Energy, Type: Feature, ReportID: 0x8c, Offset: 96, Size: 32, Value: 0 6.038567 Path: UPS.OutletSystem.Outlet.[1].Statistic.[4].Reset.Timer, Type: Feature, ReportID: 0x8c, Offset: 128, Size: 32, Value: 0 6.038576 Path: UPS.OutletSystem.Outlet.[2].ActivePower, Type: Feature, ReportID: 0x83, Offset: 56, Size: 16, Value: 157 6.038584 Path: UPS.OutletSystem.Outlet.[2].ApparentPower, Type: Feature, ReportID: 0x83, Offset: 72, Size: 16, Value: 282 6.038590 Path: UPS.OutletSystem.Outlet.[2].AutomaticRestart, Type: Feature, ReportID: 0x81, Offset: 8, Size: 8, Value: 1 6.038597 Path: UPS.OutletSystem.Outlet.[2].Current, Type: Feature, ReportID: 0x83, Offset: 88, Size: 16, Value: 1.2 6.077774 Path: UPS.OutletSystem.Outlet.[2].DelayBeforeShutdown, Type: Feature, ReportID: 0x8d, Offset: 0, Size: 32, Value: 0 6.113789 Path: UPS.OutletSystem.Outlet.[2].DelayBeforeStartup, Type: Feature, ReportID: 0x90, Offset: 0, Size: 32, Value: 0 6.113806 Path: UPS.OutletSystem.Outlet.[2].FlowID, Type: Feature, ReportID: 0x80, Offset: 16, Size: 8, Value: 4 6.113812 Path: UPS.OutletSystem.Outlet.[2].OutletID, Type: Feature, ReportID: 0x80, Offset: 24, Size: 8, Value: 1 6.113821 Path: UPS.OutletSystem.Outlet.[2].PowerFactor, Type: Feature, ReportID: 0x83, Offset: 104, Size: 8, Value: 55 6.113827 Path: UPS.OutletSystem.Outlet.[2].PresentStatus.Switchable, Type: Feature, ReportID: 0x81, Offset: 16, Size: 8, Value: 1 6.147518 Path: UPS.OutletSystem.Outlet.[2].PresentStatus.SwitchOn/Off, Type: Feature, ReportID: 0x82, Offset: 0, Size: 8, Value: 1 6.147538 Path: UPS.OutletSystem.Outlet.[2].PresentStatus.SwitchOn/Off, Type: Input, ReportID: 0x82, Offset: 0, Size: 8, Value: 1 6.182160 Path: UPS.OutletSystem.Outlet.[2].RemainingCapacityLimit, Type: Feature, ReportID: 0x84, Offset: 0, Size: 8, Value: 0 6.219571 Path: UPS.OutletSystem.Outlet.[2].ShutdownTimer, Type: Feature, ReportID: 0x87, Offset: 0, Size: 16, Value: 65535 6.255267 Path: UPS.OutletSystem.Outlet.[2].StartupTimer, Type: Feature, ReportID: 0x8a, Offset: 0, Size: 16, Value: 3 6.321171 Path: UPS.OutletSystem.Outlet.[2].Statistic.[1].Energy, Type: Feature, ReportID: 0x86, Offset: 0, Size: 32, Value: 561000 6.321190 Path: UPS.OutletSystem.Outlet.[2].Statistic.[1].Interval, Type: Feature, ReportID: 0x86, Offset: 32, Size: 32, Value: 3600 6.321199 Path: UPS.OutletSystem.Outlet.[2].Statistic.[4].Energy, Type: Feature, ReportID: 0x86, Offset: 64, Size: 32, Value: 1.11775e+10 6.344154 Path: UPS.OutletSystem.Outlet.[2].Statistic.[4].ModuleReset, Type: Feature, ReportID: 0x65, Offset: 0, Size: 8, Value: 0 6.344171 Path: UPS.OutletSystem.Outlet.[2].Statistic.[4].Reset.Energy, Type: Feature, ReportID: 0x86, Offset: 96, Size: 32, Value: 0 6.344179 Path: UPS.OutletSystem.Outlet.[2].Statistic.[4].Reset.Timer, Type: Feature, ReportID: 0x86, Offset: 128, Size: 32, Value: 0 6.344188 Path: UPS.OutletSystem.Outlet.[3].ActivePower, Type: Feature, ReportID: 0x83, Offset: 112, Size: 16, Value: 68 6.344196 Path: UPS.OutletSystem.Outlet.[3].ApparentPower, Type: Feature, ReportID: 0x83, Offset: 128, Size: 16, Value: 94 6.344201 Path: UPS.OutletSystem.Outlet.[3].AutomaticRestart, Type: Feature, ReportID: 0x81, Offset: 24, Size: 8, Value: 1 6.344209 Path: UPS.OutletSystem.Outlet.[3].Current, Type: Feature, ReportID: 0x83, Offset: 144, Size: 16, Value: 0.4 6.383811 Path: UPS.OutletSystem.Outlet.[3].DelayBeforeShutdown, Type: Feature, ReportID: 0x8e, Offset: 0, Size: 32, Value: 0 6.419781 Path: UPS.OutletSystem.Outlet.[3].DelayBeforeStartup, Type: Feature, ReportID: 0x91, Offset: 0, Size: 32, Value: 0 6.419807 Path: UPS.OutletSystem.Outlet.[3].FlowID, Type: Feature, ReportID: 0x80, Offset: 32, Size: 8, Value: 4 6.419813 Path: UPS.OutletSystem.Outlet.[3].OutletID, Type: Feature, ReportID: 0x80, Offset: 40, Size: 8, Value: 2 6.419822 Path: UPS.OutletSystem.Outlet.[3].PowerFactor, Type: Feature, ReportID: 0x83, Offset: 160, Size: 8, Value: 72 6.419829 Path: UPS.OutletSystem.Outlet.[3].PresentStatus.Switchable, Type: Feature, ReportID: 0x81, Offset: 32, Size: 8, Value: 1 6.419835 Path: UPS.OutletSystem.Outlet.[3].PresentStatus.SwitchOn/Off, Type: Feature, ReportID: 0x82, Offset: 8, Size: 8, Value: 1 6.419840 Path: UPS.OutletSystem.Outlet.[3].PresentStatus.SwitchOn/Off, Type: Input, ReportID: 0x82, Offset: 8, Size: 8, Value: 1 6.452164 Path: UPS.OutletSystem.Outlet.[3].RemainingCapacityLimit, Type: Feature, ReportID: 0x85, Offset: 0, Size: 8, Value: 0 6.489272 Path: UPS.OutletSystem.Outlet.[3].ShutdownTimer, Type: Feature, ReportID: 0x88, Offset: 0, Size: 16, Value: 65535 6.525515 Path: UPS.OutletSystem.Outlet.[3].StartupTimer, Type: Feature, ReportID: 0x8b, Offset: 0, Size: 16, Value: 6 6.591172 Path: UPS.OutletSystem.Outlet.[3].Statistic.[1].Energy, Type: Feature, ReportID: 0x89, Offset: 0, Size: 32, Value: 244000 6.591192 Path: UPS.OutletSystem.Outlet.[3].Statistic.[1].Interval, Type: Feature, ReportID: 0x89, Offset: 32, Size: 32, Value: 3600 6.591201 Path: UPS.OutletSystem.Outlet.[3].Statistic.[4].Energy, Type: Feature, ReportID: 0x89, Offset: 64, Size: 32, Value: 8.74446e+09 6.614262 Path: UPS.OutletSystem.Outlet.[3].Statistic.[4].ModuleReset, Type: Feature, ReportID: 0x66, Offset: 0, Size: 8, Value: 0 6.614280 Path: UPS.OutletSystem.Outlet.[3].Statistic.[4].Reset.Energy, Type: Feature, ReportID: 0x89, Offset: 96, Size: 32, Value: 0 6.614292 Path: UPS.OutletSystem.Outlet.[3].Statistic.[4].Reset.Timer, Type: Feature, ReportID: 0x89, Offset: 128, Size: 32, Value: 0 6.614301 Path: UPS.OutletSystem.OutletSystemID, Type: Feature, ReportID: 0x80, Offset: 48, Size: 8, Value: 1 6.650537 Path: UPS.PowerConverter.ConverterType, Type: Feature, ReportID: 0x4a, Offset: 0, Size: 8, Value: 1 6.686274 Path: UPS.PowerConverter.Input.[1].AutomaticRestart, Type: Feature, ReportID: 0x73, Offset: 0, Size: 8, Value: 1 6.727900 Path: UPS.PowerConverter.Input.[1].Current, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 0 6.761672 Path: UPS.PowerConverter.Input.[1].FlowID, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 1 6.761686 Path: UPS.PowerConverter.Input.[1].Frequency, Type: Feature, ReportID: 0x31, Offset: 16, Size: 16, Value: 49.9 6.761693 Path: UPS.PowerConverter.Input.[1].InputID, Type: Feature, ReportID: 0x30, Offset: 8, Size: 8, Value: 1 6.799965 Path: UPS.PowerConverter.Input.[1].PresentStatus.Boost, Type: Feature, ReportID: 0x32, Offset: 0, Size: 8, Value: 0 6.799981 Path: UPS.PowerConverter.Input.[1].PresentStatus.Boost, Type: Input, ReportID: 0x32, Offset: 0, Size: 8, Value: 0 6.799987 Path: UPS.PowerConverter.Input.[1].PresentStatus.Buck, Type: Feature, ReportID: 0x32, Offset: 8, Size: 8, Value: 0 6.799993 Path: UPS.PowerConverter.Input.[1].PresentStatus.Buck, Type: Input, ReportID: 0x32, Offset: 8, Size: 8, Value: 0 6.799999 Path: UPS.PowerConverter.Input.[1].PresentStatus.FrequencyOutOfRange, Type: Feature, ReportID: 0x32, Offset: 16, Size: 8, Value: 0 6.800005 Path: UPS.PowerConverter.Input.[1].PresentStatus.FrequencyOutOfRange, Type: Input, ReportID: 0x32, Offset: 16, Size: 8, Value: 0 6.800011 Path: UPS.PowerConverter.Input.[1].PresentStatus.InternalFailure, Type: Feature, ReportID: 0x32, Offset: 24, Size: 8, Value: 0 6.800017 Path: UPS.PowerConverter.Input.[1].PresentStatus.InternalFailure, Type: Input, ReportID: 0x32, Offset: 24, Size: 8, Value: 0 6.800023 Path: UPS.PowerConverter.Input.[1].PresentStatus.Used, Type: Feature, ReportID: 0x32, Offset: 32, Size: 8, Value: 1 6.800029 Path: UPS.PowerConverter.Input.[1].PresentStatus.Used, Type: Input, ReportID: 0x32, Offset: 32, Size: 8, Value: 1 6.800035 Path: UPS.PowerConverter.Input.[1].PresentStatus.VoltageOutOfRange, Type: Feature, ReportID: 0x32, Offset: 40, Size: 8, Value: 0 6.800041 Path: UPS.PowerConverter.Input.[1].PresentStatus.VoltageOutOfRange, Type: Input, ReportID: 0x32, Offset: 40, Size: 8, Value: 0 6.800048 Path: UPS.PowerConverter.Input.[1].Voltage, Type: Feature, ReportID: 0x31, Offset: 32, Size: 16, Value: 235 6.830932 Path: UPS.PowerConverter.Input.[3].ControlStandby, Type: Feature, ReportID: 0x3e, Offset: 0, Size: 8, Value: 0 6.866207 Path: UPS.PowerConverter.Input.[3].EnergySaving, Type: Feature, ReportID: 0x39, Offset: 0, Size: 8, Value: 0 6.866223 Path: UPS.PowerConverter.Input.[3].FlowID, Type: Feature, ReportID: 0x30, Offset: 16, Size: 8, Value: 3 6.866229 Path: UPS.PowerConverter.Input.[3].InputID, Type: Feature, ReportID: 0x30, Offset: 24, Size: 8, Value: 3 6.902061 Path: UPS.PowerConverter.Input.[3].PresentStatus.Used, Type: Feature, ReportID: 0x3b, Offset: 0, Size: 8, Value: 0 6.902077 Path: UPS.PowerConverter.Input.[3].PresentStatus.Used, Type: Input, ReportID: 0x3b, Offset: 0, Size: 8, Value: 0 6.938061 Path: UPS.PowerConverter.Input.[3].StartOnBattery, Type: Feature, ReportID: 0x3a, Offset: 0, Size: 8, Value: 1 6.974283 Path: UPS.PowerConverter.Inverter.PresentStatus.Used, Type: Feature, ReportID: 0x41, Offset: 0, Size: 8, Value: 0 6.974296 Path: UPS.PowerConverter.Inverter.PresentStatus.Used, Type: Input, ReportID: 0x41, Offset: 0, Size: 8, Value: 0 7.027572 Path: UPS.PowerConverter.Output.ActivePower, Type: Feature, ReportID: 0x42, Offset: 0, Size: 16, Value: 522 7.027590 Path: UPS.PowerConverter.Output.ApparentPower, Type: Feature, ReportID: 0x42, Offset: 16, Size: 16, Value: 611 7.027597 Path: UPS.PowerConverter.Output.Current, Type: Feature, ReportID: 0x42, Offset: 32, Size: 16, Value: 2.6 7.027603 Path: UPS.PowerConverter.Output.Efficiency, Type: Feature, ReportID: 0x42, Offset: 48, Size: 8, Value: 95 7.064046 Path: UPS.PowerConverter.Output.ExtendedFrequencyMode, Type: Feature, ReportID: 0x4b, Offset: 0, Size: 8, Value: 0 7.100065 Path: UPS.PowerConverter.Output.ExtendedVoltageMode, Type: Feature, ReportID: 0x4c, Offset: 0, Size: 8, Value: 0 7.138686 Path: UPS.PowerConverter.Output.FlowID, Type: Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 4 7.172050 Path: UPS.PowerConverter.Output.ForcedReboot, Type: Feature, ReportID: 0x43, Offset: 0, Size: 8, Value: 1 7.172071 Path: UPS.PowerConverter.Output.Frequency, Type: Feature, ReportID: 0x42, Offset: 56, Size: 16, Value: 49.9 7.209322 Path: UPS.PowerConverter.Output.HighVoltageBuckTransfer, Type: Feature, ReportID: 0x4d, Offset: 0, Size: 16, Value: 265 7.245308 Path: UPS.PowerConverter.Output.HighVoltageTransfer, Type: Feature, ReportID: 0x48, Offset: 0, Size: 16, Value: 294 7.281371 Path: UPS.PowerConverter.Output.LowVoltageBoostTransfer, Type: Feature, ReportID: 0x4e, Offset: 0, Size: 16, Value: 184 7.317332 Path: UPS.PowerConverter.Output.LowVoltageTransfer, Type: Feature, ReportID: 0x47, Offset: 0, Size: 16, Value: 160 7.317349 Path: UPS.PowerConverter.Output.OutputID, Type: Feature, ReportID: 0x40, Offset: 8, Size: 8, Value: 1 7.317356 Path: UPS.PowerConverter.Output.PowerFactor, Type: Feature, ReportID: 0x42, Offset: 72, Size: 8, Value: 85 7.352209 Path: UPS.PowerConverter.Output.PresentStatus.ShortCircuit, Type: Feature, ReportID: 0x49, Offset: 0, Size: 8, Value: 0 7.352227 Path: UPS.PowerConverter.Output.PresentStatus.ShortCircuit, Type: Input, ReportID: 0x49, Offset: 0, Size: 8, Value: 0 7.388051 Path: UPS.PowerConverter.Output.SensitivityMode, Type: Feature, ReportID: 0x4f, Offset: 0, Size: 8, Value: 0 7.454940 Path: UPS.PowerConverter.Output.Statistic.[1].Energy, Type: Feature, ReportID: 0x44, Offset: 0, Size: 32, Value: 1.789e+06 7.454964 Path: UPS.PowerConverter.Output.Statistic.[1].Interval, Type: Feature, ReportID: 0x44, Offset: 32, Size: 32, Value: 3600 7.454979 Path: UPS.PowerConverter.Output.Statistic.[4].Energy, Type: Feature, ReportID: 0x44, Offset: 64, Size: 32, Value: 4.59005e+10 7.477934 Path: UPS.PowerConverter.Output.Statistic.[4].ModuleReset, Type: Feature, ReportID: 0x67, Offset: 0, Size: 8, Value: 0 7.477953 Path: UPS.PowerConverter.Output.Statistic.[4].Reset.Energy, Type: Feature, ReportID: 0x44, Offset: 96, Size: 32, Value: 0 7.477962 Path: UPS.PowerConverter.Output.Statistic.[4].Reset.Timer, Type: Feature, ReportID: 0x44, Offset: 128, Size: 32, Value: 0 7.477969 Path: UPS.PowerConverter.Output.Voltage, Type: Feature, ReportID: 0x42, Offset: 80, Size: 16, Value: 235 7.477975 Path: UPS.PowerConverter.PowerConverterID, Type: Feature, ReportID: 0x40, Offset: 16, Size: 8, Value: 1 7.514187 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 2 7.553561 Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 1 7.553579 Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x0c, Offset: 8, Size: 8, Value: 2 7.588562 Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, ReportID: 0x0d, Offset: 8, Size: 16, Value: 48 7.626811 Path: UPS.PowerSummary.Country, Type: Feature, ReportID: 0x0b, Offset: 16, Size: 8, Value: 0 7.661596 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 7.697588 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 7.697604 Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x0c, Offset: 16, Size: 8, Value: 100 7.697609 Path: UPS.PowerSummary.FlowID, Type: Feature, ReportID: 0x0b, Offset: 24, Size: 8, Value: 4 7.697615 Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x0c, Offset: 24, Size: 8, Value: 100 7.736943 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 4 7.736962 Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 0x10, Offset: 8, Size: 8, Value: 1 7.736973 Path: UPS.PowerSummary.iModel, Type: Feature, ReportID: 0x10, Offset: 16, Size: 8, Value: 10 7.736983 Path: UPS.PowerSummary.iPartNumber, Type: Feature, ReportID: 0x10, Offset: 24, Size: 8, Value: 15 7.736992 Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x10, Offset: 32, Size: 8, Value: 2 7.737001 Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x10, Offset: 40, Size: 8, Value: 3 7.737010 Path: UPS.PowerSummary.iVersion, Type: Feature, ReportID: 0x10, Offset: 48, Size: 8, Value: 5 7.768583 Path: UPS.PowerSummary.PercentLoad, Type: Feature, ReportID: 0x07, Offset: 0, Size: 8, Value: 30 7.768606 Path: UPS.PowerSummary.PowerSummaryID, Type: Feature, ReportID: 0x0b, Offset: 32, Size: 8, Value: 1 7.806602 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 7.806618 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 7.806624 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 7.806629 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 7.806635 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 7.806642 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 7.838070 Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 8, Value: 0 7.838086 Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Input, ReportID: 0x0f, Offset: 0, Size: 8, Value: 0 7.878821 Path: UPS.PowerSummary.PresentStatus.ConfigurationFailure, Type: Feature, ReportID: 0x03, Offset: 0, Size: 8, Value: 0 7.878839 Path: UPS.PowerSummary.PresentStatus.ConfigurationFailure, Type: Input, ReportID: 0x03, Offset: 0, Size: 8, Value: 0 7.878848 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 7.878857 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 7.878865 Path: UPS.PowerSummary.PresentStatus.EmergencyStop, Type: Feature, ReportID: 0x03, Offset: 8, Size: 8, Value: 0 7.878874 Path: UPS.PowerSummary.PresentStatus.EmergencyStop, Type: Input, ReportID: 0x03, Offset: 8, Size: 8, Value: 0 7.878882 Path: UPS.PowerSummary.PresentStatus.FanFailure, Type: Feature, ReportID: 0x03, Offset: 16, Size: 8, Value: 0 7.878890 Path: UPS.PowerSummary.PresentStatus.FanFailure, Type: Input, ReportID: 0x03, Offset: 16, Size: 8, Value: 0 7.878898 Path: UPS.PowerSummary.PresentStatus.Good, Type: Feature, ReportID: 0x01, Offset: 32, Size: 8, Value: 1 7.878907 Path: UPS.PowerSummary.PresentStatus.Good, Type: Input, ReportID: 0x01, Offset: 32, Size: 8, Value: 1 7.913701 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 0 7.913721 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Input, ReportID: 0x02, Offset: 0, Size: 8, Value: 0 7.913736 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x02, Offset: 8, Size: 8, Value: 0 7.913745 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x02, Offset: 8, Size: 8, Value: 0 7.913754 Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, ReportID: 0x02, Offset: 16, Size: 8, Value: 0 7.913763 Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, ReportID: 0x02, Offset: 16, Size: 8, Value: 0 7.913772 Path: UPS.PowerSummary.PresentStatus.OverTemperature, Type: Feature, ReportID: 0x03, Offset: 24, Size: 8, Value: 0 7.913781 Path: UPS.PowerSummary.PresentStatus.OverTemperature, Type: Input, ReportID: 0x03, Offset: 24, Size: 8, Value: 0 7.913791 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x02, Offset: 24, Size: 8, Value: 0 7.913799 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x02, Offset: 24, Size: 8, Value: 0 7.913808 Path: UPS.PowerSummary.PresentStatus.Switchable, Type: Feature, ReportID: 0x03, Offset: 32, Size: 8, Value: 1 7.913817 Path: UPS.PowerSummary.PresentStatus.Switchable, Type: Input, ReportID: 0x03, Offset: 32, Size: 8, Value: 1 7.950826 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x06, Offset: 0, Size: 8, Value: 100 7.950843 Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x06, Offset: 0, Size: 8, Value: 100 7.982201 Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, ReportID: 0x08, Offset: 0, Size: 8, Value: 20 8.017950 Path: UPS.PowerSummary.RemainingCapacityLimitSetting, Type: Feature, ReportID: 0x12, Offset: 0, Size: 8, Value: 20 8.054081 Path: UPS.PowerSummary.RestartLevel, Type: Feature, ReportID: 0x0e, Offset: 0, Size: 8, Value: 0 8.054105 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x06, Offset: 8, Size: 32, Value: 932 8.054115 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x06, Offset: 8, Size: 32, Value: 932 8.089980 Path: UPS.PowerSummary.Schedule, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 0 8.129582 Path: UPS.PowerSummary.Timer, Type: Feature, ReportID: 0x18, Offset: 0, Size: 32, Value: 1.3442e+08 8.129599 Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x07, Offset: 8, Size: 16, Value: 53.8 8.211575 get_model_name(Eaton 5PX, 2000) 8.211596 comparing with: ellipse 300 8.211600 comparing with: ellipse 500 8.211604 comparing with: ellipse 650 8.211607 comparing with: ellipse 800 8.211610 comparing with: ellipse 1200 8.211614 comparing with: ellipse premium 500 8.211618 comparing with: ellipse premium 650 8.211621 comparing with: ellipse premium 800 8.211625 comparing with: ellipse premium 1200 8.211629 comparing with: Ellipse 600 8.211632 comparing with: Ellipse 750 8.211635 comparing with: Ellipse 1000 8.211639 comparing with: Ellipse 1500 8.211642 comparing with: Ellipse MAX 600 8.211646 comparing with: Ellipse MAX 850 8.211649 comparing with: Ellipse MAX 1100 8.211653 comparing with: Ellipse MAX 1500 8.211656 comparing with: Protection Center 420 8.211660 comparing with: Protection Center 500 8.211663 comparing with: Protection Center 675 8.211667 comparing with: Protection Station 500 8.211671 comparing with: Protection Station 650 8.211674 comparing with: Protection Station 800 8.211678 comparing with: Ellipse ECO 650 8.211681 comparing with: Ellipse ECO 800 8.211685 comparing with: Ellipse ECO 1200 8.211688 comparing with: Ellipse ECO 1600 8.211692 comparing with: 3S 450 8.211695 comparing with: 3S 550 8.211699 comparing with: 3S 700 8.211702 comparing with: 3S 750 8.211705 comparing with: Pulsar Evolution 500 8.211709 comparing with: Pulsar Evolution 800 8.211712 comparing with: Pulsar Evolution 1100 8.211716 comparing with: Pulsar Evolution 1500 8.211719 comparing with: Pulsar Evolution 2200 8.211723 comparing with: Pulsar Evolution 3000 8.211726 comparing with: Pulsar Evolution 3000 XL 8.211730 comparing with: Evolution 650 8.211733 comparing with: Evolution 850 8.211737 comparing with: Evolution 1150 8.211740 comparing with: Evolution S 1250 8.211744 comparing with: Evolution 1550 8.211748 comparing with: Evolution S 1750 8.211752 comparing with: Evolution 2000 8.211756 comparing with: Evolution S 2500 8.211760 comparing with: Evolution S 3000 8.211764 comparing with: 5P 650 8.211768 comparing with: 5P 850 8.211772 comparing with: 5P 1150 8.211776 comparing with: 5P 1550 8.211781 comparing with: PULSAR M 2200 8.211785 comparing with: PULSAR M 3000 8.211788 comparing with: PULSAR M 3000 XL 8.211791 comparing with: EX 2200 8.211793 comparing with: EX 3000 8.211795 comparing with: EX 3000 XL 8.211797 comparing with: Pulsar MX 4000 RT 8.211800 comparing with: Pulsar MX 5000 RT 8.211802 comparing with: Nova 500 AVR 8.211804 comparing with: Nova 600 AVR 8.211806 comparing with: Nova 625 AVR 8.211809 comparing with: Nova 1100 AVR 8.211811 comparing with: Nova 1250 AVR 8.211813 comparing with: Pulsar EXtreme 700C 8.211816 comparing with: Pulsar EXtreme 1000C 8.211818 comparing with: Pulsar EXtreme 1500C 8.211820 comparing with: Pulsar EXtreme 1500C CLA 8.211822 comparing with: Pulsar EXtreme 2200C 8.211825 comparing with: Pulsar EXtreme 3200C 8.211827 comparing with: Pulsar EX 700 RT 8.211829 comparing with: Pulsar EX 1000 RT 8.211831 comparing with: Pulsar EX 1500 RT 8.211834 comparing with: Pulsar EX 2200 RT 8.211836 comparing with: Pulsar EX 3200 RT 8.211838 comparing with: EX 5 RT 3:1 8.211840 comparing with: EX 7 RT 3:1 8.211843 comparing with: EX 11 RT 3:1 8.211845 comparing with: EX 5 RT 8.211847 comparing with: EX 7 RT 8.211849 comparing with: EX 11 RT 8.211851 comparing with: Galaxy 3000 10 kVA 8.211854 comparing with: Galaxy 3000 15 kVA 8.211856 comparing with: Galaxy 3000 20 kVA 8.211858 comparing with: Galaxy 3000 30 kVA 8.211869 Report descriptor retrieved (Reportlen = 2580) 8.211871 Found HID device 8.211875 Detected a UPS: EATON/Eaton 5PX 2000 8.211905 Path: UPS.PowerSummary.Country, Type: Feature, ReportID: 0x0b, Offset: 16, Size: 8, Value: 0 8.211921 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x06, Offset: 0, Size: 8, Value: 100 8.211933 Path: UPS.PowerSummary.RemainingCapacityLimitSetting, Type: Feature, ReportID: 0x12, Offset: 0, Size: 8, Value: 20 8.211964 Path: UPS.PowerSummary.RestartLevel, Type: Feature, ReportID: 0x0e, Offset: 0, Size: 8, Value: 0 8.237334 Path: UPS.BatterySystem.Battery.DesignCapacity, Type: Feature, ReportID: 0x23, Offset: 0, Size: 32, Value: 32400 8.237376 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x06, Offset: 8, Size: 32, Value: 932 8.237439 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 4 8.319873 Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x07, Offset: 8, Size: 16, Value: 53.8 8.319909 Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, ReportID: 0x0d, Offset: 8, Size: 16, Value: 48 8.342090 Path: UPS.BatterySystem.Battery.DeepDischargeProtection, Type: Feature, ReportID: 0x22, Offset: 0, Size: 8, Value: 1 8.342134 Path: UPS.PowerConverter.Input.[3].EnergySaving, Type: Feature, ReportID: 0x39, Offset: 0, Size: 8, Value: 0 8.377999 Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1 8.378017 ABM is enabled 8.415229 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 8.415242 ABM numeric status: 3 8.415245 ABM string status: floating 8.415271 Path: UPS.PowerConverter.Output.Efficiency, Type: Feature, ReportID: 0x42, Offset: 48, Size: 8, Value: 95 8.415285 Path: UPS.PowerSummary.iVersion, Type: Feature, ReportID: 0x10, Offset: 48, Size: 8, Value: 5 8.490865 Path: UPS.PowerSummary.PercentLoad, Type: Feature, ReportID: 0x07, Offset: 0, Size: 8, Value: 30 8.521849 Path: UPS.Flow.[4].ConfigPercentLoad, Type: Feature, ReportID: 0x16, Offset: 0, Size: 8, Value: 105 8.521903 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 8.521915 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 8.557999 Path: UPS.BatterySystem.Battery.Test, Type: Feature, ReportID: 0x24, Offset: 0, Size: 8, Value: 1 8.597604 Path: UPS.BatterySystem.Battery.TestPeriod, Type: Feature, ReportID: 0x25, Offset: 0, Size: 32, Value: 604800 8.629866 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 2 8.683107 Path: UPS.PowerConverter.Output.ApparentPower, Type: Feature, ReportID: 0x42, Offset: 16, Size: 16, Value: 611 8.720992 Path: UPS.Flow.[4].ConfigApparentPower, Type: Feature, ReportID: 0x75, Offset: 0, Size: 16, Value: 2000 8.721030 Path: UPS.PowerConverter.Output.ActivePower, Type: Feature, ReportID: 0x42, Offset: 0, Size: 16, Value: 504 8.757149 Path: UPS.Flow.[4].ConfigActivePower, Type: Feature, ReportID: 0x74, Offset: 0, Size: 16, Value: 1800 8.791903 Path: UPS.PowerConverter.Input.[1].AutomaticRestart, Type: Feature, ReportID: 0x73, Offset: 0, Size: 8, Value: 1 8.827857 Path: UPS.PowerConverter.Input.[3].StartOnBattery, Type: Feature, ReportID: 0x3a, Offset: 0, Size: 8, Value: 1 8.863855 Path: UPS.PowerConverter.Output.ForcedReboot, Type: Feature, ReportID: 0x43, Offset: 0, Size: 8, Value: 1 8.863900 Path: UPS.PowerSummary.PresentStatus.Switchable, Type: Feature, ReportID: 0x03, Offset: 32, Size: 8, Value: 1 8.899749 Path: UPS.PowerConverter.ConverterType, Type: Feature, ReportID: 0x4a, Offset: 0, Size: 8, Value: 1 8.899795 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 8.936108 Path: UPS.PowerConverter.Input.[3].PresentStatus.Used, Type: Feature, ReportID: 0x3b, Offset: 0, Size: 8, Value: 0 8.977620 Path: UPS.PowerConverter.Input.[1].PresentStatus.Used, Type: Feature, ReportID: 0x32, Offset: 32, Size: 8, Value: 1 8.977655 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 8.977674 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 8.977686 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 8.977691 ABM CHRG/DISCHRG legacy string status (ups.status): chrg 8.977709 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 8.977759 Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, ReportID: 0x02, Offset: 16, Size: 8, Value: 0 8.977777 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x02, Offset: 8, Size: 8, Value: 0 9.009108 Path: UPS.LCMSystem.LCMAlarm.[2].PresentStatus.TimerExpired, Type: Feature, ReportID: 0x5d, Offset: 8, Size: 8, Value: 1 9.009141 Path: UPS.PowerConverter.Input.[1].PresentStatus.Buck, Type: Feature, ReportID: 0x32, Offset: 8, Size: 8, Value: 0 9.009161 Path: UPS.PowerConverter.Input.[1].PresentStatus.Boost, Type: Feature, ReportID: 0x32, Offset: 0, Size: 8, Value: 0 9.009181 Path: UPS.PowerConverter.Input.[1].PresentStatus.VoltageOutOfRange, Type: Feature, ReportID: 0x32, Offset: 40, Size: 8, Value: 0 9.009202 Path: UPS.PowerConverter.Input.[1].PresentStatus.FrequencyOutOfRange, Type: Feature, ReportID: 0x32, Offset: 16, Size: 8, Value: 0 9.009221 Path: UPS.PowerSummary.PresentStatus.Good, Type: Feature, ReportID: 0x01, Offset: 32, Size: 8, Value: 1 9.009270 Path: UPS.PowerSummary.PresentStatus.FanFailure, Type: Feature, ReportID: 0x03, Offset: 16, Size: 8, Value: 0 9.049881 Path: UPS.BatterySystem.Battery.PresentStatus.Present, Type: Feature, ReportID: 0x27, Offset: 0, Size: 8, Value: 1 9.049911 Path: UPS.BatterySystem.Charger.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x27, Offset: 16, Size: 8, Value: 0 9.049926 Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooHigh, Type: Feature, ReportID: 0x27, Offset: 32, Size: 8, Value: 0 9.049977 Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooLow, Type: Feature, ReportID: 0x27, Offset: 40, Size: 8, Value: 0 9.050014 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 0 9.050033 Path: UPS.PowerSummary.PresentStatus.OverTemperature, Type: Feature, ReportID: 0x03, Offset: 24, Size: 8, Value: 0 9.050052 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x02, Offset: 24, Size: 8, Value: 0 9.050068 Path: UPS.PowerSummary.PresentStatus.EmergencyStop, Type: Feature, ReportID: 0x03, Offset: 8, Size: 8, Value: 0 9.050098 Path: UPS.PowerSummary.PresentStatus.ConfigurationFailure, Type: Feature, ReportID: 0x03, Offset: 0, Size: 8, Value: 0 9.079747 Path: UPS.PowerConverter.Output.PresentStatus.ShortCircuit, Type: Feature, ReportID: 0x49, Offset: 0, Size: 8, Value: 0 9.121877 Path: UPS.PowerConverter.Input.[1].Voltage, Type: Feature, ReportID: 0x31, Offset: 32, Size: 16, Value: 235.4 9.153124 Path: UPS.Flow.[1].ConfigVoltage, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 230 9.153172 Path: UPS.PowerConverter.Input.[1].Current, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 0 9.153252 Path: UPS.PowerConverter.Input.[1].Frequency, Type: Feature, ReportID: 0x31, Offset: 16, Size: 16, Value: 49.9 9.187874 Path: UPS.Flow.[1].ConfigFrequency, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 50 9.224882 Path: UPS.PowerConverter.Output.LowVoltageTransfer, Type: Feature, ReportID: 0x47, Offset: 0, Size: 16, Value: 160 9.261021 Path: UPS.PowerConverter.Output.LowVoltageBoostTransfer, Type: Feature, ReportID: 0x4e, Offset: 0, Size: 16, Value: 184 9.297144 Path: UPS.PowerConverter.Output.HighVoltageTransfer, Type: Feature, ReportID: 0x48, Offset: 0, Size: 16, Value: 294 9.333159 Path: UPS.PowerConverter.Output.HighVoltageBuckTransfer, Type: Feature, ReportID: 0x4d, Offset: 0, Size: 16, Value: 265 9.367778 Path: UPS.PowerConverter.Output.SensitivityMode, Type: Feature, ReportID: 0x4f, Offset: 0, Size: 8, Value: 0 9.403783 Path: UPS.PowerConverter.Output.ExtendedVoltageMode, Type: Feature, ReportID: 0x4c, Offset: 0, Size: 8, Value: 0 9.439757 Path: UPS.PowerConverter.Output.ExtendedFrequencyMode, Type: Feature, ReportID: 0x4b, Offset: 0, Size: 8, Value: 0 9.439947 Path: UPS.PowerConverter.Output.Voltage, Type: Feature, ReportID: 0x42, Offset: 80, Size: 16, Value: 235 9.476897 Path: UPS.Flow.[4].ConfigVoltage, Type: Feature, ReportID: 0x72, Offset: 0, Size: 16, Value: 230 9.476939 Path: UPS.PowerConverter.Output.Current, Type: Feature, ReportID: 0x42, Offset: 32, Size: 16, Value: 2.6 9.477006 Path: UPS.PowerConverter.Output.Frequency, Type: Feature, ReportID: 0x42, Offset: 56, Size: 16, Value: 49.9 9.477019 Path: UPS.Flow.[4].ConfigFrequency, Type: Feature, ReportID: 0x0d, Offset: 0, Size: 8, Value: 50 9.477032 Path: UPS.PowerConverter.Output.PowerFactor, Type: Feature, ReportID: 0x42, Offset: 72, Size: 8, Value: 82 9.518640 Path: UPS.OutletSystem.Outlet.[1].OutletID, Type: Feature, ReportID: 0x80, Offset: 8, Size: 8, Value: 0 9.552640 Path: UPS.OutletSystem.Outlet.[1].PresentStatus.Switchable, Type: Feature, ReportID: 0x81, Offset: 0, Size: 8, Value: 0 9.616020 Path: UPS.OutletSystem.Outlet.[1].ApparentPower, Type: Feature, ReportID: 0x83, Offset: 16, Size: 16, Value: 287 9.616067 Path: UPS.OutletSystem.Outlet.[1].ActivePower, Type: Feature, ReportID: 0x83, Offset: 0, Size: 16, Value: 285 9.616089 Path: UPS.OutletSystem.Outlet.[1].Current, Type: Feature, ReportID: 0x83, Offset: 32, Size: 16, Value: 1 9.616110 Path: UPS.OutletSystem.Outlet.[1].PowerFactor, Type: Feature, ReportID: 0x83, Offset: 48, Size: 8, Value: 99 9.616138 Path: UPS.OutletSystem.Outlet.[2].OutletID, Type: Feature, ReportID: 0x80, Offset: 24, Size: 8, Value: 1 9.616173 Path: UPS.OutletSystem.Outlet.[2].PresentStatus.Switchable, Type: Feature, ReportID: 0x81, Offset: 16, Size: 8, Value: 1 9.638885 Path: UPS.OutletSystem.Outlet.[2].PresentStatus.SwitchOn/Off, Type: Feature, ReportID: 0x82, Offset: 0, Size: 8, Value: 1 9.673788 Path: UPS.OutletSystem.Outlet.[2].RemainingCapacityLimit, Type: Feature, ReportID: 0x84, Offset: 0, Size: 8, Value: 0 9.711163 Path: UPS.OutletSystem.Outlet.[2].ShutdownTimer, Type: Feature, ReportID: 0x87, Offset: 0, Size: 16, Value: 65535 9.746891 Path: UPS.OutletSystem.Outlet.[2].StartupTimer, Type: Feature, ReportID: 0x8a, Offset: 0, Size: 16, Value: 3 9.746935 Path: UPS.OutletSystem.Outlet.[2].ApparentPower, Type: Feature, ReportID: 0x83, Offset: 72, Size: 16, Value: 282 9.746958 Path: UPS.OutletSystem.Outlet.[2].ActivePower, Type: Feature, ReportID: 0x83, Offset: 56, Size: 16, Value: 151 9.746980 Path: UPS.OutletSystem.Outlet.[2].Current, Type: Feature, ReportID: 0x83, Offset: 88, Size: 16, Value: 1.2 9.747001 Path: UPS.OutletSystem.Outlet.[2].PowerFactor, Type: Feature, ReportID: 0x83, Offset: 104, Size: 8, Value: 53 9.747021 Path: UPS.OutletSystem.Outlet.[3].OutletID, Type: Feature, ReportID: 0x80, Offset: 40, Size: 8, Value: 2 9.747055 Path: UPS.OutletSystem.Outlet.[3].PresentStatus.Switchable, Type: Feature, ReportID: 0x81, Offset: 32, Size: 8, Value: 1 9.747073 Path: UPS.OutletSystem.Outlet.[3].PresentStatus.Switchable, Type: Feature, ReportID: 0x81, Offset: 32, Size: 8, Value: 1 9.747093 Path: UPS.OutletSystem.Outlet.[3].PresentStatus.SwitchOn/Off, Type: Feature, ReportID: 0x82, Offset: 8, Size: 8, Value: 1 9.781677 Path: UPS.OutletSystem.Outlet.[3].RemainingCapacityLimit, Type: Feature, ReportID: 0x85, Offset: 0, Size: 8, Value: 0 9.819019 Path: UPS.OutletSystem.Outlet.[3].ShutdownTimer, Type: Feature, ReportID: 0x88, Offset: 0, Size: 16, Value: 65535 9.854902 Path: UPS.OutletSystem.Outlet.[3].StartupTimer, Type: Feature, ReportID: 0x8b, Offset: 0, Size: 16, Value: 6 9.854950 Path: UPS.OutletSystem.Outlet.[3].ApparentPower, Type: Feature, ReportID: 0x83, Offset: 128, Size: 16, Value: 94 9.854971 Path: UPS.OutletSystem.Outlet.[3].ActivePower, Type: Feature, ReportID: 0x83, Offset: 112, Size: 16, Value: 68 9.854992 Path: UPS.OutletSystem.Outlet.[3].Current, Type: Feature, ReportID: 0x83, Offset: 144, Size: 16, Value: 0.4 9.855013 Path: UPS.OutletSystem.Outlet.[3].PowerFactor, Type: Feature, ReportID: 0x83, Offset: 160, Size: 8, Value: 72 9.890032 Path: UPS.BatterySystem.Battery.Test, Type: Feature, ReportID: 0x24, Offset: 0, Size: 8, Value: 1 9.890058 Path: UPS.BatterySystem.Battery.Test, Type: Feature, ReportID: 0x24, Offset: 0, Size: 8, Value: 1 9.890066 Path: UPS.BatterySystem.Battery.Test, Type: Feature, ReportID: 0x24, Offset: 0, Size: 8, Value: 1 9.929275 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 9.965149 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 9.965184 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 9.965212 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 2 9.965228 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 2 9.965243 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 2 9.965259 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 2 9.965273 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 2 10.001170 Path: UPS.OutletSystem.Outlet.[2].DelayBeforeShutdown, Type: Feature, ReportID: 0x8d, Offset: 0, Size: 32, Value: 0 10.037284 Path: UPS.OutletSystem.Outlet.[2].DelayBeforeStartup, Type: Feature, ReportID: 0x90, Offset: 0, Size: 32, Value: 0 10.073446 Path: UPS.OutletSystem.Outlet.[3].DelayBeforeShutdown, Type: Feature, ReportID: 0x8e, Offset: 0, Size: 32, Value: 0 10.109287 Path: UPS.OutletSystem.Outlet.[3].DelayBeforeStartup, Type: Feature, ReportID: 0x91, Offset: 0, Size: 32, Value: 0 10.109328 upsdrv_initinfo... 10.109337 upsdrv_updateinfo... 10.360175 libusb_get_interrupt: Connection timed out 10.360200 Got 0 HID objects... 10.360216 Quick update... 10.393838 Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1 10.393848 ABM is enabled 10.431063 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 10.431075 ABM numeric status: 3 10.431078 ABM string status: floating 10.431086 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 10.431092 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 10.470311 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 10.470324 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 10.470329 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 10.470334 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 10.470337 ABM CHRG/DISCHRG legacy string status (ups.status): chrg 10.470342 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 10.470418 dstate_init: sock /var/run/nut/usbhid-ups-eaton-5px-1 open on fd 5 10.470427 upsdrv_updateinfo... 10.721106 libusb_get_interrupt: Connection timed out 10.721126 Got 0 HID objects... 10.721131 Quick update... 10.721139 Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1 10.721143 ABM is enabled 10.721147 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 10.721150 ABM numeric status: 3 10.721153 ABM string status: floating 10.721158 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 10.721164 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 10.721169 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 10.721173 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 10.721178 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 10.721182 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 10.721185 ABM CHRG/DISCHRG legacy string status (ups.status): chrg 10.721189 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 12.470584 upsdrv_updateinfo... 12.720842 libusb_get_interrupt: Connection timed out 12.720861 Got 0 HID objects... 12.720867 Quick update... 12.751293 Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1 12.751307 ABM is enabled 12.788896 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 12.788908 ABM numeric status: 3 12.788912 ABM string status: floating 12.826780 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 12.863031 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 12.900173 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 12.900185 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 12.900191 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 12.900199 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 12.900203 ABM CHRG/DISCHRG legacy string status (ups.status): chrg 12.900207 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 14.472173 upsdrv_updateinfo... 14.722859 libusb_get_interrupt: Connection timed out 14.722884 Got 0 HID objects... 14.722891 Quick update... 14.749145 Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1 14.749157 ABM is enabled 14.786472 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 14.786490 ABM numeric status: 3 14.786523 ABM string status: floating 14.824849 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 14.860478 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 14.898477 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 14.898544 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 14.898550 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 14.898555 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 14.898559 ABM CHRG/DISCHRG legacy string status (ups.status): chrg 14.898563 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 16.473763 upsdrv_updateinfo... 16.724399 libusb_get_interrupt: Connection timed out 16.724443 Got 0 HID objects... 16.724449 Quick update... 16.747058 Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1 16.747071 ABM is enabled 16.784236 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 16.784250 ABM numeric status: 3 16.784253 ABM string status: floating 16.822177 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 16.858555 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 16.895438 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 16.895459 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 16.895469 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 16.895479 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 16.895484 ABM CHRG/DISCHRG legacy string status (ups.status): chrg 16.895492 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 18.474146 upsdrv_updateinfo... 18.724923 libusb_get_interrupt: Connection timed out 18.724952 Got 0 HID objects... 18.724956 Quick update... 18.762579 Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1 18.762596 ABM is enabled 18.799640 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 18.799662 ABM numeric status: 3 18.799667 ABM string status: floating 18.838017 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 18.874026 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 18.911419 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 18.911470 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 18.911551 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 18.911562 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 18.911568 ABM CHRG/DISCHRG legacy string status (ups.status): chrg 18.911575 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 20.475753 upsdrv_updateinfo... 20.726863 libusb_get_interrupt: Connection timed out 20.726900 Got 0 HID objects... 20.726914 Quick update... 20.760427 Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1 20.760447 ABM is enabled 20.797526 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 20.797551 ABM numeric status: 3 20.797555 ABM string status: floating 20.836150 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 20.871759 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 20.909158 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 20.909198 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 20.909216 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 20.909240 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 20.909248 ABM CHRG/DISCHRG legacy string status (ups.status): chrg 20.909256 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 22.477327 upsdrv_updateinfo... 22.728159 libusb_get_interrupt: Connection timed out 22.728181 Got 0 HID objects... 22.728185 Quick update... 22.758007 Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1 22.758018 ABM is enabled 22.795300 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 22.795314 ABM numeric status: 3 22.795318 ABM string status: floating 22.833432 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 22.869423 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 22.906797 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 22.906815 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 22.906827 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 22.906835 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 22.906841 ABM CHRG/DISCHRG legacy string status (ups.status): chrg 22.906846 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 24.478878 upsdrv_updateinfo... 24.729082 libusb_get_interrupt: Connection timed out 24.729108 Got 0 HID objects... 24.729123 Quick update... 24.755833 Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1 24.755842 ABM is enabled 24.793278 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 24.793308 ABM numeric status: 3 24.793314 ABM string status: floating 24.831278 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 24.867513 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 24.904643 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 24.904658 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 24.904664 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 24.904669 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 24.904672 ABM CHRG/DISCHRG legacy string status (ups.status): chrg 24.904683 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 26.479712 upsdrv_updateinfo... 26.730527 libusb_get_interrupt: Connection timed out 26.730547 Got 0 HID objects... 26.730552 Quick update... 26.753828 Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1 26.753836 ABM is enabled 26.790729 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 26.790742 ABM numeric status: 3 26.790746 ABM string status: floating 26.829004 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 26.865102 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 26.902101 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 26.902129 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 26.902134 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 26.902140 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 26.902144 ABM CHRG/DISCHRG legacy string status (ups.status): chrg 26.902150 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 28.480219 upsdrv_updateinfo... 28.730685 libusb_get_interrupt: Connection timed out 28.730705 Got 0 HID objects... 28.730711 Quick update... 28.769591 Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1 28.769605 ABM is enabled 28.806410 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 28.806425 ABM numeric status: 3 28.806430 ABM string status: floating 28.844661 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 28.880694 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 28.918039 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 28.918057 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 28.918067 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 28.918101 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 28.918106 ABM CHRG/DISCHRG legacy string status (ups.status): chrg 28.918113 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 30.481806 upsdrv_updateinfo... 30.732316 libusb_get_interrupt: Connection timed out 30.732335 Got 0 HID objects... 30.732340 Quick update... 30.767207 Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1 30.767220 ABM is enabled 30.804256 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 30.804271 ABM numeric status: 3 30.804276 ABM string status: floating 30.842794 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 30.878642 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 30.915760 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 30.915789 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 30.915795 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 30.915800 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 30.915803 ABM CHRG/DISCHRG legacy string status (ups.status): chrg 30.915807 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 32.482501 upsdrv_updateinfo... 32.733127 libusb_get_interrupt: Connection timed out 32.733148 Got 0 HID objects... 32.733152 Quick update... 32.764912 Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1 32.764926 ABM is enabled 32.801953 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 32.801967 ABM numeric status: 3 32.801970 ABM string status: floating 32.840199 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 32.876214 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 32.913253 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 32.913272 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 32.913278 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 32.913283 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 32.913287 ABM CHRG/DISCHRG legacy string status (ups.status): chrg 32.913291 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 34.484081 upsdrv_updateinfo... 34.735026 libusb_get_interrupt: Connection timed out 34.735045 Got 0 HID objects... 34.735049 Quick update... 34.762868 Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1 34.762881 ABM is enabled 34.799901 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 34.799914 ABM numeric status: 3 34.799919 ABM string status: floating 34.838031 Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0 34.873920 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0 34.911033 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 34.911055 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0 34.911065 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1 34.911074 Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3 34.911079 ABM CHRG/DISCHRG legacy string status (ups.status): chrg 34.911086 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0 Cheers, James.
signature.asc
Description: Message signed with OpenPGP
_______________________________________________ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser