Resolved here too..

On Tue, Apr 24, 2018 at 7:30 AM Phil Lavin via Outages <[email protected]>
wrote:

> Those prefixes had been withdrawn now – traffic is flowing correctly again
> for us. If that was the cause, I suspect things are back to rights for
> everyone now?
>
> One wonders why HE doesn’t apply filters on a peer with 20 legit prefixes…
>
>
>
> *From:* Outages <[email protected]> *On Behalf Of *Joseph B via
> Outages
> *Sent:* 24 April 2018 13:56
>
>
> *To:* [email protected]
> *Subject:* Re: [outages] Google 8.8.8.8 Resolution of Route53 domains
>
>
>
>
>
> Tue Apr 24 11:05:41 UTC onwards one of Hurricane Electric's peers AS10297 
> started
> advertising the following subnets via HE.
>
>
>
> 205.251.192.0
>
> 205.251.193.0
>
> 205.251.195.0
>
> 205.251.197.0
>
> 205.251.199.0
>
>
>
> These are all Amazon subnets, usually originated as part of /23s and
> seemingly host a fair bit of AWS Route53.
>
>
>
> If you (or your DNS resolver) are a HE transit customer you will be
> impacted the most.
>
>
>
> Cheers,
>
>
>
> Joseph
>
>
>
>
>
> On Tue, Apr 24, 2018, at 9:50 PM, Phil Lavin via Outages wrote:
>
> This doesn’t feel right, though I’ll admit I’ve never checked before. Our
> only route to ns-163.awsdns-20.com (205.251.192.163) is through HE:
>
> inet.0: 757581 destinations, 2107440 routes (757301 active, 0 holddown,
> 522 hidden)
>
> + = Active Route, - = Last Active, * = Both
>
> 205.251.192.0/24   *[BGP/170] 01:12:08, localpref 70
>
>                       AS path: 6939 10297 I, validation-state: unverified
>
>                     > to 216.66.90.21 via ge-1/0/5.0
>
> AS10297 is eNET inc. Is this expected?
>
>
>
> *From:* Outages <[email protected]> *On Behalf Of *Phil Lavin
> via Outages
> *Sent:* 24 April 2018 13:04
> *To:* [email protected]
> *Subject:* Re: [outages] Google 8.8.8.8 Resolution of Route53 domains
>
>
>
> Looks more specific to AWS than it does to Google+AWS. Can’t resolve
> against some of AWS’s NS directly:
>
> phil@phil-debian:~$ dig cloudcall.com IN A @ns-163.awsdns-20.com
>
> ; <<>> DiG 9.10.3-P4-Debian <<>> cloudcall.com IN A @ns-163.awsdns-20.com
>
> ;; global options: +cmd
>
> ;; connection timed out; no servers could be reached
>
>
>
> *From:* Outages <[email protected]> *On Behalf Of *Phil Lavin
> via Outages
> *Sent:* 24 April 2018 12:56
> *To:* [email protected]
> *Subject:* Re: [outages] Google 8.8.8.8 Resolution of Route53 domains
>
>
>
> Yeh. Still digging into it.
>
>
>
> *From:* Outages <[email protected]> *On Behalf Of *Zach Hanna
> via Outages
> *Sent:* 24 April 2018 12:54
> *To:* [email protected]
> *Subject:* [outages] Google 8.8.8.8 Resolution of Route53 domains
>
>
>
> Anyone else seeing SERVFAIL for route53-hosted domains trying to resolve
> with Google DNS?
>
> *_______________________________________________*
>
> Outages mailing list
>
> [email protected]
>
> https://puck.nether.net/mailman/listinfo/outages
>
>
> _______________________________________________
> Outages mailing list
> [email protected]
> https://puck.nether.net/mailman/listinfo/outages
>
_______________________________________________
Outages mailing list
[email protected]
https://puck.nether.net/mailman/listinfo/outages

Reply via email to