Latest update from AT&T:
AT&T Corporate Real Estate teams are now gathering on site after pausing work last night due a fire that reignited on site around midnight. The Fire Marshall has joined the AT&T team to provide official approval to proceed. Last night, the teams were able to accomplish testing the busbar, placing the temporary generators, completing power cabling, and opening all the breakers on the individual floors. It is estimated that this round of power related work is about 75% complete. The target is for energizing is 1200 CST. A partial analysis by the AT&T Structural Engineer initial found no concrete or steel damage that caused major concern. Once team re-engage this morning, they will complete their full analysis and ensure it is safe for restoration crews to proceed. AT&T Mechanical Engineers have confirmed there is roughly 3 feet of water in the basement with potential damage to mechanical equipment in that area. It is also suspected that commercial power may not be available for some time and as a result power will come from AT&T and Tennessee Emergency Management Agency generators. Additional technician support will be made available rotating over a 24 hour period. Core CBB teams continue to work on the secondary plan to reroute around the Nashville 2nd Ave location. They had some success this morning at 05:05 CT when core connectivity was established for the Winchester, KY office. Partial 911 connectivity has been restored in that specific area. Work will continue on the CBB reroute plans in several locations around the Southeast Region. We have installed a SatCOLT positioned in the area of the CO NSVLTNMT building and is up and taking traffic to aid in communication. The secondary SatCOLT arrived and has been turned up to provide additional coverage. The next update will be issued at approximately 13:00 CT, unless there is a significant change in status On Fri, Dec 25, 2020, 7:49 PM Ross Tajvar <r...@tajvar.io> wrote: > Got this internally, sharing here: > > Here is the update from AT&T: > > > > The front 1/3rd of their building is structuraly damaged. That includes > fiber entry. > > They have no power and there is major flooding on all floors including > the basement. > > The Fire Department is en route with pump trucks to help with the > flooding. > > They have Building Engineers and Electricians on the way to look into > the structure and getting power turned on. > > They have 2 850KW generators on the way and 2 1MW generators on standby. > > They have new A/C Chillers on the way (Existing Chiller plant was > destroyed) > > On Fri, Dec 25, 2020 at 3:38 PM Jay R. Ashworth via Outages < > outages@outages.org> wrote: > >> ----- Original Message ----- >> > From: "Kurt Duncan via Outages" <outages@outages.org> >> >> > Anyone else seeing phone or internet issues due to the AT&T building >> being >> > damaged by the explosion in Nashville ? >> >> Let's please continue to confine replies here to specific information >> about >> network impacts, and keep the speculation threads to -discuss; thanks to >> whomever already started that thread. I would name them, but the >> caffeine >> hasn't kicked in yet. >> >> If you're in that building in Nash, we'll be particularly interested in >> anything you're allowed to tell us in between bailing. >> >> Cheers, >> -- jr '<admin/>' a >> -- >> Jay R. Ashworth Baylink >> j...@baylink.com >> Designer The Things I Think RFC >> 2100 >> Ashworth & Associates http://www.bcp38.info 2000 Land >> Rover DII >> St Petersburg FL USA BCP38: Ask For It By Name! +1 727 647 >> 1274 >> _______________________________________________ >> Outages mailing list >> Outages@outages.org >> https://puck.nether.net/mailman/listinfo/outages >> >
_______________________________________________ Outages mailing list Outages@outages.org https://puck.nether.net/mailman/listinfo/outages