Open the doors?

On January 14, 2024 9:52:24 PM EST, Mike Hammett via Outages 
<outages@outages.org> wrote:
>
>IBX: CH1 
>IBX Address: 350 E Cermak Rd, Chicago, 60616 
>Number: INC0025932 
>Date and Time of Occurrence: 2024-01-14 08:20:49 Site Local Time 
>
>
>To view the incident and its updates, please use Service Insight. 
>New update on Incident INC0025932: Equinix IBX Site Staff reports that 
>temperatures have stabilized with an average temperature of 120 F degrees. One 
>chiller is now fully operational, and another chiller is online but operating 
>at reduced capacity. Equinix IBX Critical Facility Engineers continue to work 
>on restoring the required 4-out-of-6 chillers to return cooling back to normal 
>operations. Portable chillers are currently enroute with an estimated arrival 
>time of 21:00 Site Local Time. Upon arrival, IBX Critical Facility Engineers 
>and our vendor partner will work diligently to get the portable chillers 
>online as quickly as possible. We will send another update once the portable 
>chillers are operational. 
>
>
>If not already implemented, Equinix site staff highly recommends that 
>customers power down non-essential loads within the data center and/or 
>transfer those operations to backup sites to assist with efforts at lowering 
>the temperature within the facility. 
>
>
>The severe weather in the Chicago area, contributing to the initial failure, 
>continues to hamper efforts at resolution, but our teams are working 
>diligently to resolve the issue as quickly as possible. IBX Critical Facility 
>Engineers continue to supply outside air to decrease the collocation area's 
>temperature, and all fans have been deployed to support cooling the IBX. 
>• Service Offering: CH1 - Location - Floor 
>• Affected Assets: 05 
>• Asset Condition: Temperature above operating range 
>• Situation status: Under investigation 
>
>
>The next update will be provided in approximately 30 minutes or earlier if 
>available. 
>
>
>
>
>
>----- 
>Mike Hammett 
>Intelligent Computing Solutions 
>
>Midwest Internet Exchange 
>
>The Brothers WISP 
>
>----- Original Message -----
>
>From: "Mike Hammett via Outages" <outages@outages.org> 
>To: "outages" <outages@outages.org> 
>Sent: Sunday, January 14, 2024 2:04:51 PM 
>Subject: [outages] Equinix CH1 Overheating 
>
>
>Equinix CH1 is overheating due to some chiller failures. The vendor is on-site 
>troubleshooting. Ambient temperature is currently 28 degrees higher than 
>normal. 
>
>
>
>
>----- 
>Mike Hammett 
>Intelligent Computing Solutions 
>
>Midwest Internet Exchange 
>
>The Brothers WISP 
>
>
>_______________________________________________ 
>Outages mailing list 
>Outages@outages.org 
>https://puck.nether.net/mailman/listinfo/outages 
>

-- 
Sent from my Android device with K-9 Mail. Please excuse my brevity.
_______________________________________________
Outages mailing list
Outages@outages.org
https://puck.nether.net/mailman/listinfo/outages

Reply via email to