Hi Randall,

Through long experience I have found that only the original Lead Acid AGM or 
Gel Cells that come in a brand new UPS have anywhere close to 5 years in them.  
Any time I have replaced a set of these in a UPS no matter how much money I 
have spent on whatever kind of batteries I've never gotten 5 years again.   At 
most it's been 3 years.  Sometimes 2 years.   Maybe the Lithium batteries are 
going to be better but those UPSes are too spendy for my budget, yet.

Now, the "textbook" answer from APC is that their SmartUPSes have a 
"calibration mode"   The way this works is, you put a set of fresh batteries in 
an SmartUPS.  Then you let them completely charge for a day or so.  Then you 
run a calibration test from the control panel of the UPS.  The test puts the 
batteries under load and starts a clock and then starts checking the voltage of 
the batteries.  When the battery voltage drops below 11.2 volts or some such 
then the test stops.  The UPS then "learns" the battery's "discharge curve" and 
changes a calibration factor.  The factor allows the UPS to tell how long the 
battery is going to last when put under load.

The SmartUPS then weekly self-tests the batteries by putting them under load 
for a few seconds.  Based on what level the battery voltage drops as a result 
of being put under load the UPS is then supposed to be able to predict how long 
the batteries are going to last in a real blackout.

When the batteries are a year old then you are supposed to run a calibration 
test again which figures out if the calibration factor needs to be changed.

Now, I do not know if this testing by APC is really able to predict how long an 
actual battery lasts or whether it's snake oil.

The articles I have read on lead acid batteries all seem to say some basics.  
First point is that if the battery is overcharged then the electrolyte starts 
boiling off the water. (ie: converting the water into free hydrogen and oxygen) 
 With a car starting battery this is not a problem since if you just check the 
electrolyte level and keep the battery topped off, then you are fine.  With a 
sealed lead acid battery then the electrolyte paste has some magic chemical in 
it that supposedly "recombines the hydrogen and oxygen back into water"  

The second point is that temperature matters greatly.  Here is the output of 
apcupsd from my 14 year old SmartUPS:

root@officeserver:/usr/home/tedm # apcaccess
APC      : 001,042,1055
DATE     : 2026-06-10 22:29:42 -0700
HOSTNAME : officeserver
VERSION  : 3.14.14 (31 May 2016) freebsd
UPSNAME  : APCUPS
CABLE    : USB Cable
DRIVER   : MODBUS UPS Driver
UPSMODE  : Stand Alone
STARTTIME: 2025-12-17 05:22:44 -0800
MODEL    : Smart-UPS 1500
STATUS   : ONLINE
LINEV    : 120.9 Volts
LOADPCT  : 29.2 Percent
LOADAPNT : 22.7 Percent
BCHARGE  : 100.0 Percent
TIMELEFT : 56.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME  : 0 Seconds
OUTPUTV  : 120.2 Volts
DWAKE    : 0 Seconds
DSHUTD   : 0 Seconds
ITEMP    : 27.0 C
BATTV    : 27.2 Volts
LINEFREQ : 60.0 Hz
OUTCURNT : 2.75 Amps
LASTXFER : Automatic or explicit self test
NUMXFERS : 7
XONBATT  : 2026-06-03 07:45:32 -0700
TONBATT  : 0 Seconds
CUMONBATT: 46 Seconds
XOFFBATT : 2026-06-03 07:45:41 -0700
LASTSTEST: 2026-06-03 07:45:33 -0700
SELFTEST : OK
STATFLAG : 0x05000008
MANDATE  : 2012-11-03
SERIALNO : AS1244115771
BATTDATE : 2023-12-14
NOMOUTV  : 120 Volts
NOMPOWER : 1000 Watts
NOMAPNT  : 1440 VA
FIRMWARE : UPS 15.0 / 00.5
END APC  : 2026-06-10 22:30:23 -0700
root@officeserver:/usr/home/tedm #

You will notice that there is an internal temp there.  This is because this 
model of UPS has an internal temperature sensor.  You will also notice that 27C 
is at the top upper limit of ideal operating temperature.  This model of UPS 
has 100% steel case and this particular UPS is sitting on the concrete floor of 
my basement so it's as cold as it can get yet there's still heat in the UPS.

You will also note that the battery date is 2023.  This is because when I last 
changed the batteries in this UPS I configured that date into the NVRAM of the 
UPS.

You will note the load % is about 30%.   This is around the minimum amount of 
load needed for an adequate self-test.  Too little load and the UPS will not be 
able to drain the batteries at all during a 3 second self-test and thus will 
not be able to get usable data regarding the battery.

You will also note "timeleft" is 56 minutes.
]
I think that it is probably not possible for a 3 year old sealed lead acid 
battery set to power a 2.75 amp load plus the inverter power loss for an hour.  
The ridiculous timeleft, the excessive heat, really point to the beginnings of 
thermal runaway.  These batteries are close to the end of their life - even 
though the UPS self test has NOT caught this yet.  They now have significant 
internal resistance and are generating excessive heat in the UPS   I should 
replace them.
  
Ted

-----Original Message-----
From: PLUG <[email protected]> On Behalf Of American Citizen
Sent: Wednesday, June 10, 2026 5:37 PM
To: [email protected]
Subject: [PLUG] hammered by sudden UPS power failure during a key backup

To all

I am struggling to recover from a very bad power failure during a key upgrade 
from my OS openSuse Leap 15.6 to Leap 16.0 upgrade.

My UPS unit completely clicked off right during the backup.

It has been several hours now and I am trying to carefully pick up all the 
pieces and verify that I did NOT lose any data.

My question to all of you is simple:

How can you tell the health of the lead-acid batteries in your UPS unit? 
>From what I can gather, this cannot be done live via any linux operations.

My lead acid batteries were shot, and bulging out their case.

Yes I was aware that I had 5 years time on these back up lead-acid batteries 
and was risking total failure, which actually occurred this afternoon for me.

How do you keep on top of the UPS units so you don't have a rather foolish 
incident like mine today?