Allan:

We recently experienced some problems charging a new set of IBE batteries with XW equipment. The apparent solution was reached just before I left for a back packing trip so I did not have time to post the results. Apparently, the flags on the IBE batteries developed a talcum powder like deposit between the flags and the cables, in spite of being cleaned and sealed recently. Re-cleaning them improved charging and discharging. We may have a defective terminal sealant product. We reapplied the same product because that is what we had on a Saturday and we want to know if we need to discontinue use of it. I will post further results.

In the meantime, we are learning that higher equalize voltages on VLA batteries is better. We theorize that industrial chargers of the type that are not micro-processor controlled allow higher voltages to occur during charging. Battery industry techs are familiar with these devices but may not realize that they are not as precise at voltage regulation as a modern inverter/charger. The batteries like these higher voltages and don't get them with your XW or VFX inverter. This is just a theory and we are working to verify it.

William Miller



At 10:53 AM 8/3/2008, you wrote:
Wrenches,
Thank you for the whole set of responses.

I haven't been to the site yet, but plan to stop there this week. As the
symptoms are not easily explained, I wanted to put the problem out for ideas
here first, to reduce the chance of missing something. I will report back
with what I learn.

I will first check whether the 0.4 V discrepancy is related to battery
temperature. It seems to me that the simplest way to do this is to check the
MX60 settings during equalization. If the measured voltage is at the MX60's
temperature-compensated EQ voltage, then a warm environment is the apparent
cause of the reduced voltage.


_______________________________________________
List sponsored by Home Power magazine

RE-wrenches@lists.re-wrenches.org

http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to