Hi William,

That is the way to do it. The inverter controls the generator automatically, based on battery voltage and / or current. The generator can be started manually whenever desired. The inverter (critical) loads will also be fed by the gen-set through the internal transfer switch on the inverter, while batteries are being charged.

Drake


At 09:46 PM 11/24/2008, you wrote:
Friends:

I am bidding an installation in which the customer owns a whole house generator. The generator is 30 KVA and we will be installing a 4.5 or 6.0 KVA XW system. Obviously, the inverter will not power the entire house. If we segregate the non-critical loads and connect them to a grid-fed panel, the generator will not power them. If we let the generator run every time there is an outage, this negates the need for a inverter system. What to do?

The transfer switch sends a two wire start signal to the generator upon a grid outage. After the transfer switch senses generator voltage, it effects a transfer.

My brainstorm is to intercept that two wire start signal. I will connect it instead to the XW inverter. We will segregate the loads, feeding the critical loads from the XW and the Non-critical loads from the output of the transfer switch. In the case of a grid outage, the critical loads will receive uninterrupted power. The Non-critical loads will not have power unless the generator is started by the XW. Once the XW (or the home owner) starts the generator, the transfer will occur. We will put a control panel in the house so the home-owner can start the generator if the No-critical loads are needed.

This seems clever to me, but I am biased.  Am I missing something???


William Miller



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
740-856-9648

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to