Hi Geoff,

Nice heads up on the SI needing to be “set up” prior to commissioning.

We are getting closer to a similar design ourselves. We have a SB7000US being 
fed by 36 Sanyo Hit Power 200’s on the drawing board that we are going to feed 
into a grid tie inverter system. Right now I am convinced that the SI5048’s 
will need to be paired up in order to feed this amount of current back through 
them to the grid if there aren’t any loads on in the residence, unless someone 
can let me know that this is not the case. 

I envision each SI requiring its own manual transfer switch between it and the 
grid, feeding the dedicated loads AC subpanel in case we need to pull it off 
the wall for servicing. Is this typical in your designs? Rethinking this if one 
SI is down for repairs the entire AC sub panel will need to be fed by the grid 
so there is a balanced 240VAC signal to it.

We are looking into the new East Penn Deka Unigy ll sealed batteries. They seem 
to be a good deal less money than the GNB’s.  Anyone have any experience with 
these? 

With two SI5048’s sucking on this battery bank there is the possibility of some 
serious current transfer taking place. We are proposing an absolute minimum 
battery size that can go full load draw down for three hours, to 50% DOD, my 
inclination is to make this 6 hours. At 3 hours we would need a 500 amp hour 
battery. What are others doing about battery sizing in this scenario? (our 
client hasn’t revealed what loads he wants to back up unfortunately so we are 
approaching this in this manner)

Right now we are still in the dark as to whether or not there will be a gen set 
involved. 

I do know a WebBox will be interfaced between the SI’s and the SB’s.

Thanks for the continuing discussion on this thread and Happy Thanksgiving to 
one and all.

 

Sincerely,

Chris Worcester
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
www.solarwindworks.com <http://www.solarwindworks.com/> 
[EMAIL PROTECTED]
"Proven Energy Solutions"

 

From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Geoff Greenfield
Sent: Wednesday, November 26, 2008 7:28 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] More on AC coupling - SI and SB

 

Matt-

 

What is your prefered/recomended way to address the 240 VAC SB series (we 
typically dont want to use a bunch of 700s or 1800s) and the 120 VAC SI series? 
 We used a pair of Outback PSX-240s but that was extra work/cost.  Other 
(larger) transformers? Torroid coil? Eaton? I'm surprised SMA doesnt have a 
nice interface worked out for the North American market...

 

Also wrenches... if you go down this route, invest the time ahead of time on 
learning/preping for the set up etc for SI in this application.  It is not out 
of the box ready to go, but involves a software upgrade, laptops and the right 
patch cord (an issue if you are 5 hours away...).

For a brighter energy future,

Geoff Greenfield
Founder and CEO
Third Sun Solar & Wind Power Ltd.
340 West State Street, Unit 25
Athens, OH 45701

740.597.3111     Fax 740.597.1548
www.Third-Sun.com

Clean Energy - Expertly Installed







----- "Tump" <[EMAIL PROTECTED]> wrote: 
> 

Matt, I have long been interested in installing the SMA SI & SBs but I have a 
VERY tough time selling $9ks worth of inverters, just to get things started.

In the system below I would not of hesitated in installing the SMA SI & SB! I 
too agree that w/this type of scenario described below, I  would have given 
quite a bit of thought to using the SMAs. Can't beat the battery charging, no 
charge controllers & expandability.

 Please if there is someone out there that has had experience w/ the SMA SI & 
SB let us know if it is all that it is cracked up to be!

With passport in hand, I offer my help if someone out there  has a large system 
like this, that will be using the SI & SB/WB  type of set up.

TUMP

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Matt Tritt
> Sent: Tuesday, November 25, 2008 9:21 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] More on AC coupling
> 

I am curious as to why OutBacks were used for this system instead of using 
SunnyIslands and SunnyBoys? From what I can tell about the SI system, virtually 
no aspect of battery charging, auto gen-start/stop, and interactive inverter 
control has been overlooked - or remains to be engineered in the field by the 
installer. Because SunnyIslands have the ability to "talk" to Sunny (or 
Windy)Boys, excess energy is taken care of by "integrated load shedding" - no 
need for multiple relays, dumpoads and voltage sensors. :-) The only limitation 
to these systems (and only in 60 Hz land) is a maximum of 20 kW single, and 15 
kW three phase per autonomous load. I really like the flexibility of being able 
to connect all AC inputs on the same line, as well as having the option to do 
direct battery charging from a DC source (as long as you use a shunt to measure 
current).
> I know this doesn't answer your questions, but for similar applications in 
> the future it would be good to take a close look at the SunnyIsland system. 
> They're cool.
> Matt T
> Mark Dickson wrote: 

> 

Hello Wrenches,

On the heels of the previous thread:

We just got finished installing a system that utilizes an Outback Quad stack 
and a 5.2kW array coupled to the AC panel via a Fronius IG5100--due to a long 
home-run.  The VFX’s are wired into the home in their traditional manner, 
providing the “grid” for the Fronius.  As the solar comes in, excess power not 
used in the home back feeds the batteries through the VFX’s.  I have a series 
of relays operating dump loads and finally a power cut-off for when the 
batteries reach critical level.  We installed the system yesterday and turned 
it on for a test run (then back off to power it up in 2009 for the ITC’s)—it 
worked great!

I have a couple questions for you all:

*       Seems how we are back feeding the inverters and forfeiting their charge 
control, where would you set the dump loads to kick on? 

*       For now I have them set at: 1st load to kick on at float voltages, 2nd 
to kick on at bulk voltages and 3rd to kick the solar power off at the EQ 
voltages.  Does this make sense?  The bank is made up of Rolls 4ks-25ps 
batteries. 

*       Following a recent discussion on the Wrenches list with a similar 
system:  Do I need to worry about back feeding the generator if it is runnin in 
the morning when the sun comes up?  Do I need a relay that will shut it down 
when solar comes on line? 
*       I plan on setting the Absorb and Float set times to a miimum.  Would 
you recommend this? 

Thanks for your input!

Mark Dickson

Oasis Montana Inc.






  _____  



 
_______________________________________________
List sponsored by Home Power magazine
 
List Address: RE-wrenches@lists.re-wrenches.org
 
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/> 
 
  





  _____  



 
 
Internal Virus Database is out of date.
Checked by AVG - http://www.avg.com <http://www.avg.com/>  
Version: 8.0.175 / Virus Database: 270.9.4/1794 - Release Date: 11/17/2008 8:48 
AM
 
  


> _______________________________________________ List sponsored by Home Power 
> magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: 
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules 
> & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: 
> www.members.re-wrenches.org 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to