Hello Jay and Tump,

I set up a mate for autostart six weeks ago. Before leaving the remote job site I started the genny from the mate by raising the two minute start voltage above the current battery voltage and waited two minutes. The genny started confirming that the AGS was functioning properly.

I recently talked with the mostly savvy client and he claims that the generator has never autostarted and that the battery voltage remains below the ags 2h and 24h settings for extended periods of time without the genny starting. He has been starting the genny manually from the power center to get the batteries charged.

Is this the problem that you have seen? It was only a two hour drive each way in October when the short cut through the mountains was open. Now I am looking at a 3-4 hour drive each way over icey roads otherwise I would visit the site with a spare mate without hesitation.

Is the time and date loss a problem in conjunction with the ags issue?

Jeff


Thirsty Lake Solar
PO Box 538
Eureka, MT 59917
Jeff Wongstrom
NABCEP Certified Solar Installer
406-889-5324
thirstylakesolar.com



On Dec 15, 2008, at 9:33 PM, jay peltz wrote:

Hi Mark,

No this issue I've had is that the mate just won't start the generator with usual symptoms of system shut down.

But when I go to the mate and press start, generator starts right up. All setpoints are correct. Replace the mate, and all is good, again same setpoints.

So I can only surmise the problem is a mate issue that I've yet to track down, but have a fix.


jay

peltz power

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to