Keith:

No matter how you slice it, every breaker panel and every conductor in the feeder from the inverter to the meter must meet the 120% rule. You can not dedicate one panel as an "AC Combiner" and exceed the 120% rating on that panel only. It does not matter if the source is one inverter or 10 inverters. You either meet the 120% requirement from section (B) or you supply a supply side tap as allowed in (A).

William Miller


At 02:40 PM 2/9/2009, you wrote:
Hello

With the growth of the solar industry coupled with the generous incentives now offered on fed part of the equation, we are seeing some trends here and wondering what the approach has been in other areas. What kind of feedback are you receiving from the AHJ?

There are some integrators who now are installing "systems" meaning, multiple small inverters that are married to smaller arrays as opposed to one large array with one large inverter.

So, it is quite conceivable to have, for example, 3- 3000 W SMA inverters on a customers home. So, the point of connection issues arise. When you look at 690.64B, it speaks to the 120% of the busbar rating.

What are folks doing in other areas, for this above example to address the mechanical/electrical challenges associated with this situation, when if you had 1- 200 amp residential service? There is alot of discussion, like installing a 125 amp rated subpanel; interuppting the feeder from the electric service and installing a 225 amp panel with a higher rated buss (hard to find or custom made thru Cutler Hammer or others) etc.

We can also see a trend using the enphase products as well, but not as much pronounced. It could be conceivable for a client to want to build their system up over a few years and have 15, 175 watt panels on a circuit (2P15 amp) and grow the system up to lets say, 45, 175 watt panels (3-2P15 amp). Same situation, different inverter manufacturer. My sense is this trend will continue for the forseeable future, and alot of wrenches will find orphaned systems out there and we should look at ways to address point of connection issues that are bound to present themselves.

Thanks

Keith

Please note new e-mail address and domain:

William Miller
Miller Solar
Voice :805-438-5600     Fax: 805-438-4607
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to