David,
There will be less than a 1 volt drop in 36 feet of 10 AWG at the 11 amps you get from the Evergreen modules. I don't think anyone will notice.
David

David Katz



David Palumbo wrote:

Does the following series string wiring cause a problem? With (18) Evergreen ES-A 205's (low voltage modules 18.4Vmp) in series feeding a grid tie inverter with a long series connector in the middle of the string. (2) Top Of Pole 9 module mounts with the series connection from module #8 on the first pole to module #9 on the second pole. This MC cable connection would be, about, 36 feet in length to go 10' down the pole below grade 18" for 13' and back up the second pole 10' (in conduit all the way) .

Will this extra long series wire cause problems?

I could use other modules of course but that would raise the cost per watt by 70 cents.

Dave