Jeff,

It is somewhat possible to use all ten inverters, but with some severe
limitations.  The best solution depends upon exactly what you've got, and
what your client needs.

The joy begins with the fundamental limitation of G series inverters to
Classic Stack only.  They parallel on the grid side, but normally need
totally different output panels, battery banks and PV input.  You'd think
you could break up your 10 inverters into 5 "systems" (each on its own Hub4
and RTS) sharing a common battery, feeding 5 separate protected loads
panels.  But unfortunately no, it's not quite that easy.

The issue is, at some point a month or so down the line the grid power
drops, and the system begins to draw down the batteries.  After grid power
resumes, all 5 "systems" begin to charge the shared battery bank.  No
problem, eh?  What's to worry?  Well, eventually one of those inverter pair
"systems" will see the battery as being full, and switch back to GT mode.
It tries to sell down the batteries.  However, the other handful of systems
think the battery isn't quite full, and they ramp their charging back up.
Eventually the client wonders why his meter no longer turns backwards, and
calls you back out.

IF you have 6kW or less of renewable input, I'd suggest leave the system
wired as it is (two G series selling back, 8 standard FX in Outback Stack to
a separate protected big loadcenter) but disable AC charging capability on
the 8 stack.  This will leave you with ~6kW of backup charging capability.
You have to leave the AC charging to the G inverters, as they need to be the
ones who determine when it's ok to stop charging and sell back. The output
of the G series inverters will need to be run to a separate protected load
panel, and all charge controllers need to share the same Hub with the G's.

If you have more than 6kW of renewables, then split off additional inverters
or pairs of inverters with their own Hub.  Each would then need its own
separate protected load panel, and would of course need to be swapped out
for G series.  However, and this is the fun part, at this point you need to
disable ALL AC charging capability.  All recovery after a power outage will
have to come from renewables.  Which might or might not be a good thing.

Good luck


Phil Undercuffler
Director, Battery-based and Off-grid
Distribution Sales Group
Conergy
Our World Is Full of Energy
1730 Camino Carlos Rey Suite 103
Santa Fe, NM  87507
p.undercuff...@conergy.us
Direct | 505.216.3841
Toll Free | 888.396.6611 x4841
Fax | 505.473.3830
www.conergy.us



--original message:

I have not seen the system yet, but was told he has ten (10) Outback
inverters, 2 configured for sell back and 8 not....Was told they could
be factory re-configured to all sell back, but can only stack two
inverters in sell mode....If true, why can't you just parallel multiple
stacks of dual inverters and just feed each pair to their own circuit
breaker in the main panel?

Jeff Yago
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to