...And the Voc is present every morning before the current is high enough to start the controller. That's when I would expect to have a problem. boB, I doubt that the Voc sample duration is long enough to cause a problem.

I know that Rick got back on this list a few months ago so if you (Rick) have any input to help Walt, we welcome your comments.

Larry Crutcher


On Jun 27, 2009, at 2:35 AM, boB Gudgel wrote:

Wind-sun.com wrote:
Yes, it is a poor design. though you may not have any problems there with the heat de-rating of the panels. If the panel temperature gets under about 40C you may blow out the input. As long as you have a load on the output of the contgroller, it will keep the voltage down, but if the output is disconnected the input could go up to full voltage.

Remember that this controller opens up every so often, (8 seconds or so?) to check Voc and adjust the MPP-V based on that measurement.

boB




Who designed such a system?
..................................................................................................
Northern Arizona Wind & Sun - Electricity From The Sun Since 1979
Online Store: http://store.solar-electric.com/
Solar Discussion Forum: http://www.wind-sun.com/ForumVB/
..................................................................................................

  ----- Original Message -----
  *From:* Walt Ratterman <mailto:wratter...@sunenergypower.com>
  *To:* 'RE-wrenches' <mailto:re-wrenches@lists.re-wrenches.org>
  *Sent:* Friday, June 26, 2009 3:22 PM
  *Subject:* [RE-wrenches] Solar Boost Controller in Senegal

  Hello,


  I am in a very remote part of Senegal, (near the Guinea  and Mali
  borders…) and I have come across some prefabricated “plug and
  play” American made systems installed for educational institutions.


  The systems use two Sharp panels that are 220Watts, 33.6 Voc, 29.2
  Vmp, wired in series, using #10AWG home run wire from the panels
  back to the charge controller.


  Charge Controller is a Solar Boost 50.

Batteries are Dekka AGM – two strings of 250AH, 12V batteries. (four batteries total).


  My specific question is about the controller.  This is a 24V in /
  24V out charge controller with MPPT.  I have not used this before,
  so I am not familiar with the details of operation.


  The data sheet that I downloaded says that the maximum open
  circuit voltage is 57 VDC.  But, this system is hitting the charge
  controller with two panels of 33.6 VDC wired in series for
  73.2VDC.  So, why is the controller not fried, or what am I seeing
  wrong here.  I suppose with the panel temperature being elevated
  maybe 35 degrees above 25 degrees and a resulting 17.5% loss,
  coupled with some voltage drop, the system may actually be seeing
  less than the 57 volts...


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to