The AGM batteries are probably a better choice than gelled, but the fact that 
some are down to 5 volts is the real problem.

A typical AGM will lose around 1-2% charge per month at 25 degrees C. If they 
are at 5 volts, that indicates that they either sat around for over a year 
unused and uncharged, and possibly in a very high temperature environment. The 
2nd possibility is that there is some kind of constant load on them, even when 
the units are not turned on - which would be poor design.

The Midnite controller is not available yet, so your only real choices with the 
panels you have are the Outback FM60 or the Xantrex XW-SCC - both of them are 
in the $600 range.

..................................................................................................
Northern Arizona Wind & Sun - Electricity From The Sun Since 1979
Solar Discussion Forum: http://www.wind-sun.com/ForumVB/
..................................................................................................
  ----- Original Message ----- 
  From: Walt Ratterman 
  To: 'Rick Cullen - Blue Sky Energy, Inc.' ; 'RE-wrenches' 
  Sent: Tuesday, June 30, 2009 1:26 AM
  Subject: Re: [RE-wrenches] Solar Boost Controller in Senegal


  Hello all,

   

   

  I would like your input on what you think should be done here.

   

  Nine systems were purchased from Earthwalk.  One has been deployed for four 
months.  A second unit is being deployed now.  This leaves seven in the 
warehouse.  (And we wont even get into the fact that we have AGM batteries here 
instead of the advertised GEL batteries, and the voltage is so low they might 
not even work……I will deal with that separately…..)

   

  While it is clear that the panels do not match up with the controller, it is 
not clear why they are still working (other than the heat and dirt) and if they 
will continue to work.  

   

  One solution would be to just leave everything alone and tell them what they 
should do if the system(s) fail.  In some cases, this might be the right action 
to take.  But in this case, I think the folks who sold the prefabricated unit 
should be held accountable, and provide a system that is designed to work 
properly.  The schools paid good money for this equipment and they should at 
least have a running start at success, which is difficult to come by in this 
part of the world on a good day.

   

  So – when we tell the schools to insist that the system be fixed, what do you 
think we should tell them?

   

  Due to the characteristics of the panel (not being either 12V or 24V nominal) 
they need a MPPT controller.  I suppose we could tell them to change to a 
controller that will accept the output of the panel.  This would be either 
Outback, Midnite Solar, or possibly the new Morningstar 15A controller.  Any 
suggestions?

   

  The other route would be to have them change the panels, and keep the 
prefabricated system as it is.  Rick:  what would you recommend the best 
voltage / current combination to replicate the need for a 440 to 500 watt peak 
array output with the SB50?   

   

  Given the relative cost of the panels versus the controller, the manufacturer 
may likely decide to switch the controllers, but it is not as easy as it 
sounds.  If either the Outback or Midnite controllers are used, they will not 
fit into the small space the cabinet allowed for the SB50.  But I will deal 
with that another way.  (We will just build an all new cabinet here in Senegal).

   

  So – any ideas or thoughts I have missed are welcome!!

   

  Thanks so much for all of the great feedback.  I think, like most of us, 
every day is a learning experience, even if we think we have done this 100 
times before.  

   

  Take care,

   

  Walt

   

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to