Solar Pros, 

I've had real reservations about using traditional bus-type combiners that fit 
2/0 down to #10 awg wires. They are almost always a poor fit and electrical 
connection for smaller gauge wires. 

A neat solution I found to make 100% contact with all screw-type connectors, I 
started using a "bootlace" ferrule on the wire ends. The thinwall copper/tin 
sleeve will crimp easily onto the wire and is easily compressed into a form 
matching the connector jaws. I use it exclusively on DIN rail type terminal 
blocks and would use it on larger wires >#10 but the Paladin 4-jaw crimper only 
goes up to #10.

The internal jumper makes an excellent connection to any number of dist blocks 
using threaded rather than compression connections. 

Alliedelec.com   
400-0144 ferrule
889-1441 crimper
 502-3240 internal jumper
 502-3744 terminal blk

Jim Duncan
North Texas Renewable Energy Inc
817.917.0527
nt...@earthlink.net
www.ntrei.com 

--------------------------------------------------------------------------------

  ----- Original Message ----- 
  From: d...@foxfire-energy.com 
  To: RE-wrenches 
  Sent: Monday, July 27, 2009 6:17 AM
  Subject: Re: [RE-wrenches] CBI circuit breakers


  The only problem I've had with them is that their connectors can allow multi 
stranded wire to "broom out", (after installation) -- causing a loose / high 
resistance contact. I've learned to torque / wiggle & twist and retorque all 
multi strand connections. I have had one side of a 60A QO breaker go open out 
of the blue. db


  Dan Brown
  President
  Foxfire Energy Corp.
  Renewable Energy Systems
  (802)-483-2564
  www.Foxfire-Energy.com
  NABCEP #092907-44


    -------- Original Message --------
    Subject: Re: [RE-wrenches] CBI circuit breakers
    From: Allan Sindelar <al...@positiveenergysolar.com>
    Date: Mon, July 27, 2009 1:36 am
    To: "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org>

    I have had no problems to date, Kent. Can you be more specific as to what
    problems you have had? 

    Allan Sindelar
    al...@positiveenergysolar.com
    NABCEP Certified Photovoltaic Installer
    EE98J Journeyman Electrician
    Positive Energy, Inc.
    3201 Calle Marie
    Santa Fe, New Mexico 87507
    505 424-1112
    www.positiveenergysolar.com

    -----Original Message-----
    Is it just me, or have other wrenches had problems with the CBI circuit 
    breakers used in the Outback or Midnite combiner boxes?

    Kent Osterberg
    Blue Mountain Solar, Inc.
    http://www.bluemountainsolar.com/


    _______________________________________________
    List sponsored by Home Power magazine

    List Address: RE-wrenches@lists.re-wrenches.org

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm

    Check out participant bios:
    www.members.re-wrenches.org




------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

<<attachment: DIN.jpg>>

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to