There have been some good advice related to battery bank sizing and a better 
description of how Sunny Islands work with SunnyBoys, but I am afraid we are 
getting away from my original post that started this and that was:

Since a battery based inverter has a battery charging section and all kinds of 
software control over the charging process when connected to the grid, why does 
the battery charging process "go wild" when the grid is down and the AC power 
is being backfed from a separate AC coupled inverter.  Also, why do we keep 
having to field wire and program an added power relay or a separate diversion 
load relay to prevent over-charging and destroying an AGM battery bank because 
the battery charging process suddenly has no clue how to charge the battery 
bank.

Yes, the Sunny Island varies frequency which will cause an AC coupled SunnyBoy 
to be faked out and drop off line to avoid overcharging the battery bank, but 
it seems to me this is all just software programming, so why can't any inverter 
manufacturer simply control battery charging no matter where the AC power is 
coming from?  Why can't grid tie inverters used in an AC coupled application 
have the software to recognize a full battery condition and stop charging 
without having to drop off line on an out of limit grid condition and then 
cycle through the 5 minute wait? 

I am not an electronics engineer, but I don't see where any hardware changes 
are required, just some added software to select during initial setup.  Many of 
you may not deal with battery based systems, but half of our systems are and AC 
coupled is a great way to avoid long low voltage DC wire run losses.   We 
select generator type from a setup menu, how about "Press 1 for standard 
inverter setup, press 2 for AC coupling".

Jeff Yago

_____________________________________________________________
Netscape.  Just the Net You Need.
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to