If the ballasted system is properly designed to withstand the wind loading (90 mph to 150 mph), I would say that that most definitely qualifies as "firmly secured". Is someone actually giving you trouble on this issue, or are you just thinking ahead?

R. Walters
r...@solarray.com
Solar Engineer




On Oct 26, 2009, at 1:51 PM, Jason Szrom wrote:

Hello Wrenches…

In typical ballasted systems, the combiner box is mounted on unistrut fastened to roof stand-offs which are not fastened to the roof. I was wondering what your opinion would be about this in reference to the following NEC section:

110.13 Mounting and Cooling of Equipment
(A) Mounting. Electrical equipment shall be firmly secured to the surface on which it is mounted.

Has anyone ever had a problem with this during an inspection?

Thanks,

Jason Szrom
Engineer

Solar Energy Systems, LLC
1205 Manhattan Ave
Suite 1210
Brooklyn, NY 11222

718-389-1545 x13
www.solarEsystems.com

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to