Kirpal,

I have two older versions of this bulletin.  The 2005 version mentions a limited UL listing (E2875) for switching three 600-volt dc circuits.  It is interesting that the 2007 version does not mention a UL listing for that use, but otherwise it looks like the same document.  So this change may have happened some time ago without anyone being aware of it.  With the 2009 bulletin, you probably couldn't get a system wired that way in Oregon to pass inspection.  At least you couldn't if the inspector knows that there is no 3rd party certification.  On the other had, at least SQ D is still certifying that it is suitable for that purpose.  Manufacturer certification for non-standard uses is not uncommon.  I'm suspicious that back in 2005 Some Manufacturer Asked for the special listing and perhaps even paid for it.

Kent Osterberg
Blue Mountain Solar, Inc



Kirpal Khalsa wrote:
Hi All......
 
I recently came across a revised technical bulletin from square D ( http://ecatalog.squared.com/pubs/Electrical%20Distribution/Safety%20Switches/Heavy%20Duty/3110DB0401.pdf )......we have for years been using the Square D DC Disconnect of various amperages (30, 60, 100) as disconnects leading upto the inverter from the array.....we have frequently wired one string to each of the three poles of the disconnect......we have had this configuration inspected by inspectors regularly with approval everytime......this new revision of the document from Square D shows this is no longer a UL listed method.....they are now stating in this document that they are "self certifying" this technique.......have any of you come across this or know why Square D has back tracked? 
 
Something else I noticed is that they have raised the amperage rating on the 30A disconncect per pole by 2 amps from 18 to 20 which is good especially when using higher amperage modules like Evergreen ES-A series which would not have ben allowed to use the 30A disconnect as the short circuit current rating was too high for the derated poles. 

This is not a huge concern as more and more of the inverters we are using these days have an appropriate disconnect included with the inverter negating the need for an additional stand alone disconnect. 
 
On a side note............Are there any other manufacturers making listed muiti pole DC disconnects in which each pole can handle one string?  Also there is definately a need for roof mounted multi string (1-4 strings) combiner boxes with integrated DC disconnects for residential applications that have a reasonable price.......any one know if any?
 
 
--
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer
Renewable Energy Systems
www.oregonsolarworks.com

_______________________________________________ List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  

No virus found in this incoming message. Checked by AVG - www.avg.com Version: 9.0.725 / Virus Database: 270.14.131/2609 - Release Date: 01/08/10 23:35:00
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to