Downsize the main breaker?  I would if I could, but the customer only has 
100 Amps now, and the solar is fed with two breakers, a 30A and a 40A.  So to 
be under 120Amps, I would have to size the main to 50 Amps, which may be 
problematic.
    I can also do the line side tap, but had heard that a load analysis may be 
accepted instead.  The loads of the house will never use more than 100 Amps.  I 
am wondering if any codes or white papers detail that option.  

 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:    707-769-9037




________________________________
From: Eric Andrews <e...@ecosolarnow.com>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Sent: Tue, March 30, 2010 10:25:45 AM
Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

  
Nick-
 
Just
downsize the main breaker.  For example,
a 200 amp panel w/ a 200 amp main breaker could be reduced to a 150 amp main
breaker to allow for more solar to be connected.  You need to calculate for the 
120% rule.
 
Eric R. Andrews
NABCEP
Certified PV Installer


      
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org