Aluminum wire got its bad name during the era when it was use in 15
and 20 amp circuits, with #12 and #10 wire. That stuff is a
nightmare. As an electrician that has cleaned up some of the messes,
I can supply ample horror stories.
#2 and larger sizes of AL work fine. It is important to use
antioxidant on the connections. Separate copper wire from aluminum
using a listed splicing device.
Aluminum wire will turn to white powder in an underground cable where
the insulation has been breached. This is true for DC or AC.
At 05:51 PM 7/26/2010, you wrote:
I have used AL wire in DC circuits for 30 years and have never had a
problem. If you carefully follow the protocols for working with AL
you should have the same experience. As pointed out the cost
difference can be staggering. I'm designing an o-t-g 3kW PV system
now that has this array 1300' from the batteries, AL is the only
reasonable answer.
From the Solar, Wind and Hydro powered office of Jeff
Oldham/Regenerative SOLutions
____________________________________________________________
<http://thirdpartyoffers.juno.com/TGL3132/4c4e03bf90d8b9f2c2st05vuc>SHOCKING:
2010 Honda Civic for $1,732.09
<http://thirdpartyoffers.juno.com/TGL3132/4c4e03bf90d8b9f2c2st05vuc>SPECIAL
REPORT: High ticket items are being auctioned for an incredible 90% off!
<http://thirdpartyoffers.juno.com/TGL3132/4c4e03bf90d8b9f2c2st05vuc>ctips.net
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org