"Since the GEC for Enphase starts at the inverter on the roof, you must have a minimum of 8AWG running among the microinverters and down to the grounding electrode system. In the 2008 NEC and 2011 NEC, this conductor can serve the purpose of the ac EGC as well and can be terminated on the service panel grounding bus." Yes, but this conductor does not need to be "unboken", correct? This conductor, running among the microinverters can be terminated onto a mechanical pressure terminal which serves as the equipment ground buss in a load center which is not part of service enterance equipment and may be located anywhere on the premise. The remainder of the circuit is then provided by the EGC as it runs back to the service enterance and then the GEC to the GES. Correct?
Mark Frye Berkeley Solar Electric Systems 303 Redbud Way Nevada City, CA 95959 (530) 401-8024 <http://www.berkeleysolar.com/> www.berkeleysolar.com _____ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks Sent: Tuesday, September 14, 2010 8:41 AM To: 'RE-wrenches' Subject: Re: [RE-wrenches] GEC for Enphase inverters Mark and Rebekah, The term "continuous" is a requirement for any circuit and implies electrical continuity and current-carrying capability. Both the GEC and EGC must be continuous or you don't got one. It is not defined in NEC Article 100. What most people are referring to when they say that a GEC must be continuous is "unbroken" or the NEC talks about "irreversibly spliced." Splicing of a GEC is usually a last resort because there is no other option. For instance, multiple bonding jumpers coming off of multiple inverters would need to be irreversibly spliced to the main GEC that should proceed unbroken from the farthest inverter from the grounding electrode. 250.66 for ac and 250.166 for dc are consistent in requiring the minimum GEC to be 8AWG copper. Since the GEC for Enphase starts at the inverter on the roof, you must have a minimum of 8AWG running among the microinverters and down to the grounding electrode system. In the 2008 NEC and 2011 NEC, this conductor can serve the purpose of the ac EGC as well and can be terminated on the service panel grounding bus. Bill. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Rebekah Hren Sent: Tuesday, September 14, 2010 7:25 AM To: RE-wrenches Subject: Re: [RE-wrenches] GEC for Enphase inverters The code does require the GEC to be continuous (250.64C), and I believe that the AC EGC for the Enphase metal inverter cases is in fact the same as the DC GEC since the point of system bonding on the DC side is inside the inverter. See art. 100 definitions:Grounding Electrode Conductor. A conductor used to connect the system grounded conductor...to a point on the grounding electrode system. So this means that for Enphase systems the AC EGC (which is also the DC GEC) should be at minimum 8 awg (250.66) and continuous? Seems like it to me. Rebekah Hren --- On Tue, 9/14/10, Mark Frye <ma...@berkeleysolar.com> wrote: From: Mark Frye <ma...@berkeleysolar.com> Subject: Re: [RE-wrenches] GEC for Enphase inverters To: "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org> Date: Tuesday, September 14, 2010, 10:05 AM I believe the AC GEC runs from; the point where the ungrounded current carrying conductor is bonded to the enclosure of the service enterance equipment; to the connection to the ground electrode system. Conductors that run from the service enterance equipment, thru the premis to the Enphase are bonding jumpers that are not required to be continuous. Mark Frye Berkeley Solar Electric Systems 303 Redbud Way Nevada City, CA 95959 (530) 401-8024 <http://www.berkeleysolar.com/> www.berkeleysolar.com _____ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller Sent: Monday, September 13, 2010 9:46 PM To: RE-wrenches Subject: [RE-wrenches] GEC for Enphase inverters Friends: According to the 2005 NEC 250.64(C), the GEC for an AC system needs to be continuous without splices unless they are irreversible. I am not clear where this conductor starts and ends. Is it from the ground buss in a sub-panel to the disconnect switch on the roof, or to each inverter? Also, non-reversible splices need to be listed for use in grounding systems. Any suggestions on make and model of splices so listed? Any advise from those more experienced is much appreciated. William Miller Please note new e-mail address and domain: William Miller Miller Solar Voice :805-438-5600 email: will...@millersolar.com http://millersolar.com <http://millersolar.com/> License No. C-10-773985 -----Inline Attachment Follows----- _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org