I just did a review of the TL inverters by SMA for possible use.

A few points that are relevant:
They require the use of an external fused combiner (they also sell). It has
support for up to 6 strings, with both + and - fuse positions provided.

The integrated DC disconnect has no fusing - it will accept only two
conductors

The manual says these inverters are supposed to be installed in threes

They only work on 208VAC

Obviously they are lighter than their transformer based cousins

There is a warning to beware of stray array capacitances in excess of 2
micro Farads or more and 50mA from the cells to ground or the inverter will
disconnect

Obviously an EGC is still necessary from the frame of the array

Required clearance around the inverter has been increased to 12" (36" below)

Replaceable varistors are used to protect DC inputs from high voltages
(inside DC disconnect)

Still 600VDC upper limit

AC max conductor diameter is 2AWG, min is #6

DC conductors - #10 to #6

They recommend operating the DC disconnect once a year, 10 times to keep the
contacts clean

 

FYI - thought I'd share.

 

-Glenn Burt

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August Goers
Sent: Friday, December 10, 2010 3:50 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Tranformless inverter

 

Hi Bill and Wrenches -

 

For ungrounded arrays what specific fusing and or DC disconnect requirements
are needed compared to grounded arrays? 

 

I'm trying to sort through the code but nothing is popping out at me besides
what was already mentioned about needing to disconnect both the positive and
negative lines on the DC side. In SMA's case I'm guessing that their new
transformerless inverters with integrated DC disconnects and fuses may
already take of all the requirements?

 

Best,

 

August

 

 

August Goers

 

Luminalt Energy Corporation

1320 Potrero Avenue

San Francisco, CA 94110

m: 415.559.1525

o: 415.641.4000

aug...@luminalt.com

 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Friday, October 01, 2010 8:29 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Tranformless inverter

 

All,

 

Transformerless inverters are simply a subset of ungrounded or resistively
grounded PV systems covered by the NEC in 690.35 since the 2005 code cycle.
Power-One has been marketing their ungrounded inverter in the U.S. for
several years now. It was listed by CSA. The requirements for ungrounded
systems in 690.35 are as follows:

 

&bull              "Photovoltaic power systems shall be permitted to operate
with ungrounded photovoltaic source and output circuits where the system
complies with 690.35(A) through 690.35(G).

&minus      (A) Disconnects. All photovoltaic source and output circuit
conductors shall have disconnects complying with 690, Part III.

&minus      (B) Overcurrent Protection. All photovoltaic source and output
circuit conductors shall have overcurrent protection complying with 690.9.

&minus      (C) Ground-Fault Protection. All photovoltaic source and output
circuits shall be provided with a ground-fault protection device or system
that complies with (1) through (3):

&bull              (1) Detects a ground fault.

&bull              (2) Indicates that a ground fault has occurred

&bull              (3) Automatically disconnects all conductors or causes
the inverter or charge controller connected to the faulted circuit to
automatically cease supplying power to output circuits.

&minus      (D) The photovoltaic source and output conductors shall consist
of the following:

&minus      (1) Nonmetallic jacketed multiconductor cables

&minus      (2) Conductors installed in raceways, or

&minus      (3) Conductors listed and identified as Photovoltaic (PV) Wire
installed as exposed, single conductors.

&minus      (E) The photovoltaic power system direct-current circuits shall
be permitted to be used with ungrounded battery systems complying with
690.71(G).

&minus      (F) The photovoltaic power source shall be labeled with the
following warning at each junction box, combiner box, disconnect, and device
where the ungrounded circuits may be exposed during service:

WARNING

ELECTRIC SHOCK HAZARD

THE DC CIRCUIT CONDUCTORS OF THIS

PHOTOVOLTAIC POWER SYSTEM ARE

UNGROUNDED AND MAY BE ENERGIZED

WITH RESPECT TO GROUND DUE TO

LEAKAGE PATHS AND/OR GROUND FAULTS.

&minus      (G) The inverters or charge controllers used in systems with
ungrounded photovoltaic source and output circuits shall be listed for the
purpose.

 

We now have several products newly on the market to include on the list such
as the SMA and Exeltech products. Ungrounding the array requires additional
fusing and disconnects, but the most significant difference is that the
module wiring and all external cable must be PV Wire/Cable. Therefore only
modules with PV Wire/Cable can be used in these systems. You must confirm
from the manufacturer that they have made the switch. Hopefully all
manufacturers will be installing PV Wire/Cable soon so that this will not be
a problem anymore.

 

It is a good call to use up your USE-2 and order PV Wire/Cable from now on.

 

Bill.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Exeltech
Sent: Friday, October 01, 2010 6:39 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Tranformless inverter

 


Transformerless grid-tie inverters are permitted under the National Electric
Code as of 2008.  The Nationally Recognized Testing Laboratories (UL,
ETL/Intertek, CSA, etc.) took a while to develop the testing procedures for
testing to UL1741, which was the basis for most of the delay.

SMA isn't the only company with transformerless grid-tie inverters.  I know
of one American manufacturer with transformerless models on the market as
well.

Transformerless inverters are smaller, much lighter, and tend to be more
efficient than transformer-based units.  No transformer also means lower
product cost, and less shipping expense.  Win-win-win.


Dan


--- On Fri, 10/1/10, Drake <drake.chamber...@redwoodalliance.org> wrote:


From: Drake <drake.chamber...@redwoodalliance.org>
Subject: Re: [RE-wrenches] Tranformless inverter
To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
Date: Friday, October 1, 2010, 6:58 AM

I also received this advertisement.  Previously I had investigated the
smaller SMA transformerless inverters, and was told that this type would not
be allowed in the US until the 2011 code.  Has the ban been lifted?



At 12:52 AM 9/29/2010, you wrote:

Wrenches:

I received an advertisement from a distributor that SMA is now shipping 8, 9
and 10 KW transformerless inverters.  Don't these require double insulated
PV wiring and no connection  to ground on the AC side? It's been too long
since this subject last crossed my desk and I want to refresh my memory on
the specifics.

William Miller


Please note new e-mail address and domain:

William Miller 
Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com <http://millersolar.com/> 
License No. C-10-773985

 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to