Fellow Wrenches,

The discussion about battery venting reminds me of a useful and inexpensive program, BattMV, for determining ventilation requirements per EN-50272.  EN-50272 is a European standard used to determine how much air flow is needed for a room, I don't know of a equivalent standard used in the U.S.  It takes a surprising amount of ventilation.  For a 400-AH 48-volt L16 bank charged at 57.6 volts and 24 amps, it's about 7 CFM just to keep the %H2 down to 4%.  A 12-volt Zephyr vent is good for about 5 CFM!   If you think you are venting enough, take some time and study this issue.

Kent Osterberg
Blue Mountain Solar