Standard residential utility meters couldn't care less about power factor and will ignore reactive power. Additional utility bill savings by using these reactive-capable microinverters is $0.

Dan brought up a good point that adding too much capacitance also hurts power factor- so even if a utility did start caring about residential power factor, they wouldn't want these devices on every house because then their feeders would become excessively capacitive when motors weren't running. IMHO reactive power from these devices only makes sense if it's configurable and dispatchable by either the utility or a building's energy management system. And it doesn't seem to be.


-------- Original Message --------
Subject: Re: [RE-wrenches] Xslent?
From: Mark Frye <ma...@berkeleysolar.com>
To: 'RE-wrenches' <re-wrenches@lists.re-wrenches.org>
Date: 2011/1/10 12:14

SMA now delivers large inverters that provide several options for power
factor correction provided by the output of the inverter.
So we are not talking about the viability of the technology. There may
still be a question of how well the technology is implemented in this
particular microinverter.
The main question here is the efficacy of claims of an advantage for
small residential customers such that reduced PV array sizes deliver
equivalent energy as metered by the local utility.
Having followed the the whole power factor correction device discussion,
I still have some question in my mind as to the resolution of the
question of whether or not standard residential utility meters will
measure and accure a credit for improved power factor.

Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
_www.berkeleysolar.com_ <http://www.berkeleysolar.com/>

------------------------------------------------------------------------
*From:* re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Exeltech
*Sent:* Monday, January 10, 2011 8:59 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Xslent?

By the way, in answer to answer your original question, capacitors of
proper value, when installed in a circuit containing inductive loads,
are capable of allowing the circuit to attain a power factor of 1.0. As
part of our Underwriter's Laboratories testing for our grid-tied
inverters, a test fixture is used that's capable of both inductive and
capacitive reactance (it's part of the anti-islanding tests). I've
witnessed the power factor being adjusted from 0.7 leading and lagging
to an absolute perfect 1.0000 (yes, four decimals). It's all done by
varying the value of capacitance in the circuit. Thus, if one were to
use lab-grade test equipment, and take the time needed to make such a
precision adjustment, it's possible to achieve absolute unity in an
inductive circuit by "tuning" it with a capacitive circuit.


Dan


--- On *Mon, 1/10/11, North Texas Renewable Energy Inc
/<nt...@1scom.net>/* wrote:


    From: North Texas Renewable Energy Inc <nt...@1scom.net>
    Subject: Re: [RE-wrenches] Xslent?
    To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
    Date: Monday, January 10, 2011, 8:29 AM

    
    How efficient is a capacitor in offsetting the power factor error?
    99.9%...±2%...?
    Jim Duncan

        -----Original Message-----
        *From:* re-wrenches-boun...@lists.re-wrenches.org
        [mailto:re-wrenches-boun...@lists.re-wrenches.org]*on Behalf Of
        *Exeltech
        *Sent:* Sunday, January 09, 2011 9:03 PM
        *To:* RE-wrenches
        *Subject:* Re: [RE-wrenches] Xslent?

        --- On Fri, 1/7/11, Peter Parrish
        <peter.parr...@calsolareng.com> wrote:

        >  What ever is done to reduce the reative power, it has to be done

        >  in real time (with a fraction of 0.016 seconds, the 60 Hz cycle).

        >  You can’t wait until later in the evening to solve a problem that

        >  is occuring during the day.


        Peter is absolutely correct. Power factor correction MUST occur
        on a half-cycle by half-cycle basis, and at the exact moment of
        power consumption by the reactive load. Anything else won't be
        effective, and may in fact worsen the power factor at a given
        point in the grid.


        >  Real time compensation can be often done with capacitors alone

        >  or in conjuction with some smart electronics. Remember that for

        >  short periods of time capacitors can store considerable amounts

        >  of energy and can smooth out these reactive currents.


        Capacitors placed across a power line will store energy for
        exactly one-half cycle. At that point, the polarity reverses,
        the capacitor is discharged to to zero, then recharged to the
        opposite polarity. This process repeats every cycle.

        What DOES take place is a phase shift (displacement) in the
        current flow relative to the voltage waveform. Power factor
        correction is done with capacitor banks (we see them in
        substations and on power poles) to offset the power factor of
        the grid itself, which by its design is inherently inductive due
        to long runs of wire. Very large motors will have individual
        "tuning" capacitors installed to offset inductive reactive
        current flow. These capacitors are disconnected whenever the
        respective motor to which they're connected is not in use. On
        occasion, excessive capacitance exists in a circuit that must be
        offset by inductance, but this is rare.


        Like Tom Cruise said in Top Gun .. "It's complicated."


        Dan




        --- On *Fri, 1/7/11, Peter Parrish
        /<peter.parr...@calsolareng.com>/* wrote:


            From: Peter Parrish <peter.parr...@calsolareng.com>
            Subject: Re: [RE-wrenches] Xslent?
            To: "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org>
            Date: Friday, January 7, 2011, 5:39 PM

            I know only a little about Power Factor “charges”, but we
            can figure out some other “engineering” issues.

            Power Factor is a measure of the amount of reactive
            (out-of-phase) power compared to real (in-phase) power. It
            is somewhat complicated but the PF is unity for 100% in
            phase and 0 for 100% out-of-phase power.

            The important thing to remember is that (while holding the
            real power constant) for PFs less than unity there is in
            addition to the real power, and “in-flow” of power and an
            “outflow” of power four times a cycle. One might say, “Why
            do I care about reactive power? It flows in and out with no
            net contribution over the long run!). True, but the in-flow
            and out-flow represents higher currents on the lines and
            morelosses. Or it means that there have to be oversized
            service conductors to avoid the extra losses. Even if the
            losses are avoided, the higher currents can trip overcurrent
            protection devices, and of course the utility company needs
            to supply (and take back) the extra currents in real time.

            What ever is done to reduce the reative power, it has to be
            done in real time (with a fraction of 0.016 seconds, the 60
            Hz cycle). You can’t wait until later in the evening to
            solve a problem that is occuring during the day.

            Real time compensation can be often done with capacitors
            alone or in conjuction with some smart electronics. Remember
            that for short periods of time capacitors can store
            considerable amounts of energy and can smooth out these
            reactive currents.

            I can well imagine how an inverter can be designed to
            generate both real and reactive power, and therfore an
            inverter can reduce the amount of reactive power that needs
            to be supplied by the utility company – but not when the sun
            isn’t shining. I suspect that these types of inverters will
            have oversized output circuit wiring to handle the reactive
            currents without adversely impacting their efficiency rating.

            If I have time this weekend, I will take a look at
            Apparent’s website.

            - Peter

            Peter T. Parrish, Ph.D., President
            California Solar Engineering, Inc.
            820 Cynthia Ave. , Los Angeles , CA 90065
            CA Lic. 854779, NABCEP Cert. 031806-26
            peter.parr...@calsolareng.com
            Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885

            
------------------------------------------------------------------------

            *From:*re-wrenches-boun...@lists.re-wrenches.org
            [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
            Behalf Of *Jamie Johnson
            *Sent:* Friday, January 07, 2011 2:03 PM
            *To:* RE-wrenches
            *Subject:* Re: [RE-wrenches] Xslent?

            It's an interesting product for a niche market if it
            actually works as they say (Disclaimer:I am not claiming
            that it does), after speaking with an individual who I
            believe is the VP of Production for Apparent (use to work
            for EnPhase according to their website), he claims that the
            product is currently installed at the Google campus on a
            solar canopy for some of their EV chargers (can anyone
            verify this?)

            They have several other beta installs as well, however the
            individual I spoke to said they were only installing small
            systems at beta test sites (where the Util co charges for
            VAR's using separate meters like for EV charging) for now.
            No pricing has been set for the inverters, and they are not
            available for sale to installers yet.

            Apparently they claim the inverter can create/produce VAR's
            by taking 1 watt of power from the grid at night or from the
            solar output during the day and turning it into
            approximately 9 VAR's to offset the customers charges for
            VAR usage from the Grid. This is where the KVAh production
            on the graph before sunrise and after sunset comes from.

            I still would need to see a third party head to head
            comparison test before I believed it. Again niche market
            inverter for when the utility co charges for VAR's.

            Jamie

                -------- Original Message --------
                Subject: Re: [RE-wrenches] Xslent?
                From: August Goers <aug...@luminalt.com>
                Date: Fri, January 07, 2011 10:24 am
                To: RE-wrenches <re-wrenches@lists.re-wrenches.org>

                Hi All -

                Thanks for the helpful info! We did a little more
                research on our end and
                I guess Apparent is the new brand name for the Xslent
                product. What
                baffles me is the chart where they show that they're
                producing power
                before and after sunrise and sunset:

                http://www.apparent.com/products/mgi.html

                The system must include batteries? Someone on their
                marketing team is
                really going to town...

                Best, August

                -----Original Message-----
                From: re-wrenches-boun...@lists.re-wrenches.org
                [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
                Behalf Of jay peltz
                Sent: Thursday, January 06, 2011 4:43 PM
                To: RE-wrenches
                Subject: Re: [RE-wrenches] Xslent?

                HI Peter,

                I agree with you that for now on residential it makes no
                sense.
                However for commercial that might have to pay extra for
                PF issues, to have
                the inverter adjust for this makes sense.
                Its the reason they( inverter companies ) are doing it.
                I"ve heard a better more complete reason of course from
                Bill Brooks, who
                maybe can chime in.

                sorry got away from me,


                jay
                peltz power
                On Jan 6, 2011, at 2:34 PM, Peter Parrish wrote:

                >  I can't understand how any inverter WOULDN'T deliver
                its power with the
                >  voltage and current 100% IN PHASE.
                >
                >  When the voltage and current are not 100% in-phase
                that represents
                reactive
                >  power. Reactive power flows positive for a quarter of
                the AC cycle, then
                >  negative for a quarter of a cycle, then positive and
                then negative. The
                net
                >  result over one AC cycle is ZERO power delivered to
                the load.
                >
                >  So reactive power is worthless.
                >
                >  Worse, it results in higher currents (and voltages)
                for the same amount
                of
                >  in-phase power, putting additional stress on circuits.
                >
                >  - Peter
                >
                >
                >  Peter T. Parrish, Ph.D., President
                >  California Solar Engineering, Inc.
                >  820 Cynthia Ave. , Los Angeles , CA 90065
                >  CA Lic. 854779, NABCEP Cert. 031806-26
                >  peter.parr...@calsolareng.com
                >  Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
                >

                _______________________________________________

                _______________________________________________


            -----Inline Attachment Follows-----

            _______________________________________________
            List sponsored by Home Power magazine

            List Address: RE-wrenches@lists.re-wrenches.org

            Options & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

            List-Archive:
            http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

            List rules & etiquette:
            www.re-wrenches.org/etiquette.htm

            Check out participant bios:
            www.members.re-wrenches.org



    -----Inline Attachment Follows-----

    _______________________________________________
    List sponsored by Home Power magazine

    List Address: RE-wrenches@lists.re-wrenches.org
    </mc/compose?to=re-wrenc...@lists.re-wrenches.org>

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm

    Check out participant bios:
    www.members.re-wrenches.org




_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to