August, SMA recently updated their SI firmware so it would better communicate with the electronic governors on Kohler generators. On two projects so far, this new firmware has proven not to work on Generac generators (now with their own electronic governors, even the small air-cooled units), which I was previously advised to use by SMA due to their compatibility with the SI system.
I recommend a Winco generator, because they have no electronic governor to fight with the SI controls. Not sure if UL matters to you, but the 12kW isn't yet UL listed (a single part on the Honda motor is not UL listed, preventing the entire unit from getting a listing), but I have heard that they are working on it. With the new SI firmware, you could also use a Kohler, but Kohler has previously stated that their generators are not warranted for off-grid use. I would check in with SMA too; they have told me that they are working on lists of generators that do and don't work with the SI. If the tech you talk to doesn't know what you are talking about, try to talk to Steve Jefferson. Good luck, -Phil On Wed, Mar 16, 2011 at 9:58 AM, August Goers <aug...@luminalt.com> wrote: > Hi Off Grid Wrenches - > > I need to select a propane generator to provide a steady state load of > approximately 8 kW for a offgrid Sunny Island system. The project is for > an art studio and the loads are primarily all lights. > > I don't have much experience with generators so I thought I'd reach out > and see what products and manufacturers are popular out there. > > Thanks, > > August > > > August Goers > > Luminalt Energy Corporation > 1320 Potrero Avenue > San Francisco, CA 94110 > m: 415.559.1525 > o: 415.641.4000 > aug...@luminalt.com > _______________________________________________ > List sponsored by Home Power magazine > > List Address: RE-wrenches@lists.re-wrenches.org > > Options & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out participant bios: > www.members.re-wrenches.org > >
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org