On 8/15/2011 6:34 PM, Darryl Thayer wrote:
Hi wrenches, I have been informed off list that my system is not a supported configuration, that one phase can be paralelled, but the other two can not, one only on each of the other legs. So unless Outback comes back with more info, I was wrong. (mine still works, it was suggested I am very lucky) I have used the Apollo in different configurations, stacked in single phase, but I have not tried 3 phase stacks. Maybe you could conact Apollo.
Darryl



If you mean your system in Minneapolis, that is OK because they are only paralleled on the input (grid) side.

You can have as many inverters as you want selling back to the grid (even on 3 phase) as you did... Just can't parallel their outputs for off grid use when the power goes down. Each inverter CAN drive its own AC branch load
though.

boB






*From:* Darryl Thayer <daryl_so...@yahoo.com>
*To:* RE-wrenches <re-wrenches@lists.re-wrenches.org>
*Cc:* Julie Haugh <j...@greenhousepc.com>
*Sent:* Monday, August 15, 2011 10:43 AM
*Subject:* Re: [RE-wrenches] Large, off grid

Another method is to use the 120 volt VFX 3648, with one master and 14 slaves. (15 total, 5 in paralled on each leg) Check this with Outback as the 3 phase is different now than it was back in 2003. The three phase was the master generated a square wave and each slave would use this to lag either 120 or 240 degrees. For standalone not grid tie. I did a multi inverter on standalone 3 phase. Also a good source for this might be Julie Haugh <j...@greenhousepc.com <mailto:j...@greenhousepc.com>>; She has done a lot of work with Outbacks
Darryl

*From:* jay peltz <j...@asis.com>
*To:* RE-wrenches <re-wrenches@lists.re-wrenches.org>
*Sent:* Friday, August 12, 2011 1:02 PM
*Subject:* Re: [RE-wrenches] Large, off grid

Hi Daryl,

You might look at the new Outback 8kw 120/240v

I know that you can connect up to 10 in parallel, i don't know if you can do it 3 phase however.

jay

peltz power






On Aug 12, 2011, at 8:42 AM, penobscotso...@midmaine.com <mailto:penobscotso...@midmaine.com> wrote:

> Hello wrenches,
>  We have an opportunity to install a very large (60 kw) off grid system
> in Mexico. It is currently three phase. I do have the option of
> changing out the air conditioners (36 of them) to 120 single phase, but
> it is an added layer of complexity/cost that it would be nice to avoid.
>  The largest off grid system I've done is 21 kw so far, and it was
> single phase and fairly straightforward.
>  Does anyone know of a three phase, off grid inverter than can be
> paralleled for 500 (possibly 450) amps oputput. I am currently dealing
> with three 120 volt lines (2/0) and a neutral, running to a transformer
> to "clean up" the power from the gennie a bit. The client is determined
> to do this as he has spent about $500,000.00 USD in diesel over the
> last 5 years.I would very much like to get that transformer out of the
> picture...
>  I am well versed in the complexities/pitfalls of battery systems this
> large. I'm planning on using the Surrette YS-31series to minimize the
> footprint, as well as use Water Miser caps and install three separate
> deionizing water systems. My issue is the inverters. I have seen a
> Korean inverter, Sunsine (http://www.dongeiecos.com/) that is capable
> of this, but I am not sure I want my first install of this inverter to
> be 3000 miles away....
>  Anyone?
>
> Thanks,
> Daryl DeJoy
> NABCEP Certified PV installer
> Penobscot Solar Design
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org <mailto:RE-wrenches@lists.re-wrenches.org>
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org <mailto:RE-wrenches@lists.re-wrenches.org>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org <mailto:RE-wrenches@lists.re-wrenches.org>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to