Alan: Thanks for setting me straight about 3-phasing the Outback Radian
- I was not aware they are limited to parallel single phase applications.
Regards,
Gary Willett
On 10/21/2011 15:29, Allan Sindelar wrote:
Gary,
I was surprised by this information, as I had presumed that both units
were for single-phase only. So I checked.
Mary Raub in tech support at Outback told me that the Radian works
only in 120/240 single-phase, although they are stackable in parallel.
Someone in Schneider tech support told me that the XW can be used in
three-phase, up to six units (36 kW). Setup instructions are in
Appendix D of the XW installation guide, found online at
http://www.global-download.schneider-electric.com/85257849002EB8CB/all/5CC689CC3CB7FD10852578BF005EA759/$File/xw-hybrid-inverter-charger_installation-guide%28975-0239-01-01_rev-e%29.pdf.
Thanks, Allan
*Allan Sindelar*
_Allan@positiveenergysolar.com_ <mailto:al...@positiveenergysolar.com>
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
*Positive Energy, Inc.*
3201 Calle Marie
Santa Fe, New Mexico 87507
*505 424-1112*
_www.positiveenergysolar.com_ <http://www.positiveenergysolar.com/>
On 10/21/2011 2:01 PM, Gary Willett wrote:
Allan:
Also, you might consider using six to nine Schneider/Xantrex XW6048
inverters, or six to nine Outback Radian GS8048 inverters, in a
3-phase configuration, with a common battery bank.
Also, Schneider/Xantrex has an 80A 600V charge controller that may be
advantageous depending on the distance from the PV arrays to the
inverters.
Regards,
Gary Willett, PE
Icarus-Engineering LLC
Icarus Solar Services LLC
On 10/21/2011 10:17, Allan Sindelar wrote:
Wrenches,
We have been asked for a design for an off-grid system to reduce
generator runtime for a mountain resort. Initial projections
(consumption measurement results not yet available) suggest 15-20 kW
of PV and around 30 kW of inverter capacity. However, the generators
and existing wiring are three-phase 120/208.
My assumption is that our only options are a set of six Sunny
Islands, or 9-12 Outback GVFX3648s. Are there any other options or
approaches that I'm missing?
Thank you, Allan
--
*Allan Sindelar*
_Allan@positiveenergysolar.com_ <mailto:al...@positiveenergysolar.com>
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
*Positive Energy, Inc.*
3201 Calle Marie
Santa Fe, New Mexico 87507
*505 424-1112*
_www.positiveenergysolar.com_ <http://www.positiveenergysolar.com/>
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options& settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules& etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org