As long as an appropriately sized and rated OCPD is used on the input and/or 
output circuit of both devices, it shouldn't be a problem.

If it is a problem, it is with the testing certification process, and the 
standard needs to be fixed, or the testing laboratory needs to re-evaluate 
their interpretation of the existing standard.


See ya!

Marv
Director of Technology and Support, North America
SolarEdge Technologies, Inc.
Tech Support North America:  +877.360.5292
Mobile: +530.392.0356

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Darryl Thayer
Sent: Tuesday, November 08, 2011 7:22 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] High Voltage MPPT units

Caution!!! if you parallel the imput of both the inverter and terh charge 
controller one or the other will be destroyed.  ASk BoB if you parallel on teh 
input either charge controllers or inverters one or the other dies. or both.

From: "Larry Crutcher, Starlight Solar Power Systems" <la...@starlightsolar.com>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Sent: Tuesday, November 8, 2011 9:18 AM
Subject: Re: [RE-wrenches] High Voltage MPPT units

Dick,
I had that thought as well but it leaves open the possibility of paralleling 
the grid inverter and charge controller. What effect that will have is yet to 
be explored.

This idea originated for my personal residence in Yuma which has 4400 watts of 
PV. We leave that home for several months in the summer but want to protect our 
frozen foods from power outage after having lost big $$ in ruined food. So I 
could employ the double disconnect if the AHJ will accept it but I have high 
reservations in selling that method to others.

Larry Crutcher
Starlight Solar Power Systems

On Nov 8, 2011, at 5:34 AM, Richard L Ratico wrote:

> I may be missing something here...... but, for a manual switching solution, 
> why
> not use two standard 600V DC discos. Put the PV to the top of both, load side 
> of
> one goes to the battery inverter, load side of the other to the grid tied
> inverter. Turn one off, turn the other one on. Not as elegant as a transfer
> switch, maybe more expensive, but seems dirt simple and available now.
>
> Dick Ratico
> Solarwind Electric
>
>
> --- You wrote:
> Could you use the old Dankoff trick of running through 2 poles  in series of a
> 300 v rated switch? That used to be approved, before we had all these 600 v
> rated equipment.
>
> R. Walters
> r...@solarray.com<mailto:r...@solarray.com>
> Solar Engineer
>
>
> On Nov 7, 2011, at 1:16 PM, Larry Crutcher, Starlight Solar Power Systems 
> wrote:
>
>> Ray,
>> Yes, the idea was for a low cost way to add battery backup to existing high
> voltage PV grid tie systems, not new construction.
>>
>> The second inverter does not need to be able to sell since that is handled by
> the grid tie inverter. It simple passes grid power to loads and maintains the
> battery. That means any off-grid inverter/charger or even low cost separate
> inverters and chargers may be used, a very economical solution. However, the
> idea may be of no value because it appears no one makes a transfer switch.
>>
>> Larry Crutcher
>> Starlight Solar Power Systems

_______________________________________________
List sponsored by Home Power magazine

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>






************************************************************************************
This footnote confirms that this email message has been scanned by
PineApp Mail-SeCure for the presence of malicious code, vandals & computer 
viruses.
************************************************************************************
CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
the use of the individual or entity who is the intended recipient and may 
contain information that is privileged, confidential and exempt from disclosure 
or any type of use under applicable law. If the reader of this e-mail is not 
the intended recipient, or the employee, agent, or representative responsible 
for delivering the e-mail to the intended recipient, you are hereby notified 
that any dissemination, distribution, copying, or other use of this e-mail is 
strictly prohibited. If you have received this e-mail in error, please reply 
immediately to the sender.
P  Please think of the environment before printing this email



************************************************************************************
This footnote confirms that this email message has been scanned by
PineApp Mail-SeCure for the presence of malicious code, vandals & computer 
viruses.
************************************************************************************



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to