I'm with William on this: wire sizing for volt drop or power loss is not
the same as max current safety calculations.
After first sizing for NEC requirements, you have 2 issues you're
possibly over sizing for:
1) reducing the power losses on the line to improve overall system
efficiency.
2) minimizing volt drop so that the inverter doesn't disconnect from an
over voltage issue.
For the power loss issue, I created a spread sheet (and William has one
too) that takes into account power losses, not just volt drop, and you
can allot a cost per watt for the system and then compare that to the
cost of over sizing the wire.
In this case, it doesn't make sense to save 30 watts, if the wire costs
$1000 more.
As William pointed out, you don't really want to size for max, but
instead for normal operating conditions. Even with the array at max
output, your inverter efficiency is going to reduce that by at least 5%,
and that would probably only occur for brief periods.
On issue #2 which is more important, the volt drop to avoid inverter
shut down is going to depend more on the utility. Is the utility
voltage stable, and if so what is the grid voltage usually there? If
it's already on the high side all the time (>250 on a 240), and your
line losses add another 10 volts, you might have regular shut downs
(>264 @ inverter). If grid voltage tends to be low (<230), and has low
voltage occurrences (<210), grossly over sizing the wire will only
encourage low voltage shut downs (<211 @ inverter).
Ray Walters
On 11/16/2011 10:49 PM, William Miller wrote:
Luke:
Maximum inverter output will occur rarely. Most of the time the
inverter(s) will be running at lesser output amps. One approach is to
size wiring for a certain percentage of the average operating amps.
What is the average operating amps? One way I have found to calculate
this is use PV Watts and invoke the tool that gives a data set of hour
by hour results. This includes night time hours. Delete all values
with a zero output and average the rest. I found a daily bell curve
that is about 50% of full power. Your results may vary.
Good luck,
William Miller
At 07:51 PM 11/16/2011, you wrote:
1: Given the significant cost of the AC cabling for this situation,
what is the most appropriate number to use for current in running
voltage drop calcs? The wiring is going to be significantly oversized
to achieve a ~1% VD at this length. I could use the max rated output
current of the inverter (120A), but that seems like it might be
overly conservative. Opinions?
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org