I believe the Outback configuration will spin the meter backwards when utility power is used to charge the batteries. I checked with former co-workers in a utility meter department. A meter with a detent would be the simplest way to make the meter unidirectional, but those meters are supposedly long gone. A meter programmed to be unidirectional would achieve what the installer wants.

Chris

On 12/7/2011 12:59 AM, wire...@gmail.com wrote:
David,

Here is a link to what you might be looking for:
http://www.outbackpower.com/pdf/tech_notes/120_vac_single_inverter.pdf

Larry Liesner
Wirewiz
31 Lincoln St
Westport, CT 06880
203-644-2404 <tel:203-644-2404>
wire...@gmail.com <mailto:wire...@gmail.com>
www.wire-wiz.com <http://www.wire-wiz.com>
NABCEP Certified PV Installer (# 032611-184)


On Tue, Dec 6, 2011 at 5:08 PM, Dave Palumbo <d...@independentpowerllc.com <mailto:d...@independentpowerllc.com>> wrote:

    We are installing a grid interactive, with battery back-up,
    OutBack Radian GS8048 with 5kW of PV. Vermont has a “Solar Adder”
    premium that varies from utility to utility but in this case adds
    6 cents per kWh over and above net-metering (basically to come up
    to a par value of 20 cents/kWh for PV production).

    We need to install a gross PV production meter between the main
    (utility) load center panel and the Radian inverter. We need a
    meter that is not multidirectional, as we only want to count the
    kWh’s that are pushed out into the grid (and not subtract what the
    Radian uses from utility power to satisfy the protected loads
    center when the sunlight doesn’t handle that).

    Hialeah Meter offered a GE KV2CE meter that can be programmed to
    do what we need for $ 260 plus $25 programming fee.

    The utility will have an option, but I’m wondering what other
    options others have used for this situation.

    David Palumbo

    Independent Power LLC

    462 Solar Way Drive

    Hyde Park, VT 05655

    */www.independentpowerllc.com <http://www.independentpowerllc.com> /*

    NABCEP Certified PV Installer

    Vermont Solar Partner

    23 Years Experience, (802) 888-7194 <tel:%28802%29%20888-7194>


    _______________________________________________
    List sponsored by Home Power magazine

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>





--



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


--

Christopher Warfel, P.E.
ENTECH Engineering, Inc.
Energy Utilization Experts
(401)466-8978

The information contained within this communication shall
be considered confidential and shall not be retransmitted
without knowledge of the sender. Please contact us if
this email reached you in error. Thank you.

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to