Thank you for the good responses. Here's what I have learned so far:

Re Onan: as I had mentioned in my original post, "The 6 year old system has worn out two Onan residential standby generators."  This was before our initial visit. Both generators were air-cooled 3600 rpm units, as I understand. Neither was designed for the hours it was run. However, the customer is not very pleased with Onan because of this experience, even though I'm not sure how much of the experience was Onan's fault, beyond the initial recommendation. Certainly, selling the customer a home standby unit with heater and battery charger/controller AC loads was not wise. But apparently the distributor is buying the most recent failed unit back from the customer. I would like to recommend an Onan RS20000, as these are excellent units, but the customer may resist this after bad experiences with the RS12000, even though it's a completely different unit.

Re Kohler: Kohler's 15kW unit is that it too is for home standby application. The local Kohler service rep had no model to recommend.

Re Olympian (made by Caterpillar): the smallest model sold in this country is a 25kW, well larger than we need.

Re Generac: while I am quite impressed with the 6kW EcoGen unit, that's a special model, developed for the purpose, and too small for this application. I'm hesitant to use one of their standard units.

That leaves Gillette, who makes a 15kW LP with a GM engine. I'm waiting for a quote.
Allan

Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com




On 1/10/2012 10:15 AM, Randy Brooks wrote:
Allan,

Check out Cummins/Onan units too.  

Randy Brooks

Brooks Solar, Inc.

Solar Power for People

140 Columbia View

Chelan, WA  98816

509-682-9646

ra...@brookssolar.com

www.BrooksSolar.com


On Jan 9, 2012, at 7:59 PM, Allan Sindelar wrote:

Wrenches:
We have cautiously agreed to take on a substantial upgrade and rehabilitation of a poorly designed 48V off-grid system. Our upgrade will include a substantial array addition, battery replacement, and charge controller/safety disconnect replacement. But the immediate need is for a generator. The 6 year old system has worn out two Onan residential standby generators; the second one just now (at winter solstice) has failed completely.

We expect to keep the two SW5548 inverters. The site is at 7,800' elevation. The fuel must be LP. The customer is willing to pay for a high-quality unit. We expect only to specify or recommend the unit, but not resell it, so there's no profit motivation involved; we just want the best solution..

I am looking for recommendations of a low-speed, liquid-cooled, commercial- or industrial-grade LP generator, of at least 12kW and preferably around 15kW, with a good reputation for long-term reliability, and that is not designed for home standby use (with phantom-load heaters and controls). It will be located outdoors, so must have a weather enclosure.

I occasionally am asked to answer this same question by Home Power readers, who assume I know the answer because I wrote a primer on generators for HP awhile back. Truth is, I don't have any good recommendations in this size range, and I'm really hoping that some of you experienced off-grid Wrenches who have done larger systems can help here.

Thank you,
Allan
--
Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to