> Wrenches,
> 
> I have a client with a 4.6 kw grid tied system using a Sunny Boy 6000 
> inverter.  We have AC Coupled to that system with 2 Sunny Island 5048's and 
> 8-Concorde SunXtender 3050T 6 volt batteries in series feeding an essential 
> load/critical load sub panel.  The wiring to the sub panel from the Sunny 
> Islands is #6, the max wire size that can be used in the AC 1 and AC 2, in 
> and out, of the Sunny Islands.  The 2 pole breaker at the sub panel is 70 
> amps ( 56 amps feed through current x 1.25 = 70 amps ).
> This allow the 4.6 kw solar system and the Sunny Boy 6000 to act as a micro 
> grid and charge the batteries and support the loads in the SubPanel when the 
> grid is down and still be isolated from the main service panel and the grid. 
> 
> We have moved several loads from the main 200 amp service panel into the 
> essential load/critical load panel, the well pump, the refrigerator, the 
> circulator/boiler controls for the propane fired radiant heating system and 
> some lights and communication circuits.  
> 
> The main 200 amp main service panel has an integrated manual transfer switch 
> that has allowed them to fire up the gas powered Honda generator and run all 
> of the loads when the grid was down before we installed any systems to their 
> home.  They would like to be able to continue to do this in an extended power 
> outage.
> 
> So here is the question?  In a power outage, if they fire up the generator 
> and move the manual transfer switch in the Main Service Panel to generator, 
> the Sunny Islands will see this generator power coming from the Main Service 
> Panel and switch from Back Up Mode to Pass Through Mode.  The Sunny Boy 6000 
> will send any excess power not used by the loads to the the generator (as if 
> it was a net metering arrangement ) believing it is the grid. This would 
> probably destroy the generator or some other disasterous scenario.  
> 
> So how can the generator feeding the Main Service panel be isolated from the 
> Sunny Islands and Sunny Boy feeding the SubPanel as a micro grid in a power 
> outage and still provide power to the loads that are in the Main Service 
> Panel?
> 
> Thank you for the collective wisdom and knowledge that this group has 
> acquired from years in the trenches making it all happen.
> 
> Larry
> 
> Larry Brown
> Sun Mountain
> NABCEP Certified PV Installer
> 
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to