Wrenches,

Sorry for late answer as I was/am busy in meetings.

I will recap as follows:

In a nut shell, Todd made a great point: equalizing and cycling are two 
different necessary steps in a full charge of a flooded lead acid battery. 
“Floating applications” means exactly that: they stay in floating mode 99% of 
the time. The float charge address the self-discharge of the battery. If the 
battery is seeing additional external causes for discharge, then it need to go 
through the re-charge process, which includes, depending the DOD, going through 
bulk charge, absorption charge and floating charge. On flooded lead acid 
technology, we have the luxury to do an equalization charge in lieu of the 
float charge, approximately after 30 cycles (typical 4 weeks, sometime earlier, 
sometime later, depending application specifics, size of battery, and, age of 
battery).
For memo: equalization charge address two issues – equalizing the cells so you 
do not face more than 30 points between the cells (resulting on difference 
charge acceptance), and, mitigate the acid stratification in the electrolyte 
(thus improving the charge-discharge performance and reducing corrosion).

Having said that, a  lead acid battery designed for true deep cycle is best 
used for cyclic applications that actually cycle the battery due to the 
application. That battery design will keep the battery in great condition with 
numerous cycles, provided you actually fully recharge the battery and address 
equalization periodically after completing absorption, instead of the floating 
mode. That does not mean that you need to exercise unnecessary cycle the 
battery for increasing life. Another distinction is that true deep cycle lead 
acid batteries require 50 to 100 cycles when new to reach full capacity.  Maybe 
that is where some confusion built up regarding “cycling a battery is good”.

A “UPS” battery  technology is designed specifically for 99% floating 
applications. They provide power as a “parachute” if & only when there is a 
power outage. Any exercise cycling on this battery design will ruin the 
battery. Some applications are necessary full “floating applications”: the “99% 
of the time” is actually much less than that ( power outage, loads, system  
losses, shadow loads, …) , resulting into a larger DOD. The floating charge is 
therefore not sufficient to overcome the DOD. Now we are talking requirement of 
recharging the battery (thus actually cycling it).
Note: On VRLA, equalization is no go, although a boost charge can be considered 
on AGM (application specifics, too long to describe here on the blog).

The issue is to pick the right battery design for the application, and then 
make sure the battery is full charged at each cycle.

Hope this helps, not confusing you more. There are so many perspectives to see 
from and one is easy confused…

John

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of 
toddc...@finestplanet.com
Sent: Tuesday, February 21, 2012 12:45 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] cycling flooded batteries is not necessary


the two battery manufacturers say that cycling of floated batteries is 100% 
unnecessary.



equalizing is still important to prevent stratification of the electrolyte... 
but equalizing and cycling are different things.



todd







On Tuesday, February 21, 2012 6:33am, "Drake" 
<drake.chamber...@redwoodalliance.org<mailto:drake.chamber...@redwoodalliance.org>>
 said:
In my experience, at least my batteries need to be cycled.  Here is the data.

AC coupled backup system.  The batteries are usually only supplying the 
inverter controls, with the pair of Outback 3524 inverters connected but turned 
off at the Mate.  80 watts of pv is used for a battery maintainer.  The 2160 W 
of PV usually goes straight to the grid, and is switched over when needed.

The batteries will remain essentially dormant with self discharge and control 
power somewhat balanced by a trickle charge coming from the small sub array.  
The batteries hold around 25.2 volts over night.  When they drop to 25 or 24.8, 
I charge and often equalize them.

Just equalizing will not make them hold at 25.2 V again.  Even back to back 
equalization will not keep the battery V from dropping to 25 almost 
immediately.  If I switch to off grid mode for a night to cycle the batteries 
and then bulk charge them,  they will hold the 25.2 V again.

I think cycling really is needed to mix up the acid.

Drake



Sent from Finest Planet WebMail.

This e-mail message and any attachments that accompany it may contain 
information that is confidential, privileged, or protected from disclosure.  
It is intended solely for the use of the individual(s) to whom it was intended 
to be addressed. If you have received this e-mail by mistake, or you are not 
the intended recipient, any reading, disclosure, copying or other use of this 
communication is strictly prohibited.  If you have received this communication 
in error, please immediately advise the sender at their phone number listed 
above, or by electronic mail, and also permanently delete the original and all 
copies of this e-mail and any attachments from all locations. Thank you.
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to