what is the point of having battery backup if is is so small as to not really 
be able to back anything up (except when the sun is shining)?
 
this seems like a system design error rather than a charge controller problem.
 
my .02
 
todd
 
 
 
 
On Thursday, July 19, 2012 4:35pm, "Brian Teitelbaum" 
<bteitelb...@aeesolar.com> said:




Drake,
 
I’ve been hounding a couple of the charge controller manufactures about this 
issue, but so far I just haven’t seen a light bulb go off in their heads, but 
I’ll keep trying, and maybe this is a better forum to do it.
 
MPPT controllers can be adjusted to current limit at amperage values below 
their rating, but if you do that, you are also limiting the output of the array 
in general, and the amount of PV power available to run the loads directly from 
the array (through the inverter). Not the best use of available PV power.
 
Say you have an 80A controller and a 200AH battery. With current technology, 
you have two choices:
 
Let the controller operate at 80A. If you have loads to draw off some of the 
current (or sell to the grid), great, but if not you could be seeing a charge 
rate of C/2.5, which would be pretty hard on a sealed 200AH battery, to say the 
least. Granted, the battery voltage would rise pretty quickly, and the 
controller would start to taper off, but it would still see high currents 
especially if the absorption time is set long. Not a happy scenario.
 
Or, you can set the current limiting on the controller to 20A for a C/10 charge 
rate. But if you had loads drawing 60A, you would be pulling that additional 
40A from the battery and not using the array’s full power. Also not a happy 
scenario.
 
What we need is a controller that can read the signal from a shunt at the 
battery, and use that as the basis of current limiting control. 
 
For example, if we have an array that can produce 80A of current, but we want 
to limit the battery to 20A of charge, there would be 60A of potential current 
there to run loads without drawing on the battery. If there are no loads 
running, the controller should current limit at 20A (reading from a shunt), but 
if loads are turned on, the controller should be able to let more current 
through while still limiting the battery to 20A. When loads are shut off, the 
controller should go back to a 20A limit.
 
This doesn’t all have to happen very quickly as a battery can take a heavier 
charge for a short period of time, but I think that this would be a major 
improvement of controller function.
 
Of course, if you are grid-tied you can sell all the excess power, but if the 
grid goes down, or you are off-grid….?
 
Because of the low cost of PV and the high cost of batteries these days, I’m 
seeing more and more requests for large arrays with smaller batteries. I also 
think that PV is now cheap enough to allow for oversizing of arrays for better 
battery charging on cloudy days, which can reduce generator run times. We need 
smarter controllers.
 
What say ye, charge controller gurus?
 
Brian Teitelbaum
AEE Solar
 


From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Drake
Sent: Thursday, July 19, 2012 2:21 PM
To: RE-wrenches
Subject: [RE-wrenches] Small battery bank vs too large array
 
Hello Wrenches,

Where can I get a device that will measure current through a shunt and create a 
signal to trigger a relay?   

We want to be able to use a 2 kW array with four, 200 AH sealed batteries on an 
Outback system.  2 kW of PV would be too much amperage for the batteries.  The 
idea is to open relays to disengage strings in conditions of high current to 
the batteries.

The reason for this is to create backup systems where power will be abundantly 
available when the sun shines. The system will normally connect to the grid, 
except during outages.  In normal charging conditions the power will go 
straight to the grid.  When the grid is down, power will be available for loads 
and battery charging, but batteries will be protected from overcharge?

Any suggestions on ways to accomplish this are welcome!

Thanks

Drake 


Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV Installer
740-448-7328
[http://athens-electric.com/] http://athens-electric.com/


Sent from Finest Planet WebMail.
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to