When a long circuit has surge protection at only one end, the voltage at the unprotected end of the wire will rise, by induction, during a lightning event that causes the surge protection to activate. There should be surge protection at both ends of long feeders to reduce possible damage from induced voltages.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882


On 9/7/2012 11:14 AM, Jeff Irish wrote:

Kent,

Surge protection is at the inverters, 200 feet away, on both the AC and DC sides. Nothing at the array; never thought we'd need it there. There's a 4 string fused DC combiner on the west pole of each row; no damage visible on any of them and their fuses were all ok. And yes, each pole of 10 modules is a separate DC string, 4 are combined into a DC output circuit to each of four SB7000US inverters.

Jeff

Hudson Solar

*From:*re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Kent Osterberg
*Sent:* Friday, September 07, 2012 11:56 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Extensive Lightning Damage to Modules

Jeff,

Is there any surge protection in the combiner boxes? Any damage visible in the combiner boxes? Any fuses or breakers open in the combiner boxes? Is each pole a single string of modules or multiple strings of modules?

While there where undoubtedly ground currents flowing they probably didn't cause the damage in the module junction boxes. The PV module and wiring to it form a loop - often a loop with a large area in the vicinity of the module. The current from the lightning strike has a tremendous dI/dt and the changing magnetic field from it will induce voltages in any wire loop.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com  <http://www.bluemountainsolar.com>
t: 541-568-4882
On 9/7/2012 7:40 AM, Jeff Irish wrote:

    A customer of ours has recently suffered lightning damage to 31
    out of 160 top of pole mounted modules.  This is the first time in
    10 years that I've seen modules damaged by lightning.  Lots of
    inverter GF fuses and a few inverters, but never modules.  We're
    trying to determine if it was caused by the lightning flash
    irradiating the modules or ground currents.

    The array consists of 16 DP&W top of pole mounts with 10 modules
    each, arranged in a square of 4 poles E-W and 4 rows N-S.  The
    poles are 13 feet center to center E-W and the N-S row spacing is
    about 50 feet.  The poles are 6 inch galvanized Technoposts,
    augured 5 -- 7 feet into the firm ground, connected with a network
    of about 160 feet of bare #6 copper and at least 8 copper plated
    ground rods. Altogether we have about 130 square feet of bare
    metal surface area connected and buried in the ground at and
    around the array.

    The customer saw lightning strike just after dawn a few weeks ago
    a couple hundred feet to the southwest where it also destroyed two
    utility pole mount distribution transformers and ran along the
    utility wires 100 feet south of the array.  The inverters are 200
    feet NW and suffered no damage.  The array and modules look
totally fine, except some of the J-boxes are deformed from heat. Opening the J-boxes shows varying levels of damage to one or more
    diodes, from discoloration to being broken and cracked open.

    The odd thing is the pattern of damage (we've tested all the
    modules individually for Voc and Isc).  Only modules in the south
    row of 4 poles are damaged, and the damage is concentrated on the
    modules closest to the ground; modules higher up in the air appear
    OK.  Also, damage is less frequent as you move east, away from the
    direction of the strike.

    If it was caused by ground currents, why would the current want to
    go up the poles, why only the southern row of poles, and why
    damage more modules closer to the ground and not those at the
    top?  Is it possible a flash near the ground irradiated the
    modules causing a current spike and the southern row shielded the
    other rows from most of the flash?  Anyone have experience with this?

    Jeff Irish, PE

    President

    Hudson Solar

    13 Hook Road

    Rhinebeck, NY 12572

    T.845.876.3767x110

    F.845.876.3912

    j...@hudsonsolar.com <mailto:j...@hudsonsolar.com>

    /Solar Electric Systems/

    /NYSERDA Eligible PV Installer/

    /NABCEP Certified Solar PV Installer/

    /NABCEP Certified PV Technical Sales/

    *MailScanner has detected a possible fraud attempt from
    "applewebdata:" claiming to be* HudsonSolar.com
    <applewebdata://B5F2562A-2B67-4161-84E4-42F12DC28720/www.hudsonsolar.com>

    2011 NYSERDA Excellence in Quality Award | 2011 NYSEIA Award
    Winner | 2009 Best of the Hudson Valley | 2008 SunPower Dealer of
    the Year | EDC Business Excellence Award for Innovation




_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to