Most of the inspectors I've dealt with are at least somewhat reasonable. A few are fundamentalists for their own interpretations. I'd at least show the inspector the email with Bill Brook's statement and discuss the logic of the situation. It is obvious that the intent was to protect a wire that was double fed and could overload. The AHJ has the responsibility for interpretation of the code, so can allow what s/he sees fit.

At 10:06 AM 9/28/2012, you wrote:
I agree with Dave, as do most AHJ's around Southwest Florida.

We're stuck with the strict reading of the code, despite the craziness.

Pull new, larger wire.

Jason Szumlanski
Fafco Solar


On Fri, Sep 28, 2012 at 10:02 AM, Dave Click <<mailto:davecl...@fsec.ucf.edu>davecl...@fsec.ucf.edu> wrote: Mr. Brooks had an email on this topic on 5/8, 12:58pm ET. NEC officially says that the conductor needs to be upsized but the 2014 will fix it because that is dumb. I've copied some of Bill's email below.

**
The key distinction was used in my proposal to the 2014 NEC that removed the statement “and conductor” in 705.12(D) since conductors are treated very differently in the NEC. We in 690 are the ones that got this messed up. The issue with conductors are taps. With two sources feeding a tap, the sum of the feeder breakers would have to be taken into account in sizing the tap. This does NOT mean that the tap is a full size conductor. The tap rule determines the size and the new proposal simply requires you to use both the feeder breaker and the PV breaker in sizing the tap. This assumes that both breakers are feeding the tap in the event of fault on the tap and that there would be no problem clearing that fault. If fault current was used as an argument for oversizing (it is wrong), it only has relevance in the tap scenario. A fault in a feeder with no taps does not allow the sum of the currents to flow anywhere but where the fault is—the rest of the conductor is undamaged in a fault.

...

Sizing a conductor for the sum of two breakers on opposite ends of a feeder seems to be what the code says, but it is totally ABSURD from a technical point of view. John’s articles were merely pointing out that the code language seems to be telling us to do this, regardless of whether it makes technical sense. The 2014 NEC will do away with this craziness.
**


On 2012/9/28 9:46, Kristopher Schmid wrote:
It seems to me that the conductor should not be subject to the 120% rule
despite what the code says.  The potential safety issue here is
overloading the neutral bus, right?  While feeding currents could be
additive in the panel, they would be subtractive on the feeder, no?  I
seem to remember seeing this discussion on the list before.

Kris

On Fri, Sep 28, 2012 at 8:26 AM, Aaron Mandelkorn <<mailto:reoso...@gmail.com>reoso...@gmail.com
<mailto:reoso...@gmail.com>> wrote:

    I agree.  With a 150A bus being fed by 100A from the grid leaves 80
    additional amps (120% of 150A) to feed the bus from outside sources.
      It seems to me that 40A of PV being back fed will be just fine.

    Aaron Mandelkorn
    NABCEP Certified PV Installer
    Renewable Energy Outfitters
    Box 65 Salida, CO. 81201
    <tel:%28970%29596-3744>(970)596-3744 <tel:%28970%29596-3744>
    <mailto:reoso...@gmail.com>reoso...@gmail.com <mailto:reoso...@gmail.com>
    <http://www.reosolar.com>www.reosolar.com <http://www.reosolar.com>


    On Sep 28, 2012, at 6:32 AM, Drake wrote:

    Are you sure you can't?  Since the bus has a rating of 150 A and
    is protected by a 100 A breaker, there is plenty of room to not
    over amp the bus from the two sources of power.

    The amperage from the inverter will cancel amperage coming from
    the utility in the feeder.  The wire will never supply over the
    100 A.  The theoretical max the inverter could backfeed would be
    40 Amps in the 100 Amp cable if no loads were being supplied.  It
    would certainly not be a safety issue.  Am I missing something in
    the code?


    At 12:51 AM 9/28/2012, you wrote:
    Mac:

    Nope.


    William Miller

    PS:  It's pretty straight forwards, the code says "bus or conductor."

    wm

    PPS:

    Can  you customer live with a smaller feeder breaker, say 125
    amps?  If so, your gold.

    wm



    At 06:43 PM 9/27/2012, you wrote:
    Hello wrenches,

    I am looking for advice on how the 120% rule applies to feeders
    for a subpanel.  I have this scenario:
    150A bus rating on subpanel with main breaker of 100A.  The
    conductors feeding this subpanel are 100A rated conductors.  Can
    I backfeed with a 40A breaker?

    Thanks

    --



    Mac Lewis


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to