Hi Fellow Wrenches,

Thanks for the insight that AMR systems could interfere with not only data monitoring (previous thread) but also with the inverter control function, too.

I have attempted to gain some insight into the AMR system the local utility uses (Cellnet) but talking to the utility people, they would have you believe this is privileged if not secret info. When Ameren first implemented the system (reportedly the largest AMR system in the nation) they advertized that they would know within seven seconds that you were without power. That number has been seriously revised upwards in the interim.

Anyone have any info about using/accessing the AMR info for the customer to view?

As always, TIA for the collective wisdom,
Bill Loesch
Solar 1 - Saint Louis Solar
On 09-Oct-12 7:06 AM, Jeff Wongstrom wrote:
All,

The utility(Flathead Electric Co-op) has recently completed automatic meter reading using a power line carrier for all co-op members.  I will give them a call to find out the type and frequency of signaling. The state 104 has been occurring within 10 minutes of connecting to the grid.  Perhaps the IG uses the zero crossing and is confused by the meter reading signal.  

I have talked with Fronius and it looks like they may send an IG+ as an upgrade.  Perhaps the IG+ does not get confused by meter reading signals. Fingers crossed. If it does go into state 104 maybe opening up the frequency window will help.

We have no other inverters on this utility for comparison and have had no feedback on the hand full of grid-tied systems out there.

Thanks for the valuable input,

Jeff


Jeff Wongstrom
NABCEP Certified
406.291.3416



On Oct 8, 2012, at 7:38 PM, Kent Osterberg wrote:

Jeff,

Is there any chance the utility has recently implemented a remote meter reading system? The Aclara

                    TWACs remote meter reading system communicates
                  by putting a pulse on the line that is very near the
                  zero crossing of the voltage waveform. Unfortunately
                  the zero crossing is easily and often used as a
                  reference point for frequency measurements. Devices
                  that watch the zero crossings are often confused by
                  the TWACS signal. The signal isn't there constantly --
                  only when the local kWr meter has been asked to send
                  data.
Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882
On 10/8/2012 9:34 AM, Jeff Wongstrom wrote:
Hello wrenches,

We have a Fronius IG3000 that chronically and frequently cycles into and out of a state 104(grid frequency not within admissible range).   The utility has monitored the supply and claims to have found no frequency or supply issues.   Fronius sent a replacement inverter but the error persists. The tie in point was moved from the critical loads sub panel to the main distribution panel.  The state 104 persists with ALL other breakers open.  A Fluke DMM min/max function captures no frequency readings outside of the inverter frequency window-same with voltage readings.   

Any suggestions or recommendations?

Thanks,

Jeff





_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to