HI Dan, The Radian from outback can be rebuilt. I don't know if they are sending out replacement guts or just replacement inverter modules however.
Jay peltz power On Oct 14, 2012, at 5:54 AM, <[email protected]> wrote: > I like Outback because I can rebuild them on the wall. I'd be eying two > VFX3648 (Or VFX7248 is what they used to call them). I suspect Magnum is > similar, but I really haven't seen that many around. As for starting motor > loads, NEC article 430 has gobs of info on projecting starting currents and > sizing conductors (Check out the tables toward the end of the article). Keep > in mind much has to do with conductors sizing. I'd be shooting for a max loss > of 3% at full current draw.. especially in the low voltage conductors. As for > installation, I like set ups where the inverters are inclosed in a closet and > set up so that the main fresh inlet air to the building washes thru the > closet (Powered by gravity - no fans). Good luck. db > > > Dan Brown > Foxfire Energy Corp. > Renewable Energy Systems > (802)-483-2564 > www.Foxfire-Energy.com > NABCEP #092907-44 > >
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org