Hi William

Thanks

I've got the V set points done and it will manually turn on/off the genset via 
the SCP, so that works, but voltstime get below set points, or so it seems

Of course it's 2 hrs each way with bad cell service. 

Just trying to get the most info before I go out there and do the sit there and 
see if it starts. 

Thanks. 

Jay

Sent from my iPhone

On Dec 26, 2012, at 8:26 PM, William Miller <will...@millersolar.com> wrote:

> Jay:
> 
> You may THINK you have all the settings right but the SCP is not intuitive.  
> I have a nagging feeling that I have gone through this and found some 
> disassociated menu with a setting that needed to be changed.  I will peruse 
> the manual and see if I find anything.
> 
> I use to think the output was open collector (wet) but I was told it was a 
> dry reed relay, so polarity should not be an issue.  I would ohm the 
> disconnected leads to ground in the diode mode, using both lead polarities to 
> verify.  Although if you have manual start you have already bypassed this 
> possibility.
> 
> Can you try setting the start voltage a volt above whatever your battery 
> voltage is at the moment for testing.
> 
> Setup if more trouble than it should be.  I use Gen. Type 2 for two wire 
> starting.
> 
> Good luck.
> 
> William
> 
> PS:  Have you checked the menus: AGS/CFG Trigger/Start DCV 30 sec through DCV 
> 24 hour?  They come disabled and the auto start will not work unless one or 
> more are enabled.  This is unlike the SW which came with the triggers enabled 
> by default.  This may be what I was thinking of.
> 
> WM
> 
> 
> At 05:52 PM 12/26/2012, you wrote:
>> > Hi all
>> 
>> I've got a client with a XW and AGS.
>> 
>> 
>> When I go there, manual on/off works.
>> 
>> He says however that it will not auto start, ie system shutdown due to low 
>> voltage
>> 
>> I thought I've got all the settings right, but ??
>> 
>> Any ideas?
>> 
>> Thanks
>> 
>> Jay
>> 
>> Peltz power
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
>> No virus found in this incoming message.
>> Checked by AVG - www.avg.com
>> Version: 8.5.455 / Virus Database: 271.1.1/5487 - Release Date: 12/25/12 
>> 19:34:00
> 
> Miller Solar
> Voice :805-438-5600
> email: will...@millersolar.com
> http://millersolar.com
> License No. C-10-773985
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to