Mark:

I don't know the SolarBridge product as well as some others.
Like you, I would ASS U ME the lack of a grounding lug would indicate that a 
GEC is not needed.
Referring to the manufactures written instructions on grounding in the manual 
is always the best reference.

You are correct, there are 2 cases where you would not need a GEC per Code.

1) The unit is Listed as an AC Module so it is exempt from DC side 
requirements.  This is not to be confused with a micro-inverter installed in 
the field on a module which would still need to meet the DC side requirements.

2) The inverter operates with a floating array, i.e. the array positive or 
negative (or neutral in a bi-polar array) are not bonded to ground.  Just to 
clarify one point ... With a floating array the inverter topology could be 
either isolated (HF or LF transformer) or non-isolated (transformerless).  The 
main criteria is if array conductors are, or are not, bonded to ground by the 
inverter (which is not necessarily related to a specific topology).

Best Regards,

John Berdner
General Manager, North America

SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3201 ext 747
M: 530.277.4894

-----Original Message-----
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Monday, January 14, 2013 8:11 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules

I am interested in the SolarBridge , it has no chasis lug so it must not 
require a GEC, right?

So why does it not require a GEC? Is it because it is not an isolated inverter? 
Because it is an isolated inverter that does not have a grounded current 
carrying conductor on the DC side? Because it is listed as an AC module so who 
cares what is happening on the DC side?

On 1/14/2013 6:52 PM, John Berdner wrote:
> Mark:
>
> The GEC is required if the inverter bonds one of the PV conductors to ground 
> (as Enphase does).
> Enphase support may not have a problem with it but not using a GEC (with all 
> the GEC requirements) on any system with a grounded array is definitely a 
> Code violation in NEC 2008 and 2011.
> I don't recall it being eliminated in the 2014 Code either but could be wrong.
>
> If the inverter does not bond the array positive or array negative to ground 
> then the array is ungrounded so no GEC is required.
> Non-isolated inverters (also referred to as transformerless inverters) do not 
> bond the array negative or array positive to ground and so no GEC is required 
> (EGC is still required).
>
> If you have a Listed AC module then none of the DC side requirements apply so 
> no GEC would be required unless required by the manufacturer's instructions.
> Unfortunately, adding a micro-inverter to a module in the field does not make 
> it a Listed ac module.
>
> Best Regards,
>
> John Berdner
> General Manager, North America
>
> SolarEdge Technologies, Inc.
> 3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new
> address.)
> T: 510.498.3201 ext 747
> M: 530.277.4894
>
>
> -----Original Message-----
> From: re-wrenches-boun...@lists.re-wrenches.org
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
> Frye
> Sent: Monday, January 14, 2013 3:31 PM
> To: RE-wrenches
> Subject: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules
>
> Does anyone have the latest on the GEC for micro-inverters/ACPV issue?
>
> I know it is still in NEC 2008 and I believe 2011 with plans to address it in 
> 2014.
>
> I am specifically interested in the issue of GEC means continues 
> (irreversible splices) and the whole business of the DC side of these devices 
> constituting a separately derived system.
>
> Enphase technical support is fine if the micro inverter chasis is bonded to a 
> EGC only, but they leave the lug on the chasis if you want/need to build a 
> GEC.
>
> SolarBridge (pre-assembled micro-inverter) seems to be devoid of a chasis lug 
> and therefore by extension does not/can not had a GEC in the system.
>
> Exeltech (integrated micro-inverter aka. ACPV) does not seem to have a lug on 
> its chasis.
>
> Has the industry pretty much moved to not requiring a GEC for these devices 
> and if so, how are the AHJ taking it?
>
> Thanks,
> Mark Frye
> Berkeley Solar Electric Systems
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
> CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
> the use of the individual or entity who is the intended recipient and may 
> contain information that is privileged, confidential and exempt from 
> disclosure or any type of use under applicable law. If the reader of this 
> e-mail is not the intended recipient, or the employee, agent, or 
> representative responsible for delivering the e-mail to the intended 
> recipient, you are hereby notified that any dissemination, distribution, 
> copying, or other use of this e-mail is strictly prohibited. If you have 
> received this e-mail in error, please reply immediately to the sender.
> P Please think of the environment before printing this email
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
the use of the individual or entity who is the intended recipient and may 
contain information that is privileged, confidential and exempt from disclosure 
or any type of use under applicable law. If the reader of this e-mail is not 
the intended recipient, or the employee, agent, or representative responsible 
for delivering the e-mail to the intended recipient, you are hereby notified 
that any dissemination, distribution, copying, or other use of this e-mail is 
strictly prohibited. If you have received this e-mail in error, please reply 
immediately to the sender.
P Please think of the environment before printing this email
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to