Yes, the entire GEC requirement is a pain in the neck and IMHO makes no sense 
for grid tied PV.
Historically it comes out of the rural electrification days when you had DC 
systems actually "supplying premises wiring", i.e. lighting circuits, outlets, 
etc.
In that context the bond between the DC circuit conductors and Ground is a 
critical conductor just as it is in an AC system supplying premises wiring.
If you lose the ground reference in one of these systems then the voltage on 
the circuit conductors can float all over the place and bad things can happen. 
(think loose neutral in a split phase AC system).
The Code requirements for a GEC are restrictive precisely to assure the 
integrity of the bond to ground.
I have long contended that grid tied PV systems do not supply premises wiring  
and so the GEC requirement does not even apply.
Others in high places disagree.

No matter... the industry moving to ungrounded systems which eliminate the need 
in another way.
This is but one of many reasons I like ungrounded arrays.

Best Regards,

John Berdner
General Manager, North America

SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3201 ext 747
M: 530.277.4894


-----Original Message-----
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August Goers
Sent: Tuesday, January 15, 2013 11:12 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules

Hi John,

I definitely see your point and that is why I was somewhat questioning the use 
of WEEBs with Enphase below. Enphases's instructions (link posted in thread 
below) seem to indicate a support of running the continuous GEC on the rack and 
then bonding the microinverter to the rack with WEEBs. Maybe I am 
misinterpreting the document or perhaps Enphase has another take.
There is no question that according to NEC 250.64(C) the GEC must be 
continuous. In the 2008 NEC handbook section 690.42 Point of System Grounding 
Connection has an application note "Connections are to be made in accordance 
with markings on the equipment or in the installation instructions."

All that said, it seems like technology is leaning towards listed AC Modules or 
floating array inverters. It sounds like that removes the requirement for a GEC 
which is great to help reduce installation costs.
The GEC has always been a pain in the neck.

Best,

August


-----Original Message-----
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of John Berdner
Sent: Monday, January 14, 2013 7:07 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules

August:

The WEEB or other Listed grounding means between the inverter case and the 
structure are not "contiguous or irreversible spliced" and therefore do not 
meet the requirements for a GEC.
If the structure is then grounded via a bolt on lug it also is not irreversible 
or contiguous.
If you can unbolt something and disconnect the ground then it is not contiguous 
or irreversibly spliced.
Both of the above are ok for EGC but not for GEC.

GEC is a pain in the neck but the Code requirements are clear.
If the PV array conductor (pos or neg) is bonded to ground by the inverter then 
the inverter requires a GEC with all the related requirements - no if and's or 
but's.

Best Regards,

John Berdner
General Manager, North America

SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new
address.)
T: 510.498.3201 ext 747
M: 530.277.4894


-----Original Message-----
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August Goers
Sent: Monday, January 14, 2013 4:32 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules

Hi Mark,

There have been some recent threads on this list touching on this topic.

As far as I understand, Enphase microinvertes still require a GEC up to and 
including the 2011 NEC. I don't know about the 2014 NEC. Enphase bonds the 
positive DC module conductor to ground. Pages 16 and 17 of their M215 
installation manual address grounding:

http://enphase.com/wp-uploads/enphase.com/2011/06/Enphase_M215_Installatio
nOperation_Manual.pdf

Products such as Solar Bridge that are listed as Alternating Current (AC) 
Modules (per NEC 690.2) don't need a Grounding Electrode Conductor (GEC) as 
long as there are no conductors connected to ground within the product.
Solar Bridge has a good article on this:

http://solarbridgetech.com/microinverters-and-ac-pv-modules-are-different/

This all takes us back to using Enphase with grounding washers like WEEBs for 
the GEC. According to what I read in their instructions (and after many phone 
calls), it sounds like they are okay with us running the GEC on the racking in 
#6 and then bonding the microinverters to the rack with WEEBs. Seems a little 
strange but it's been working for us.

Good topic!

Best,

August
415.559.1525


-----Original Message-----
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Monday, January 14, 2013 3:31 PM
To: RE-wrenches
Subject: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules

Does anyone have the latest on the GEC for micro-inverters/ACPV issue?

I know it is still in NEC 2008 and I believe 2011 with plans to address it in 
2014.

I am specifically interested in the issue of GEC means continues (irreversible 
splices) and the whole business of the DC side of these devices constituting a 
separately derived system.

Enphase technical support is fine if the micro inverter chasis is bonded to a 
EGC only, but they leave the lug on the chasis if you want/need to build a GEC.

SolarBridge (pre-assembled micro-inverter) seems to be devoid of a chasis lug 
and therefore by extension does not/can not had a GEC in the system.

Exeltech (integrated micro-inverter aka. ACPV) does not seem to have a lug on 
its chasis.

Has the industry pretty much moved to not requiring a GEC for these devices and 
if so, how are the AHJ taking it?

Thanks,
Mark Frye
Berkeley Solar Electric Systems
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
the use of the individual or entity who is the intended recipient and may 
contain information that is privileged, confidential and exempt from disclosure 
or any type of use under applicable law. If the reader of this e-mail is not 
the intended recipient, or the employee, agent, or representative responsible 
for delivering the e-mail to the intended recipient, you are hereby notified 
that any dissemination, distribution, copying, or other use of this e-mail is 
strictly prohibited. If you have received this e-mail in error, please reply 
immediately to the sender.
P Please think of the environment before printing this email 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
the use of the individual or entity who is the intended recipient and may 
contain information that is privileged, confidential and exempt from disclosure 
or any type of use under applicable law. If the reader of this e-mail is not 
the intended recipient, or the employee, agent, or representative responsible 
for delivering the e-mail to the intended recipient, you are hereby notified 
that any dissemination, distribution, copying, or other use of this e-mail is 
strictly prohibited. If you have received this e-mail in error, please reply 
immediately to the sender.
P Please think of the environment before printing this email
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to