There is another solution that can work.
If you install a diversion charge controller on the battery then this should 
prevent back feeding the generator.
As the battery reaches the set point the diversion regulator kicks in and 
prevents the "extra" power from flowing back to the genny.

I would probably wire the diversion regulator so that it was not in the circuit 
unless the grid was down to make sure the VFX charge control is managing the 
battery most of the time.
Set the diversion regulator slightly lower than the VFX float setting and test 
it first just to be sure.

Best Regards,

John Berdner
General Manager, North America

[cid:image001.jpg@01CDF3D0.4AE4FB00]

SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3201 ext 747
M: 530.277.4894

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of SunHarvest
Sent: Wednesday, January 16, 2013 9:54 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] off grid PV connected to generator

Finally got through to Outback. They said the GVFX could be wired with a genny 
line-side of the inverter in order for the genny to charge the batteries and 
that this configuration could potentially cause problems for the genny. The 
likelihood of the PV sending power to the generator is extremely small as the 
inverter needs to see 5 minutes of perfect power in addition to sensing a near 
full battery bank before it will attempt to "sell" power back to the AC source. 
Additionally, when the genset is connected with the AGS the generator will turn 
on automatically when the batteries require absorption and automatically turn 
off when the batteries are "full" (according to set points). The moment when 
the batteries reach that "full" set point is when the inverter may attempt to 
"sell" power back but this is when the AGS will shut down the generator.

I have, on my house, an older Xantrex SW4024 and it works fine with my Kohler 
8.5kW genset but then again, it has two AC-IN inputs which operate in mutual 
exclusion. Outback mentioned that while the FX series inverters do not enjoy 
this feature, the Radian inverter re-introduces this configuration. Hallelujah!

So, it sounds like the solution for the Outback grid-tied BB system is to 
install an AGS...which is part of the plan as soon as the homeowner completes 
some required genny repairs.

The solution for the grid-tied Enphase system, it seems, will have to be asking 
the homeowner to shut off his PV when the grid goes down...Ugh.

But reading back through the older posts in this thread, pretty much all 
recommending against configuring the genset supply-side of the inverter, the 
question remains, for me at least, how does the generator charge the batteries 
if the genny is load-side of the inverter?

Eric
SunHarvest

----- Original Message -----
From: SunHarvest<mailto:e...@harvesthesun.com>
To: RE-wrenches<mailto:re-wrenches@lists.re-wrenches.org>
Sent: Wednesday, January 16, 2013 8:47 AM
Subject: Re: [RE-wrenches] off grid PV connected to generator

For claification, the two installs with which I'm concerned are:

1) Grid or 8.5kW Genset ---> Manual transfer switch ---> FlexPower One 
w/GVFX3524, FM80, Mate ---> transformer to 240vac ---> Residential Loads.
This set up also has batteries and an old 600Wstc PV array tied in to the FP1.

2) Grid or ~10kW Genset determined by auto transfer switch, all located at 
utility main panel/meter located
about 400' from main residence ---> Subpanel and sub meter at main residence 
<--- PV-designated subpanel <--- 8.4kW PV array w/Enphase micros.

It's good to hear (thanks Phil) that PV doesn't auto disconnect when the genny 
kicks on (didn't think this was the case) but if the PV does not disconnect 
don't we end up with PV potentially backfeeding to the genset?? Isn't this 
thread discussing how PV backfeeding to a genny is a dangerous configuration??

David, I can't disconnect the GVFX when the grid is down and the genny on as 
both grid and genset supply the AC-IN to the inverter via the manual transfer 
switch. But your comment begs the question: Why do you recommend disconnecting 
the inverter?

Still trying to connect to an Outback tech (Katee Wood)...

Eric
SunHarvest

----- Original Message -----
From: David Katz<mailto:dk...@aeesolar.com>
To: RE-wrenches<mailto:re-wrenches@lists.re-wrenches.org>
Sent: Wednesday, January 16, 2013 8:12 AM
Subject: Re: [RE-wrenches] off grid PV connected to generator

Phil,
If Eric is using the FX ot GTFX in an AC coupled mode, he would need to 
disconnect the grid tie inverter when the generator was running.  From the 
thread, I cannot tell if this is his situation.
David Katz

Sent from my HTC smartphone on the Now Network from Sprint!

----- Reply message -----
From: "Phil Undercuffler" <solarp...@gmail.com<mailto:solarp...@gmail.com>>
To: "RE-wrenches" 
<re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>>
Subject: [RE-wrenches] off grid PV connected to generator
Date: Tue, Jan 15, 2013 8:07 pm

Eric,

Good questions, and you hit on a number of topics so let me see if I can 
address them one at a time, not necessarily in chronological order.

Yes, the optimal application for the GTFX / GVFX inverter series is grid tie 
with battery backup.  If you just want backup to the grid, the traditional FX 
is a great solution.  If you need extended run-time and want to integrate a 
generator, then the Radian series is a better solution because it can not only 
integrate both grid and generator, but it can change its operating parameters 
based on which input it's connected to.

The SW, XW and Radian inverters are all capable of operating on-grid 
(grid-interactive or backup) or off-grid (with or without a generator).  
However, none will automatically disconnect the PV when the genny auto-starts, 
nor would I suggest that they should.  Realistically, the system should only 
start the genny when the batteries are near depletion -- if it's started, the 
batteries need all the help they can get.  Rather, the generator should only be 
disconnected (turned off) when the batteries reach the absorb setpoint.  BTW, I 
can't speak for everyone but none of those inverters have that functionality, 
at least not yet.

With 600 Watts of connected PV, I wouldn't worry about disconnecting the PV.  
Even with a small battery bank, the sun will set before that size of array 
drives the bank anywhere close to an absorb voltage.  Add another zero to the 
PV size and my answer would be different, of course.

Also, if you do wind up installing an automatic transfer switch with a 
battery-based inverter system, don't allow the ATS to control the generator 
starting, even if that flies against every tradition of the generator sales 
guy.  You don't want the genny running through every minute of the power 
outage, you want the system to start the genny only when the batteries are low.

Good luck with it, and enjoy the sun!

Phil



On Tue, Jan 15, 2013 at 1:50 PM, SunHarvest 
<e...@harvesthesun.com<mailto:e...@harvesthesun.com>> wrote:
Further, I recently installed a GVFX for a customer. I'm hearing from certain 
sources that the grid-tied line of inverters from Outback are not designed to 
interface with a generator. Really??

I was told by Outback to install a transfer switch line/supply side of the 
inverter; that this was the only way to interface the genny with the inverter; 
that the AC Hot In could come from grid or a genset. And indeed, this is the 
only way I can figure out how to get the genny to charge the batteries when the 
grid goes down. But then again, I don't have the extensive electrical 
background that allows me to think outside the box as often as I would 
like...that's why I'm posing my query here for the pros. In this Outback 
install I have to again advise the homeowner to open the PV breaker to the 
inverter during generator operation, right? Even though he has a modest 600W 
(STC) array and an 8.5kW Kohler genset. Hardly the opportunity for solar to 
feed back to the genny under the most sunny and cool of days. I'm more 
concerned with the Enphase install.

The Xantrex SW series inverters are fully capable of operating on-grid or 
off-grid with a genset. So do those inverters automatically disconnect the PV 
when the genny auto-starts? And with the Outback, is the Mate supposed to do 
the same (as long as the genny is operated by the auto-start and not a transfer 
switch)?

________________________________
_______________________________________________
List sponsored by Home Power magazine

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
________________________________
_______________________________________________
List sponsored by Home Power magazine

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
the use of the individual or entity who is the intended recipient and may 
contain information that is privileged, confidential and exempt from disclosure 
or any type of use under applicable law. If the reader of this e-mail is not 
the intended recipient, or the employee, agent, or representative responsible 
for delivering the e-mail to the intended recipient, you are hereby notified 
that any dissemination, distribution, copying, or other use of this e-mail is 
strictly prohibited. If you have received this e-mail in error, please reply 
immediately to the sender.
P  Please think of the environment before printing this email

<<inline: image001.jpg>>

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to