I would certainly agree with Will here. You can't make that argument as stated, 
it's wrong. Please don't try to make it to your AHJ, you take the chance of 
f-ing it up for everyone around there. I think the best argument you can try 
is:  aside from the usual 3-4lbs/sq/ft that the array itself ads to the roof 
load, snow will be very unlikely to build up on the modules to the degree that 
it builds up anywhere else on the roof. The freezing-rain-before-a-snow 
phenomena is very real and it WILL happen sooner or later. Not often perhaps 
and under most conditions the snow will leave the modules before the roof. 
But...Gotta be real about that.
Bob-O Schultze


On Feb 19, 2013, at 11:06 AM, Will White wrote:

Most structural engineers I’ve seen take a reduction for slippery surface but I 
think you’d be stretching things to say adding PV panels reduces the load to 
zero.  I have a 45 degree pitch roof and I get snow build up some times 
especially if we get freezing rain before the snow. 
 
Also if you have an asphalt shingle roof you can create an unbalanced load with 
snow sliding off the south side and sticking on the north side.  Most engineers 
take this into consideration too.
 
Thanks,
Will
 
__________________________________________________________________________________________
Will White
Regional Field Operations Manager – New England
 
Real Goods Solar
64 Main St.
Montpelier, VT 05602
Tel: (802) 223-7804
Cell: (802) 234-3167
www.realgoodssolar.com
 
 
 
 
 
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Gary Bassett
Sent: Tuesday, February 19, 2013 1:48 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Snow loads
 
Has anyone in the snow belt areas have any luck with convincing their local 
building inspectors that the snow melts or slides from panels, much like a 
metal roof only better. Thus your snow load would be reduced to zero where the 
panels have been installed.
 
Gary
 
 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to