Meant to say, "You should tweak #3 & #4 above..."

Drake,

Charging an AGM battery does not have to occur at the maximum charge voltage 
allowable; you can charge at a lower voltage for longer periods of time and 
still achieve 100% SoC. Since you have grid power to work with, slow down the 
charge cycle.

Assuming you have a late model ME-RC and version 5 or higher inverter, you can 
custom program the charge voltages. Here's what I would do: 
Go to Custom settings for battery type (setup menu 04).
Set the Absorb voltage for 26.8.
Set the Float for 26.4
Set the absorb time to 8 hours
Be sure the charge rate( setup menu 05) is 100%.

Near the end of the absorb charge cycle, measure the current going into the 
battery. If it is less than 0.2 amps/100AH capacity, the bank is full. You 
should #3 & #4 above until it works out for the low temp. comp. and charge time 
but it should work well.

If you are concerned about this lower voltage, set up a periodic equalize 
charge to 28.8.

Larry Crutcher
Starlight Solar Power Systems





On Mar 7, 2013, at 3:00 PM, Drake wrote:

Hello Wrenches,

I had an unexpected glitch in AC coupling a Magnum 4024 PAE inverter.  The 
system utilizes AGM batteries, which (according to Concorde tech support) have 
a very strict upper voltage limit.

The relay used to stop the current input from the direct grid tie inverter, 
when battery voltage is high, is controlled by a Morningstar Relay Driver.  The 
relay driver is set to shut off the charge at 28.8 volts.

The charger on the Magnum is set to charge the batteries to  28.6 volts.  

The plan was to be able to charge batteries from the Magnum without tripping 
the AC connection between the grid tie inverter to the grid.  The Magnum should 
charge to 28.6 volts, 0.2 volts below the relay driver's programmed trigger 
point. 

There is one catch to using this approach. The Magnum inverter has a remote 
temperature sensor in the battery bank. The relay driver is not temperature 
corrected. Therefore, when the batteries are cold, the charging voltage goes up 
in the Magnum.  This higher voltage trips the relay controlled by the driver, 
and disconnects the grid tie inverter from the grid.  

I've played with the voltage set points, but the charge voltage on the Magnum 
would be too low for good battery maintenance.  If these were liquid 
electrolyte batteries, I'd crank up the voltage on the relay driver.  Since 
they are AGM batteries, it doesn't seem like a good idea to do that. 

The work around for this at present is to;
Charge batteries at night in the winter
No problem is expected in the summer
The batteries are in an insulated box in a shed connected to the house. The 
inside of the battery box has a screened hole that is supposed to allow heated 
air into the box.  This vent doesn't keep the batteries warm enough to prevent 
the problem. 

Is there a temperature sensitive, voltage controlled relay or diver available?  
Has anyone used a temperature bulb with the relay driver in a way that could 
solve this problem? Has anyone else come up against this issue, and if so, what 
was your solution?

Thanks,

Drake 


Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV Installer
740-448-7328
http://athens-electric.com/ 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to