What problems is the system having?

Regarding your proposed 3P wiring solution, I don't know whether this has been fixed recently, but Outbacks in 3P historically haven't monitored the angle between phases. Under grid-connected operation it's not a problem, but after they lose the grid connection, you'd be relying on each inverter independently and consistently putting out exactly 216,000.00000 cycles of AC. This is only a problem with 208V 3P or 1P loads on your protected load panel. Since you don't have those currently, you'd be OK as long as you upsize the neutral and add a placard stating that no 208V loads should be added.

DKC

On 2013/3/28 11:23, Bill Turberville wrote:
I know I saw a thread on this but I cannot find it in the archive.  I
have inherited a customer that has a four inverter Outback system, 240V
1 Phase, on a 208Y120V 3 Phase 4 Wire system, that constantly has
problems.  A 208V to 240V 1 phase transformer was installed feeding the
input, but the system still struggles.  Will this system ever work
correctly as is, or does it need to be rewired for 3 phase and use the
third inverter as a spare.  This would include a lot of work rewiring
the output panel.  Any ideas?

W.C. (Bill) Turberville P.E.

President

ECE Solar

Electrical Contracting Enterprises LLC

3080 Stage Post Road Suite 107

Bartlett, TN 38133

901-348-9230 ext 101 phone

901-348-2192 fax

901-289-6346 cell

billt...@ece-llc.com <mailto:billt...@ece-llc.com>



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to