Gary - I'm not sure what the application is, but if you are trying to
convince an AHJ that this breaker is suitable for backfeed (i.e. approved
for current flow in both directions) then you can just point the to the
Code:


*NEC 2011 705.12(D)(5) Suitable for Backfeed. Circuit breakers, if backfed,
shall be suitable for such operation.  See related
ROP<http://code.necplus.org/document.php?id=necss%3A70-2011%3Anecs70-705.12#>
UL<http://code.necplus.org/document.php?id=necss%3A70-2011%3Anecs70-705.12#>
*
* *

*Informational Note: Circuit breakers that are marked “Line” and “Load”
have been evaluated only in the direction marked. Circuit breakers without
“Line” and “Load” have been evaluated in both directions.  *


For a brighter energy future,


Andrew Truitt
NABCEP Certified PV Installation Professional™ (ID# 032407-66)

Principal
Truitt Renewable Energy Consulting, LLC****

(202) 486-7507

LinkedIn Profile <http://www.linkedin.com/pub/andrew-truitt/8/622/713>

Company Website <http://truittreconsulting.weebly.com/>
 <%28202%29%20486-7507>****




"Don't get me wrong: I love nuclear energy! It's just that I prefer fusion
to fission. And it just so happens that there's an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it's wireless!"

~William McDonough








On Tue, Apr 23, 2013 at 11:23 AM, Carl Adams <swingjun...@gmail.com> wrote:

>
>
> -Forwarded on behalf of Gary Easton at ARP-Solar
>
>
> With Regards
> Carl Adams, President
> SunRock Solar, LLC
> 513.290.9072 (cell)
> 513.766.6025 (office)
>
>
>
> ---------- Forwarded message ----------
> From: gary easton <g...@arp-solar.com>
> Date: Tue, Apr 23, 2013 at 1:12 PM
> Subject: backfeeding breakers
> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
>
>
> Hello,
> Can anyone point me to the data sheet indicating the reverse feed
> capability of a seimens QP 20 A 240 V breaker?
>
> --
> Gary Easton
> Appalachian Renewable Power
> Stewart, Ohio 45778
> NABCEP Certified Solar PV
>
> T: 740-277-8498
>  www.arp-solar.com
>
> “First they ignore you. Then they laugh at you. Then they fight you. Then
> you win.”
> ~Ghandi
>
>
>
>
> --
> Gary Easton
> Appalachian Renewable Power
> Stewart, Ohio 45778
> NABCEP Certified Solar PV
>
> T: 740-277-8498
>  www.arp-solar.com
>
> “First they ignore you. Then they laugh at you. Then they fight you. Then
> you win.”
> ~Ghandi
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to